[Equest-users] Issue with floors being offset in Wizard?
Michael Campbell via Equest-users
equest-users at lists.onebuilding.org
Mon Sep 18 12:35:25 PDT 2017
Nick,
Thank you for this detailed response.
This is incredibly helpful and I really appreciate you taking the time to
help me address this issue.
Thanks,
On Mon, Sep 18, 2017 at 2:54 PM, Nicholas Caton <
Nicholas.Caton at schneider-electric.com> wrote:
> This could serve as a helpful guide/reading for others, so I’ve
> re-attached the files for illustration (without edits).
>
>
>
> This is a pretty complex project and I don’t have your familiarity Mike
> with what exactly it’s supposed to look like, so I’m going to make a few
> assumptions to illustrate the approach.
>
>
>
> Assuming your CAD efforts were in tip-top shape prior to importing, I’m
> expect the cause has something to do with a combination of non-uniform
> origin points during the dwg import dialog (I can’t review/edit these
> without the files)… or perhaps accidental CAD panning during
> footprint/zoning vertex definitions. Regardless, I’m moving away from the
> cause in order to highlight a solution.
>
>
>
> I’m going to assume for this demo that the 4th shell, which seems in
> “in-alignment” with others, is correct and we just want to shift the two
> shells below it so they perfectly overlay/underlay. I’ve indicated in
> green an axis to which I will demonstrate shifting the 3rd and 2nd shell
> onto:
>
> Note this procedure to determine the necessary shell position input
> corrections can be done at any time during or after wizard stage
> development, but the actual edits are “detailed” level so will need to be
> applied post-wizards:
>
>
>
> First I’ll navigate to wizards open up the *3rd shell (“1st Floor”)*
> custom footprint screen. We want this to shift a moderate amount to align
> with the *4th shell (“2nd Floor”)*. Draw attentions to the drop down
> dialog for background overlays:
>
> (quick aside: If you don’t fill in a shell’s footprint
> with zones, you’ll find the wizards generate adiabatic walls in lieu of
> exterior surfaces for the “exposed” interior zones. If that isn’t
> intentional, you can adjust the shell’s footprint vertices to align with
> your zone’s perimeters to avoid that issue. This might be deliberate for
> this project, but seems worth pointing out for everyone’s general
> edification.)
>
>
>
> If I select the “2nd Floor” shell in this dialog, I can observe 2
> vertices I’d like to align. Note the “correct” 2nd floor is illustrated
> with blue lines and has vertices you can snap to, but aren’t selectable for
> editing:
>
> Note the active (Cyan-colored) vertex.
>
>
>
> From this view, with polygon snapping turned on, you can create a new
> vertex from the highlighted point, and drag it to where you want that point
> to be on the overlaid shell footprint. The information in the bottom of
> the Custom Building Footprint window will tell you exactly what that
> vertex’s shift is in X/Y dimensions:
>
> Jot this information down in your physical/electronic notepad for
> reference.* E3 Shift: dX = 2.1 , dY = -5.7*
>
>
>
> Rinse and repeat with the *2nd Shell (“Basement”)*, again overlaying the
> “correct” *4th shell (“2nd Floor”)*:
>
>
>
> This case is a little more extreme. *E2 Shift: dX = 23.5 and dY = 1.8*
>
>
>
> Armed with this info, we can confidently finish our efforts in the wizards
> and enter the detailed mode. From here, you can edit the FLOOR inputs for
> X and Y by the noted deltas:
>
> *E2 Shift: dX = 23.5 and dY = 1.8*
>
> *E3 Shift: dX = 2.1 , dY = -5.7*
>
> Example:
>
> Entering these edits as expressions as illustrated allows you to retain
> what the wizards generated and document / avoid human-error with your
> algebra if that’s of interest, but it isn’t necessary.
>
>
>
> Finally, check your work in 3D view – looks pretty okay!
>
>
>
> Hope this helps!
>
>
>
> ~Nick
>
>
>
> *Nick Caton, P.E., BEMP*
>
> Senior Energy Engineer
> Regional Energy Engineering Manager
>
> Energy and Sustainability Services
> Schneider Electric
>
> D 913.564.6361 <(913)%20564-6361>
> M 785.410.3317 <(785)%20410-3317>
> F 913.564.6380 <(913)%20564-6380>
> E nicholas.caton at schneider-electric.com
>
> 15200 Santa Fe Trail Drive
> <https://maps.google.com/?q=15200+Santa+Fe+Trail+Drive+%0D+Suite+204+%0D+Lenexa,+KS+66219+%0D+United+States&entry=gmail&source=g>
> Suite 204
> Lenexa, KS 66219
> United States
>
>
>
>
>
> *From:* Michael Campbell [mailto:mcamp1206 at gmail.com]
> *Sent:* Monday, September 18, 2017 10:05 AM
> *To:* Nicholas Caton <Nicholas.Caton at schneider-electric.com>
> *Cc:* equest-users at lists.onebuilding.org
> *Subject:* Re: [Equest-users] Issue with floors being offset in Wizard?
