[Equest-users] Metal frame walls
Bishop, Bill via Equest-users
equest-users at lists.onebuilding.org
Thu Sep 21 11:42:06 PDT 2017
Hi John,
Per ASHRAE 90.1, Table A9.2-2, with R-19 between 6” framing @ 24” O.C., effective R-Value is R-8.6 for the frame/batt layer. Then add the R-Values of the continuous layers to get the assembly R-Value.
Regards,
~Bill
William Bishop, PE, BEMP, BEAP, CEM, LEED AP | Pathfinder Engineers & Architects LLP
Senior Energy Engineer
[cid:image001.jpg at 01D332E7.E5361F80] [cid:image002.jpg at 01D332E7.E5361F80]
134 South Fitzhugh Street Rochester, NY 14608
T: (585) 698-1956 F: (585) 325-6005
bbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com> www.pathfinder-ea.com<http://www.pathfinder-ea.com/>
[http://png-5.findicons.com/files/icons/977/rrze/720/globe.png]Carbon Fee and Dividend - simple, effective, and market-based.
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of John Aulbach via Equest-users
Sent: Thursday, September 21, 2017 2:37 PM
To: Equest-users <equest-users at lists.onebuilding.org>
Subject: [Equest-users] Metal frame walls
Hi Gang:
Every once in a while, a model appears.
I have forgotten how to do a metal frame wall with infill batt insulation. The wall is a 2 x 6 @ 24" centers with 6" R-19 insulation. I also know that there is 4 " board insulation continuous across the steel.
Where can i go for the equivalent R-values?
Thanks in advance.
John Aulbach, PE
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170921/e589f22e/attachment-0004.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 1517 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170921/e589f22e/attachment-0008.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 1647 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170921/e589f22e/attachment-0009.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 3859 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170921/e589f22e/attachment-0004.png>
More information about the Equest-users
mailing list