[Equest-users] SV-A: Discrepancy between system OA rate and sum of zone OA rates
Bishop, Bill
bbishop at pathfinder-ea.com
Fri Nov 3 12:10:29 PDT 2017
Hi Darryl,
From your SV-A report, if you sum the zone outside air flows, then add the zone exhaust flows, and divide by the supply cfm, you get the OA ratio of 0.223.
Hope that helps.
Also, I think I need bifocals.
Regards,
~Bill
William Bishop, PE, BEMP, BEAP, CEM, LEED AP | Pathfinder Engineers & Architects LLP
Senior Energy Engineer
[cid:image013.jpg at 01D354B6.03B6A980] [cid:image014.jpg at 01D354B6.03B6A980]
134 South Fitzhugh Street Rochester, NY 14608
T: (585) 698-1956 F: (585) 325-6005
bbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com> www.pathfinder-ea.com<http://www.pathfinder-ea.com/>
[http://png-5.findicons.com/files/icons/977/rrze/720/globe.png]Carbon Fee and Dividend - simple, effective, and market-based.
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Darryl Kasun via Equest-users
Sent: Friday, November 03, 2017 2:38 PM
To: equest <equest-users at lists.onebuilding.org>
Subject: [Equest-users] SV-A: Discrepancy between system OA rate and sum of zone OA rates
Good day everyone,
When I review the SV-A report for a PVAVS, there is a discrepancy between the OA rate at the system level and the sum of the zone OA rates and I'm not sure why. Hoping someone can help me out.
Here's the SV-A report:
[Inline image 1]
The OUTSIDE-AIR-FLOW was entered for each zone. No other OA inputs were entered at the zone level.
At the system level, below shows some of the OA inputs:
[Inline image 3]
And here's the MinOA Sch:
[Inline image 4]
Any help would be appreciated!
Thanks
Darryl
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20171103/5c039535/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image013.jpg
Type: image/jpeg
Size: 1517 bytes
Desc: image013.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20171103/5c039535/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image014.jpg
Type: image/jpeg
Size: 1647 bytes
Desc: image014.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20171103/5c039535/attachment-0001.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image015.png
Type: image/png
Size: 3856 bytes
Desc: image015.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20171103/5c039535/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image016.png
Type: image/png
Size: 232646 bytes
Desc: image016.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20171103/5c039535/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image017.png
Type: image/png
Size: 75459 bytes
Desc: image017.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20171103/5c039535/attachment-0002.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image018.png
Type: image/png
Size: 85157 bytes
Desc: image018.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20171103/5c039535/attachment-0003.png>
More information about the Equest-users
mailing list