I see this was answered as I’m typing, but here’s my logic path if it’s helpful:
1. LS-B confirms you’ve effectively killed all sources of heat load that wouldn’t be introduced by the HVAC (i.e. ventilation loads).
2. You have no exhaust in the zone.
3. It therefore has to be a load introduced from the system (ventilation or active cooling or similar).
I observe electric heating and empty inputs / defaults for the OA and active cooling inputs for the associated PSZ system. If I push cooling capacity and min OA fraction to zero, I get no unmet heating hours.
Philosophical food for thought (future reference): Hindsight 20-20, you may have made an issue like this harder to solve by doing something “extreme” like eliminating all interior surfaces, in kind removing all means of heat transfer… if the space has no way to get rid of built up heat it might cause a system to do something weird like desperately economize in sub freezing temps to deal with ever-building heat loads, creating a new artificial problem out of the earlier shotgun remedy efforts. If you should find no remedy in this sort of “turning the dials,” I’ve found it is usually a good practice to undo / step back those efforts before trying other solutions.
Here’s that LS-B for reference:
[cid:image001.png at 01D49874.A131F0E0]
~Nick
[cid:image002.png at 01D49874.A131F0E0]
Nick Caton, P.E., BEMP
Senior Energy Engineer
Regional Energy Engineering Manager
Energy and Sustainability Services
Schneider Electric
D 913.564.6361
M 785.410.3317
F 913.564.6380
E nicholas.caton at schneider-electric.com<mailto:nicholas.caton at schneider-electric.com>
15200 Santa Fe Trail Drive
Suite 204
Lenexa, KS 66219
United States
[cid:image003.png at 01D49874.A131F0E0]
From: Equest-users <equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org>> On Behalf Of Chris Hadlock via Equest-users
Sent: Thursday, December 20, 2018 1:05 PM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] mystery heating load
[External email: Use caution with links and attachments]
________________________________
I've had a few responses requesting the modeling files so I've attached the INP and PD2 file (weather file is CWEC\Toronto.bin). The zone in question is "L0 Elev Lobby S" and I've already removed all exterior surfaces from this space (i.e. there are no Child Components). I've assigned this zone to it's own system (it's the last system on the air-side tab) called "Test System". I've already created the hourly reports where you'll see all of the underheated hours (which only occur in the winter). The LS-B report shows no (zero) htg load. I realize the system is not really providing any heating to this zone the way it's setup.
Thanks,
Chris
On Thu, Dec 20, 2018 at 1:26 PM Chris Hadlock <cjhadlock at gmail.com<mailto:cjhadlock at gmail.com>> wrote:
Hello,
I've created a model using eQuest 3.65 (DOE 2.2) build 7173 that is of a 20 storey multi-residential building located in Toronto, Ontario (Canada). There is a basement with a elevator lobby that is an interior space (no exterior walls).
My model keeps telling me I have underheated hours for this lobby. I'm trying to figure out why there is a heating load and I'm stumped. I have removed what I believe to be all potential sources of heat loss. I've deleted the underground floor (which was R-100 anyway), I've deleted the interior walls (just to be thorough), there is no infiltration, and I've set the ventilation to zero. In my mind, there is no source of heat loss. I've even added a significant (10 W/ft2) equipment load and yet there are still underheated hours (I've even reduced my Tstat setpoint to 60F).
I've run an hourly report to help figure out the loads for both the space ("Sum of all weighted loads except infil and latent") and zone ("Load Calc'd SPACE Sensible load at const temp (Btu/hr)"). These reports all indicate a positive load (i.e. net heat gain) from my lights, plug loads and occupants. However through this process I'm also questioning these reports as the lighting, people and equipment load being reported don't exactly align with my modeled schedules for these loads....but I've put a pin in that.
Regardless, I have no idea how to figure out what may be resulting in net heat loss for this zone. To be thorough, I checked the elevator lobby on the ground level and the same thing is happening. Has anybody seen this before...any ideas what might be causing heat loss for a zone with no ventilation and no walls and no infiltration? It does seem to be seasonal (i.e no underheated hours in the summer) so it has some connection to weather file but does not correlate exactly.
If you do take the time to read this, a big thank you. If you provide the answer, you'll for sure be on Santa's "nice" list.
Chris
______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20181220/4966df21/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 53403 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20181220/4966df21/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 255 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20181220/4966df21/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 8477 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20181220/4966df21/attachment-0002.png>
More information about the Equest-users
mailing list