[Equest-users] How to set thermostat to have 0 heating load
Jing Hong
hongjing.shirley at gmail.com
Mon Apr 2 09:05:19 PDT 2018
Hi Nick,
Thanks for your time and effort working on my model. The model was
generating a small amount of space heating no matter how I modified the
schedule and set-point, then I selected "not install" under heating. So far
that is the only way I can get rid of the space heating. I will keep you
all updated what the LEED review will say when I get the report.
Thank you,
Jing
On Mon, Apr 2, 2018 at 9:42 AM, Nicholas Caton <
Nicholas.Caton at schneider-electric.com> wrote:
> For what it’s worth, I’m seeing no usage for the space heat end use
> whatsoever using the MEXICO91.BIN referenced in your project. The green
> “Misc. Equipment” draw on FM1 is due to your kitchen process loads defined
> at that specific space – if you zero those loads out fuel consumption is
> completely gone:
>
>
>
> As far as LEED goes however, I can’t answer with direct experience how
> reviewers typically handle facilities in idyllic climates that don’t
> require space heating. That might be a good separate query with the lists
> here as I’m sure someone has crossed that hill, but a separate run and
> write-up to demonstrate no calls for heat are necessary might be in order
> before simply removing all heating thermostat schedules in the model… just
> a thought.
>
>
>
> ~Nick
>
>
>
>
>
> *Nick Caton, P.E., BEMP*
>
> Senior Energy Engineer
> Regional Energy Engineering Manager
>
> Energy and Sustainability Services
> Schneider Electric
>
> D 913.564.6361 <(913)%20564-6361>
> M 785.410.3317 <(785)%20410-3317>
> F 913.564.6380 <(913)%20564-6380>
> E nicholas.caton at schneider-electric.com
>
> 15200 Santa Fe Trail Drive
> <https://maps.google.com/?q=15200+Santa+Fe+Trail+Drive+%0D%0ASuite+204+%0D%0ALenexa,+KS+66219+%0D%0AUnited+States&entry=gmail&source=g>
> Suite 204
> Lenexa, KS 66219
> United States
>
>
>
>
>
> *From:* Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] *On
> Behalf Of *Jing Hong via Equest-users
> *Sent:* Tuesday, March 27, 2018 3:55 PM
> *To:* jra_sac at yahoo.com
> *Cc:* equest-users at lists.onebuilding.org; equest-users at onebuilding.org
> *Subject:* Re: [Equest-users] How to set thermostat to have 0 heating load
>
>
>
> Sure, I've attached the files. Thank you!
>
>
>
> Jing
>
>
>
> On Tue, Mar 27, 2018 at 3:47 PM, John Aulbach <jra_sac at yahoo.com> wrote:
>
> Would you kindly send your .inp and .PD2 so we in the forum might see what
> is happening?
>
> Sent from Yahoo Mail on Android
> <https://overview.mail.yahoo.com/mobile/?.src=Android>
>
>
>
> On Tue, Mar 27, 2018 at 1:20 PM, Jing Hong
>
> <hongjing.shirley at gmail.com> wrote:
>
> Hi John,
>
>
>
> After removing the whole heating thermostat schedule, the program still
> shows space heat. Do you know if eQuest allow users to trace back the space
> heat & cool for each zone?
>
>
>
> Thank you,
>
>
>
> Jing
>
>
>
> On Tue, Mar 27, 2018 at 2:35 PM, John Aulbach <jra_sac at yahoo.com> wrote:
>
> I believe if you remove the heating thermostat schedule, the program will
> show no heating.
>
>
>
> John R. Aulbach, PE
>
>
>
> On Tuesday, March 27, 2018, 8:13:01 AM PDT, Jing Hong via Equest-users <equest-users at lists.
> onebuilding.org <equest-users at lists.onebuilding.org>> wrote:
>
>
>
>
>
> Dear All,
>
>
>
> I am modeling a baseline system 10 Heating and Ventilation. But actually I
> do not need heating but only ventilation. So I set the thermostat schedule
> and design temperature to 40F to avoid heating load. However, I still got
> space heat at the report. Have any of you run into this problem before?
> How to solve it?
>
>
>
> Thank you very much!
>
> Jing
>
>
>
> --
>
> PhD Candidate, LEED AP BD+C
>
>
>
> School of Architecture and Urban Planning
>
> University of Wisconsin-Milwaukee
>
>
>
> ______________________________ _________________
> Equest-users mailing list
> http://lists.onebuilding.org/ listinfo.cgi/equest-users- onebuilding.org
> <http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org>
> To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE@
> ONEBUILDING.ORG <EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
>
>
>
>
>
> --
>
> PhD Candidate, LEED AP BD+C
>
>
>
> School of Architecture and Urban Planning
>
> University of Wisconsin-Milwaukee
>
>
>
>
>
>
>
> --
>
> PhD Candidate, LEED AP BD+C
>
>
>
> School of Architecture and Urban Planning
>
> University of Wisconsin-Milwaukee
>
>
>
>
> ______________________________________________________________________
> This email has been scanned by the Symantec Email Security.cloud service.
> ______________________________________________________________________
>
--
PhD Candidate, LEED AP BD+C
School of Architecture and Urban Planning
University of Wisconsin-Milwaukee
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180402/266c3b0e/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 45623 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180402/266c3b0e/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.png
Type: image/png
Size: 20170 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180402/266c3b0e/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 255 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180402/266c3b0e/attachment-0002.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 8477 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180402/266c3b0e/attachment-0003.png>
More information about the Equest-users
mailing list