[Equest-users] Equipment Load
Jing Hong
hongjing.shirley at gmail.com
Tue Dec 18 06:29:41 PST 2018
Hi Paul,
For our cases, we estimated 80-ish% of the heat will go right up to the
exhaust hood. So should I fill the equipment and internal energy energy
sources with the number before the 80% reduction or after? For example, I
have 10 W/sqft electricity cookers and 100,000 Btu/hr gas cookers in the
kitchen, do I fill the tables below correctly?
[image: image.png]
On Tue, Dec 18, 2018 at 6:38 AM Paul Diglio <paul.diglio at sbcglobal.net>
wrote:
> Jing:
>
> Usually there is an exhaust hood with makeup air in the kitchen. If this
> is true, then you need to estimate how much heat is actually transmitted to
> the space compared to how much heat is expelled through the hood. This
> should lower your cooling load.
>
> Paul Diglio
> 87 Fairmont Avenue
> New Haven, CT 06513
>
>
> --------------------------------------------
> On Mon, 12/17/18, Jing Hong via Equest-users <
> equest-users at lists.onebuilding.org> wrote:
>
> Subject: [Equest-users] Equipment Load
> To: equest-users at lists.onebuilding.org, equest-users at onebuilding.org,
> equestuser00 at gmail.com
> Date: Monday, December 17, 2018, 7:37 PM
>
> Dear
> All,
> I have a question regarding
> the internal load.
> Under the Equipment tab of
> the internal load, there are two tables. One is Equipment
> and another is Internal Energy Sources. For my project with
> a kitchen serving 5 hours daily, how to input the power?
> For example, based on the specification sheets, we have
> 26.5 W/sqft input power density for electricity, and
> 474,000 Btu/hr for gas equipment. However, it will make the
> cooling load so huge for cooling
> systems. Does anyone know
> how eQuest convert energy input to cooling load? Did I fill
> the tables right?
>
>
>
> Thank you!Jing_______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank
> message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
> -----Inline Attachment Follows-----
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20181218/b41d0173/attachment-0001.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image.png
Type: image/png
Size: 27955 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20181218/b41d0173/attachment-0001.png>
More information about the Equest-users
mailing list