[Equest-users] eQuest - query
Tanya Soji
tanya.soji at quantumesco.com
Wed Aug 15 23:58:26 PDT 2018
Alright. Thanks much for your info.
*From:* equest user [mailto:equestuser00 at gmail.com]
*Sent:* 16 August 2018 10:53
*To:* Tanya Soji <tanya.soji at quantumesco.com>
*Cc:* equest-users at lists.onebuilding.org
*Subject:* Re: [Equest-users] eQuest - query
Yes Tanya,
You can model same HVAC system for Zones belonging to different shells.
You can do it better in detailed edit mode-
1. Just create the HVAC system example (HVAC System 1)
2. open the zones you need to assign to this system
3. Set the Parent System to "HVAC system 1"
On Thu, Aug 16, 2018 at 12:14 PM, Tanya Soji <tanya.soji at quantumesco.com>
wrote:
Hi Tejas,
Thanks for your input. I’ve understood the mistake.
I do have files saved at different stages in eQuest, which could be of help
to proceed from wizard to detailed mode again.
However, what if the system assignment to zones in the actual building
operations is different (i.e. zones in different shells could have supply
from the same HVAC system)? Is there any possibility to model like that?
Thanks,
Tanya
*From:* equest user [mailto:equestuser00 at gmail.com]
*Sent:* 16 August 2018 10:04
*To:* Tanya Soji <tanya.soji at quantumesco.com>
*Cc:* equest-users at lists.onebuilding.org
*Subject:* Re: [Equest-users] eQuest - query
Hi Tanya,
Are you trying to ask "why are so many systems created?"
-It is because in wizard mode-under the “Air side systems” tab, you have
selected your system to be "system per zone". That’s the reason why you
have one system for each zone.
ASHRAE appendix says that in Baseline case"System per floor” should be used
and for the proposed case it has to be modeled as per the HVAC drawings.
(multiple zones under 1 system as applicable)
As of now you have already entered detailed wizard mode, so I guess the
only option you have is to create new systems and assign the zones to it.
Hope I am clear
Revert if any assistance needed.
Thanks,
Tejas
On Wed, Aug 15, 2018 at 5:27 PM, Tanya Soji via Equest-users <
equest-users at lists.onebuilding.org> wrote:
Hey there eQuest Users,
I’m new to the eQuest softwarr,
Please find the attached screenshot given below. It’s a multi-storey
building with G+6 floors (distributed differently building-wise, some are
G+4) and 3 Basement floors. There are 5 shells totally.
I’ve finished entering details on the Wizard mode and have moved on to the
Detailed mode; However, inorder to enter more specific details (zonewise),
multiple active systems are available as seen. I’m not quite sure if every
zone entry needs to be made. And also how does eQuest generate default zone
definitions ? The template given doesn’t match to the ones given such as EL1
Sys1 (MZS) (G.W1).
[image: cid:image001.jpg at 01D43549.A9FEA670]
*Thanks & Regards, *
*Tanya Soji *| *Energy Engineer *
*E.*: tanya.soji at quantumesco.com | *D.*: + 971 4 567 4212
[image: QE Logo - 13NOV2017-01.png]
QUANTUM *EUROSTAR ENERGY SOLUTION CO. L.L.C*
📍 33rd Floor, Vision Tower, Business bay. P. O. Box - 51098, Dubai - UAE.
*☎ *: + 971 4 451 4444
Ê : + 971 4 451 4441
" : www.quantumesco.com
<http://www.quantumesco.com>
[image: facebook icon]
<https://www.facebook.com/eurostargroup>[image: youtube
icon] <https://www.youtube.com/channel/UCG902il67o-nQqnMYduBVUQ/feed?view_as=subscriber>[image:
linkedin icon] <https://www.linkedin.com/company/eurostar_2/>[image:
google plus icon]
<https://plus.google.com/u/0/112676746965733378647>[image:
twitter icon] <https://twitter.com/eurostar_group?lang=en>
This e-mail is from Eurostar Group. is intended solely for the person to
whom it has been addressed. It should not be used by anyone else. It may
contain confidential and/or legally privileged information. If you are not
the intended recipient, you are notified that any use, distribution,
transmission, printing, copying, dissemination or any action in reliance on
it is strictly prohibited. If you have received this email erroneously,
please delete this message and notify the sender.
The recipient acknowledges that Eurostar Group /subsidiaries/ associated
companies, are unable to exercise control or ensure or guarantee the
integrity of/over the contents of the information contained in e-mail
transmissions and further acknowledges that any views expressed in this
message are those of the individual sender and no binding nature of the
message shall be implied or assumed unless the sender does so expressly
with due authority of Eurostar Group. If the recipient thinks that any
part of this email transgresses any law of the land, he/she I shall
immediately alert Eurostar Group, by mailing their specific concern on
compliance at eurostargroup.com Needless to reiterate that Consequently,
Eurostar does not take any liability whatsoever, for any such
transgressions.
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
<http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org>
To unsubscribe from this mailing list send a blank message to
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
This e-mail is from Eurostar Group. is intended solely for the person to
whom it has been addressed. It should not be used by anyone else. It may
contain confidential and/or legally privileged information. If you are not
the intended recipient, you are notified that any use, distribution,
transmission, printing, copying, dissemination or any action in reliance on
it is strictly prohibited. If you have received this email erroneously,
please delete this message and notify the sender.
The recipient acknowledges that Eurostar Group /subsidiaries/ associated
companies, are unable to exercise control or ensure or guarantee the
integrity of/over the contents of the information contained in e-mail
transmissions and further acknowledges that any views expressed in this
message are those of the individual sender and no binding nature of the
message shall be implied or assumed unless the sender does so expressly
with due authority of Eurostar Group. If the recipient thinks that any
part of this email transgresses any law of the land, he/she I shall
immediately alert Eurostar Group, by mailing their specific concern on
compliance at eurostargroup.com Needless to reiterate that Consequently,
Eurostar does not take any liability whatsoever, for any such
transgressions.
--
This e-mail is from Eurostar Group. is intended solely for the person to
whom it has been addressed. It should not be used by anyone else. It may
contain confidential and/or legally privileged information. If you are not
the intended recipient, you are notified that any use, distribution,
transmission, printing, copying, dissemination or any action in reliance on
it is strictly prohibited. If you have received this email erroneously,
please delete this message and notify the sender.
The recipient
acknowledges that Eurostar Group /subsidiaries/ associated companies, are
unable to exercise control or ensure or guarantee the integrity of/over the
contents of the information contained in e-mail transmissions and further
acknowledges that any views expressed in this message are those of the
individual sender and no binding nature of the message shall be implied or
assumed unless the sender does so expressly with due authority of Eurostar
Group. If the recipient thinks that any part of this email transgresses
any law of the land, he/she I shall immediately alert Eurostar Group, by
mailing their specific concern on compliance at eurostargroup.com
<mailto:compliance at eurostargroup.com> Needless to reiterate that
Consequently, Eurostar does not take any liability whatsoever, for any
such transgressions.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180816/90b845e6/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 63844 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180816/90b845e6/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 2642 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180816/90b845e6/attachment-0001.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 481 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180816/90b845e6/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.png
Type: image/png
Size: 500 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180816/90b845e6/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.png
Type: image/png
Size: 486 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180816/90b845e6/attachment-0002.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image006.png
Type: image/png
Size: 487 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180816/90b845e6/attachment-0003.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image007.png
Type: image/png
Size: 518 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180816/90b845e6/attachment-0004.png>
More information about the Equest-users
mailing list