[Equest-users] Glass Library Question
Bishop, Bill via Equest-users
equest-users at lists.onebuilding.org
Fri Sep 8 08:37:39 PDT 2017
Sounds like we could benefit from an updated DOE-2 window library based on Bruce’s observations.
As to the meaning of “e3=.4”, per Table 7 in the DOE-2 help entry for “WINDOW Library”:
Low-E:
A low emissivity metallic coating is applied in order to increase thermal IR reflectance. The coated surface is indicated by en = v, where n = 1 is the outside of the outer pane, n = 2 is the inside of the outer pane, etc., and v is the emissivity (see, for example, G-T-C = 2635, where e2 = 0.1 indicates a coating with an emissivity of 0.1 on surface #2).
So, “e3=.4” describes an assembly with a low-e coating of emissivity 0.4 on the inside surface of the inner pane.
Syracuse Glass has a good list of considerations for low-e coatings and whether to have them on the #2 or #3 surface. Generally, coat the #3 surface if heat loss is the primary consideration, and the #2 surface to limit solar heat gains.
http://www.syracuseglass.com/E-DOCS/Insulating%20Glass/EDOCS/LOW-E%20Coating%20Orientation.pdf
Regards,
~Bill
William Bishop, PE, BEMP, BEAP, CEM, LEED AP | Pathfinder Engineers & Architects LLP
Senior Energy Engineer
[cid:image002.jpg at 01D32896.FC4F3090] [cid:image004.jpg at 01D32896.FC4F3090]
134 South Fitzhugh Street Rochester, NY 14608
T: (585) 698-1956 F: (585) 325-6005
bbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com> www.pathfinder-ea.com<http://www.pathfinder-ea.com/>
[http://png-5.findicons.com/files/icons/977/rrze/720/globe.png]Carbon Fee and Dividend - simple, effective, and market-based.
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Bruce Easterbrook via Equest-users
Sent: Friday, September 08, 2017 11:19 AM
To: Paul Diglio <paul.diglio at sbcglobal.net>; Equest-users <equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] Glass Library Question
Hi Paul,
http://doe2.com/download/DOE-22/DOE22Vol4-Libraries_47.pdf, go further down to page 27 or page 33 on the pdf numbering. The last paragraph explains that the coatings on the different glass surfaces have complicated the library. I assume the e?.? is the new attempt to keep track of the different coatings and also which glass surface they are on.
You are in the emissivity table. The table above is the reflective glazing and below is electrochromic glazing. With a thermopane there are 4 glass surfaces and the new windows can have all 3 of these types of coatings and more in a single unit.
I suspect you can find the actual meanings here: https://windows.lbl.gov/software/window/6/W63_faq.html or https://windows.lbl.gov/
Glass has got very complex in the last few years and those charts represent products sold in mid 2006. Our new code asks for much better performance than these glass types are capable of. The best of these represented a window ER of 18 to 20. Our code wanted 25. Some of the new windows are getting up to an ER of 30 for a thermopane. That huge bump is almost all due to coatings and their arrangement.
Bruce Easterbrook P.Eng.
Abode Engineering
On 9/8/2017 8:59 AM, Paul Diglio via Equest-users wrote:
In the DOE-2 glass library I am looking at the double low-e (e3=.4) clear product, glass type code 2600.
Does anyone know what the e3=.4 means? There are other products, such as type 2630 with e2=.1 with a much different assembly u-value.
Thank you,
Paul Diglio
87 Fairmont Avenue
New Haven, CT 06513
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170908/0ffa09e8/attachment-0004.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 1517 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170908/0ffa09e8/attachment-0008.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.jpg
Type: image/jpeg
Size: 1647 bytes
Desc: image004.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170908/0ffa09e8/attachment-0009.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image006.png
Type: image/png
Size: 3862 bytes
Desc: image006.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170908/0ffa09e8/attachment-0004.png>
More information about the Equest-users
mailing list