[Equest-users] Space plenums have cooling load
Jones, Christopher
Christopher.r.Jones at wsp.com
Tue Apr 17 17:57:29 PDT 2018
I typically set the plenum space to CONDITIONED and the plenum zone to PLENUM. That seems to provide reasonable loads in the plenum.
Christopher R. Jones, P.Eng.
Technical Specialist
Sustainability & Energy
[cid:image003.png at 01D3D68E.B15898F0]
T +1 416-644-0252
2300 Yonge Street, Suite 2300
Toronto, ON M4P 1E4 Canada
wsp.com
Please consider the environment before printing...
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Jing Hong via Equest-users
Sent: Tuesday, April 17, 2018 6:00 PM
To: Nicholas Caton <Nicholas.Caton at schneider-electric.com>
Cc: equest-users at onebuilding.org
Subject: Re: [Equest-users] Space plenums have cooling load
Hi Nick,
Thanks for your reply. Coz my proposed U-value is worse than the baseline, it is normal that the baseline has a bit lower cooling load than the proposed. However, the plenum cooling load in the baseline is way much lower than those in the proposed, which should not be.
I figured it out. First, I realized that I should use "Plenum" instead of "unconditioned" . But it did not change too much. Second, I duplicated the proposed model, saved as Baseline, and then modified it with baseline information.
After modifying the model so many times, I might mess up some physical characteristics of the Baseline model. Starting over is easier than keeping debugging it. Especially, for a case, you cannot find the error for hours.
Hopefully, it is useful for some of you.
Jing
On Tue, Apr 17, 2018 at 4:34 PM, Nicholas Caton <Nicholas.Caton at schneider-electric.com<mailto:Nicholas.Caton at schneider-electric.com>> wrote:
Hi Jing,
It seems unintuitive to assert that your proposed case plenums has increased cooling loads – is there a good set of reasons for this?
I’m also unclear on what you mean by “it still shows cooling load for those space” – could you unpack this a little further?
Systems which use the plenums as a return air path could be a cause for why their loads are seen at the systems (though it sounds like you intend for them to be isolated). I might start with considering the sources of heat gains to your plenums, and determining what should be happening to direct/indirect heat gains to plenums over time. Should they be circulated back to systems responding to conditioned spaces? Common sources would include indirect gains from ceiling lighting fixtures, envelope (skin) loads (potentially exacerbated if spandrel glass is present), and internal loads transferred hourly from conditioned spaces below and from adjacent plenums.
If I had your model in-hand, I might scan for the presence of thermostat heating/cooling schedules being assigned to your plenum spaces, or assignments to a plenum space as a master zone for specific system types. Those could produce direct calls for airstream heating/cooling which otherwise wouldn’t be occurring.
~Nick
[cid:image004.png at 01D3D68E.B15898F0]
Nick Caton, P.E., BEMP
Senior Energy Engineer
Regional Energy Engineering Manager
Energy and Sustainability Services
Schneider Electric
D 913.564.6361
M 785.410.3317
F 913.564.6380
E nicholas.caton at schneider-electric.com<mailto:nicholas.caton at schneider-electric.com>
15200 Santa Fe Trail Drive<https://maps.google.com/?q=15200+Santa+Fe+Trail+Drive+%0D%0ASuite+204+%0D%0ALenexa,+KS+66219+%0D%0AUnited+States&entry=gmail&source=g>
Suite 204
Lenexa, KS 66219
United States
[cid:image005.png at 01D3D68E.B15898F0]
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org>] On Behalf Of Jing Hong via Equest-users
Sent: Tuesday, April 17, 2018 10:43 AM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>; equest-users at onebuilding.org<mailto:equest-users at onebuilding.org>
Subject: [Equest-users] Space plenums have cooling load
Hi All,
I have assigned all the space plenum as unconditioned. But it still shows cooling load for those space, which increase the Space Cool in the report. The plenums in the proposed model have much higher cooling load than the baseline one. How could I modify it?
Thank you!
Jing
______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
--
PhD Candidate, LEED AP BD+C
School of Architecture and Urban Planning
University of Wisconsin-Milwaukee
________________________________
NOTICE: This communication and any attachments ("this message") may contain information which is privileged, confidential, proprietary or otherwise subject to restricted disclosure under applicable law. This message is for the sole use of the intended recipient(s). Any unauthorized use, disclosure, viewing, copying, alteration, dissemination or distribution of, or reliance on, this message is strictly prohibited. If you have received this message in error, or you are not an authorized or intended recipient, please notify the sender immediately by replying to this message, delete this message and all copies from your e-mail system and destroy any printed copies. You are receiving this communication because you are listed as a current WSP contact. Should you have any questions regarding WSP's electronic communications policy, please consult our Anti-Spam Commitment at www.wsp.com/casl<http://www.wsp.com/casl>. For any concern or if you believe you should not be receiving this message, please forward this message to caslcompliance at wsp.com<mailto:caslcompliance at wsp.com> so that we can promptly address your request. Note that not all messages sent by WSP qualify as commercial electronic messages.
AVIS : Ce message, incluant tout fichier l'accompagnant (« le message »), peut contenir des renseignements ou de l'information privilégiés, confidentiels, propriétaires ou à divulgation restreinte en vertu de la loi. Ce message est destiné à l'usage exclusif du/des destinataire(s) voulu(s). Toute utilisation non permise, divulgation, lecture, reproduction, modification, diffusion ou distribution est interdite. Si vous avez reçu ce message par erreur, ou que vous n'êtes pas un destinataire autorisé ou voulu, veuillez en aviser l'expéditeur immédiatement et détruire le message et toute copie électronique ou imprimée. Vous recevez cette communication car vous faites partie des contacts de WSP. Si vous avez des questions concernant la politique de communications électroniques de WSP, veuillez consulter notre Engagement anti-pourriel au www.wsp.com/lcap<http://www.wsp.com/lcap>. Pour toute question ou si vous croyez que vous ne devriez pas recevoir ce message, prière de le transférer au conformitelcap at wsp.com<mailto:conformitelcap at wsp.com> afin que nous puissions rapidement traiter votre demande. Notez que ce ne sont pas tous les messages transmis par WSP qui constituent des messages electroniques commerciaux.
-LAEmHhHzdJzBlTWfa4Hgs7pbKl
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180418/237a6ebc/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 25844 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180418/237a6ebc/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.png
Type: image/png
Size: 255 bytes
Desc: image004.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180418/237a6ebc/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.png
Type: image/png
Size: 8477 bytes
Desc: image005.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180418/237a6ebc/attachment-0002.png>
More information about the Equest-users
mailing list