This might be true in the real world, but not in eQUEST (nor any other
simulation program that I know) because it would require CFD modeling of
the spaces.
Joe
On 12/20/2018 11:44 AM, Bruce Easterbrook via Equest-users wrote:
> Hi Chris,
> I'm thinking it could be due to infiltration. You have a 22 story
> elevator shaft that probably has a machine room on the roof. You also
> have stack effect. Any exterior air from the machine room getting in
> from this drive is going to be cold and move down to the bottom of the
> shaft and pool there. That would be the basement. It would also
> affect levels above this explaining your load in on the first floor.
> It should decline as you get higher in the building.
> Bruce Easterbrook P.Eng.
> Abode Engineering
>
> On 12/20/2018 2:05 PM, Chris Hadlock via Equest-users wrote:
>> I've had a few responses requesting the modeling files so I've
>> attached the INP and PD2 file (weather file is CWEC\Toronto.bin). The
>> zone in question is "L0 Elev Lobby S" and I've already removed all
>> exterior surfaces from this space (i.e. there are no Child
>> Components). I've assigned this zone to it's own system (it's the
>> last system on the air-side tab) called "Test System". I've already
>> created the hourly reports where you'll see all of the underheated
>> hours (which only occur in the winter). The LS-B report shows no
>> (zero) htg load. I realize the system is not really providing any
>> heating to this zone the way it's setup.
>>
>> Thanks,
>> Chris
>>
>> On Thu, Dec 20, 2018 at 1:26 PM Chris Hadlock <cjhadlock at gmail.com
>> <mailto:cjhadlock at gmail.com>> wrote:
>>
>> Hello,
>>
>> I've created a model using eQuest 3.65 (DOE 2.2) build 7173 that
>> is of a 20 storey multi-residential building located in Toronto,
>> Ontario (Canada). There is a basement with a elevator lobby that
>> is an interior space (no exterior walls).
>>
>> My model keeps telling me I have underheated hours for this
>> lobby. I'm trying to figure out why there is a heating load and
>> I'm stumped. I have removed what I believe to be all potential
>> sources of heat loss. I've deleted the underground floor (which
>> was R-100 anyway), I've deleted the interior walls (just to be
>> thorough), there is no infiltration, and I've set the ventilation
>> to zero. In my mind, there is no source of heat loss. I've even
>> added a significant (10 W/ft2) equipment load and yet there are
>> still underheated hours (I've even reduced my Tstat setpoint to
>> 60F).
>>
>> I've run an hourly report to help figure out the loads for both
>> the space ("Sum of all weighted loads except infil and latent")
>> and zone ("Load Calc'd SPACE Sensible load at const temp
>> (Btu/hr)"). These reports all indicate a positive load (i.e. net
>> heat gain) from my lights, plug loads and occupants. However
>> through this process I'm also questioning these reports as the
>> lighting, people and equipment load being reported don't exactly
>> align with my modeled schedules for these loads....but I've put a
>> pin in that.
>>
>> Regardless, I have no idea how to figure out what may be
>> resulting in net heat loss for this zone. To be thorough, I
>> checked the elevator lobby on the ground level and the same thing
>> is happening. Has anybody seen this before...any ideas what might
>> be causing heat loss for a zone with no ventilation and no walls
>> and no infiltration? It does seem to be seasonal (i.e no
>> underheated hours in the summer) so it has some connection to
>> weather file but does not correlate exactly.
>>
>> If you do take the time to read this, a big thank you. If you
>> provide the answer, you'll for sure be on Santa's "nice" list.
>>
>> Chris
>>
>>
>> _______________________________________________
>> Equest-users mailing list
>> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>> To unsubscribe from this mailing list send a blank message toEQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20181220/1d79c6fb/attachment-0001.htm>
More information about the Equest-users
mailing list