>
>
>
> Thanks for the response, Nick.
>
> Unfortunately I still seem to be having some issues.
>
> I've done many models in the past and have never had this issue, so I'm
> really having a hard time figuring out what is going on.
>
> Would someone be able to take a look at the attached files and see if you
> can provide any insight on how to get these floors to properly align?
>
> I've been trying to move each shell based on aligning common points
> between shells, but that isn't working the way I would hope.
>
> Any help is appreciated.
>
> Thank you,
>
>
>
> On Fri, Sep 15, 2017 at 9:46 AM, Nicholas Caton <Nicholas.Caton at schneider-
> electric.com> wrote:
>
> I’m sure there are multiple good approaches, but the one that works for me
> when I have fairly complex shell layouts is to do the following:
>
> 1. Before starting geometries in the wizards, make sure all your CAD
> references for multi-level buildings are origin-aligned. If you were to
> copy one onto another using the origin as a reference point, the plans
> should should properly align.
> 2. After the first shell, be sure to specify the following in the
> first screen for every subsequent shell:
>
>
> 1. Position this shell: via Coordinates
> 2. Tick the box for Exact Site Coordinates
> 3. Leave X and Y at 0.0 (matching the first shell’s default)
> 4. Provide a Z value as needed to ensure the shell is the right
> height from the ground. Note that below grade floors for a given shell’s
> Z-coordinate will extend downward from that elevation.
>
>
>
> 1. It’s never a bad idea to finish the wizards just to check your work
> in the 3D view - you can always hop back in to make corrections!
>
>
>
> For reference, in the event you’re ever well into detailed edits, and wish
> you made a different decision, these inputs are basically replicated as
> FLOOR geometries. You can adjust/tweak them here and observe the results
> in the 3D view dynamically:
>
>
>
> I suspect that because you have an “alignment” step within the wizards,
> you might not have your CAD files pre-aligned as I’m recommending above.
> If you already have a bunch of zones traced out I’d recommend just tweaking
> the floor’s X/Y coordinates post-wizards until it looks about right. You
> could overlay your CAD files outside of eQuest to inform exactly how much
> of a shift is needed.
>
>
>
> Hope that’s a bit helpful!
>
>
>
> ~Nick
>
>
>
> *Nick Caton, P.E., BEMP*
>
> Senior Energy Engineer
> Regional Energy Engineering Manager
>
> Energy and Sustainability Services
> Schneider Electric
>
> D 913.564.6361 <(913)%20564-6361>
> M 785.410.3317 <(785)%20410-3317>
> F 913.564.6380 <(913)%20564-6380>
> E nicholas.caton at schneider-electric.com
>
> 15200 Santa Fe Trail Drive
> <https://maps.google.com/?q=15200+Santa+Fe+Trail+Drive+%0D+Suite+204+%0D+Lenexa,+KS+66219+%0D+United+States&entry=gmail&source=g>
> Suite 204
> Lenexa, KS 66219
> United States
>
>
>
>
>
> *From:* Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] *On
> Behalf Of *Michael Campbell via Equest-users
> *Sent:* Thursday, September 14, 2017 10:17 AM
> *To:* equest-users <equest-users at lists.onebuilding.org>
> *Subject:* [Equest-users] Issue with floors being offset in Wizard?
>
>
>
> Hello eQUEST Users,
>
> I'm having an issue right now when drawing in the Wizard.
>
> I am working on a multi-story building and I am trying to line each floor
> up correctly when drawing the shells.
>
> I have selected to draw the floor directly above, and I align the CAD file
> with the background as it should be.
>
> However, when moving on to the Detailed Mode, the floors are offset and I
> cannot get them back to the way they were.
>
> Has anyone had this issue or know of a potential solution?
>
> Thank you,
>
> Mike Campbell
>
>
> ______________________________________________________________________
> This email has been scanned by the Symantec Email Security.cloud service.
> ______________________________________________________________________
>
>
>
>
> ______________________________________________________________________
> This email has been scanned by the Symantec Email Security.cloud service.
> ______________________________________________________________________
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170918/69461c89/attachment-0004.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.png
Type: image/png
Size: 32286 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170918/69461c89/attachment-0044.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image011.png
Type: image/png
Size: 168256 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170918/69461c89/attachment-0045.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image006.png
Type: image/png
Size: 8477 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170918/69461c89/attachment-0046.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image008.png
Type: image/png
Size: 98507 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170918/69461c89/attachment-0047.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 102183 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170918/69461c89/attachment-0048.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 112197 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170918/69461c89/attachment-0049.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image007.png
Type: image/png
Size: 62474 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170918/69461c89/attachment-0050.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image009.png
Type: image/png
Size: 38092 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170918/69461c89/attachment-0051.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 51550 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170918/69461c89/attachment-0052.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image010.png
Type: image/png
Size: 46592 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170918/69461c89/attachment-0053.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.png
Type: image/png
Size: 255 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170918/69461c89/attachment-0054.png>
More information about the Equest-users
mailing list