Nicholas Caton Nicholas.Caton at schneider-electric.com
Tue Apr 17 14:34:47 PDT 2018


Hi Jing,

It seems unintuitive to assert that your proposed case plenums has increased cooling loads – is there a good set of reasons for this?

I’m also unclear on what you mean by “it still shows cooling load for those space” – could you unpack this a little further?

Systems which use the plenums as a return air path could be a cause for why their loads are seen at the systems (though it sounds like you intend for them to be isolated).  I might start with considering the sources of heat gains to your plenums, and determining what should be happening to direct/indirect heat gains to plenums over time.   Should they be circulated back to systems responding to conditioned spaces?  Common sources would include indirect gains from ceiling lighting fixtures, envelope (skin) loads (potentially exacerbated if spandrel glass is present), and internal loads transferred hourly from conditioned spaces below and from adjacent plenums.

If I had your model in-hand, I might scan for the presence of thermostat heating/cooling schedules being assigned to your plenum spaces, or assignments to a plenum space as a master zone for specific system types.  Those could produce direct calls for airstream heating/cooling which otherwise wouldn’t be occurring.

~Nick

[cid:image001.png at 01D3D669.FC53D920]
Nick Caton, P.E., BEMP
  Senior Energy Engineer
  Regional Energy Engineering Manager
  Energy and Sustainability Services
  Schneider Electric

D  913.564.6361
M  785.410.3317
F  913.564.6380
E  nicholas.caton at schneider-electric.com<mailto:nicholas.caton at schneider-electric.com>

15200 Santa Fe Trail Drive
Suite 204
Lenexa, KS 66219
United States

[cid:image002.png at 01D3D669.FC53D920]



From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Jing Hong via Equest-users
Sent: Tuesday, April 17, 2018 10:43 AM
To: equest-users at lists.onebuilding.org; equest-users at onebuilding.org
Subject: [Equest-users] Space plenums have cooling load

Hi All,

I have assigned all the space plenum as unconditioned. But it still shows cooling load for those space, which increase the Space Cool in the report. The plenums in the proposed model have much higher cooling load than the baseline one. How could I modify it?

Thank you!

Jing



______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180417/0317fffd/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 255 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180417/0317fffd/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 8477 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180417/0317fffd/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: oledata.mso
Type: application/octet-stream
Size: 7133 bytes
Desc: oledata.mso
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180417/0317fffd/attachment.obj>


More information about the Equest-users mailing list