I have used the BDL code below to reference the SPACE input indicated to control a ZONE input for Exhaust Air. You could code the 'Activity Description' for the AHU served by it. Just a thought.
switch(#LR("SPACE","C-ACTIVITY-DESC"))
CASE "Rest": (#LR("SPACE","AREA"))/4
CASE "Break": (#LR("SPACE","AREA"))/2
CASE "REle": (#LR("SPACE","AREA"))
CASE "Elec": (#LR("SPACE","AREA"))/2
CASE "Jani": (#LR("SPACE","AREA"))/2
CASE "Mech": (#LR("SPACE","AREA"))/2
default: no_def
endswitch
[ARCH | NEXUS]<http://www.archnexus.com>
DAVID W. GRIFFIN II
BEMP
ENERGY ANALYST
2505 E Parleys Way
Salt Lake City, UT 84109
Office 801.924.5028
archnexus.com<http://www.archnexus.com>
[Twitter]<https://twitter.com/arch_nexus>[Facebook]<https://www.facebook.com/pages/Architectural-Nexus/179588705397563?ref=ts&fref=ts>[Youtube]<https://www.youtube.com/channel/UCYRPWKF-yp-AUiI8ia2XfKw?feature=mhee>[LinkedIn]<https://www.linkedin.com/company/architectural-nexus>
From: Jennings, Coles [mailto:Coles.Jennings at MasonandHanger.com]
Sent: Monday, November 13, 2017 9:03 AM
To: Bishop, Bill; equest-users at onebuilding.org
Subject: Re: [Equest-users] Advanced Scripting/Custom Default Question - Change Space Property based on System?
Thanks Bill, that makes sense. Unfortunately there is no clean relationship between floors and systems, but I think adding a system number prefix to the space description as you suggest will still provide some time savings. Very much appreciate your feedback.
Coles Jennings PE, BEMP, LEED AP BD+C
Sr. Energy Engineer, Building Sciences Manager | Mason & Hanger
A Day & Zimmermann Company
D 804.521.7045 | O 804.285.4171 | F 804.217.8520
4880 Sadler Road, Suite 300 | Glen Allen, VA 23060
Mason & Hanger<http://www.masonandhanger.com/>
We do what we say.(r)
From: Bishop, Bill [mailto:bbishop at pathfinder-ea.com]
Sent: Monday, November 13, 2017 10:58 AM
To: Jennings, Coles <Coles.Jennings at MasonandHanger.com<mailto:Coles.Jennings at MasonandHanger.com>>; equest-users at onebuilding.org<mailto:equest-users at onebuilding.org>
Subject: [EXTERNAL] RE: Advanced Scripting/Custom Default Question - Change Space Property based on System?
Hi Coles,
Spaces are defined in the BDL before systems and zones. Systems are neither parents nor children of spaces, so there is no way for spaces to reference them.
You could reference the floors of the spaces if there is a relationship of systems to floors.
What you could do is include the name of the system in the space description (C-ACTIVITY-DESC) and then reference the space description with a SWITCH statement.
Regards,
~Bill
William Bishop, PE, BEMP, BEAP, CEM, LEED AP | Pathfinder Engineers & Architects LLP
Senior Energy Engineer
[cid:image001.jpg at 01D35C95.9BAC7710] [cid:image002.jpg at 01D35C95.9BAC7710]
134 South Fitzhugh Street Rochester, NY 14608
T: (585) 698-1956 F: (585) 325-6005
bbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com> www.pathfinder-ea.com<https://urldefense.proofpoint.com/v2/url?u=http-3A__www.pathfinder-2Dea.com_&d=DwMFAg&c=xB5UQg5qXm2axe_t44neldV-XNditz6D2ZXZLA0vHlE&r=JrIPsTq2z-_669uhqn51VqSZFL7dpX6NqxKBTKpeQZ9m5XksAJHnQhCI_rEcbMFG&m=TPsuZzXb-d5_oj4vRDGXNr4Cblc5UDBybdEMWc2uwqQ&s=Ne5ZL4_R7KA8Un8Gr9yDAMK13olbWcBrcz3BBi-1iKw&e=>
[http://png-5.findicons.com/files/icons/977/rrze/720/globe.png]Carbon Fee and Dividend - simple, effective, and market-based.
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Jennings, Coles via Equest-users
Sent: Sunday, November 12, 2017 8:28 PM
To: equest-users at onebuilding.org<mailto:equest-users at onebuilding.org>
Subject: [Equest-users] Advanced Scripting/Custom Default Question - Change Space Property based on System?
Hello all,
I'm modeling a hospital building with some areas that are 24/7 and others that are on a typical 8-5 M-F schedule. There are numerous AHUs and each AHU operates on one of these two schedules. What I'd like to do is write a default script that sets the space interior load schedules (lighting, occupancy, equipment) based on which AHU that space's thermal zone is assigned to.
I often use the trick of assigning a unique min. humidity ratio for each system in a model and then writing a switch() script to change zone properties, but I am having trouble figuring out the syntax to use this trick to change space properties. There's something in the BDL hierarchy that I'm not getting.
Has anyone had success with this before?
Thanks,
Coles Jennings PE, BEMP, LEED AP BD+C
Sr. Energy Engineer, Building Sciences Manager | Mason & Hanger
A Day & Zimmermann Company
D 804.521.7045 | O 804.285.4171 | F 804.217.8520
4880 Sadler Road, Suite 300 | Glen Allen, VA 23060
Mason & Hanger<http://www.masonandhanger.com/>
We do what we say.(r)
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20171113/edcae68b/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 1242 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20171113/edcae68b/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 1308 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20171113/edcae68b/attachment-0001.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 2842 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20171113/edcae68b/attachment.png>
More information about the Equest-users
mailing list