[Equest-users] Advanced Scripting/Custom Default Question - Change Space Property based on System?
    Bishop, Bill 
    bbishop at pathfinder-ea.com
       
    Mon Nov 13 07:58:00 PST 2017
    
    
  
Hi Coles,
Spaces are defined in the BDL before systems and zones. Systems are neither parents nor children of spaces, so there is no way for spaces to reference them.
You could reference the floors of the spaces if there is a relationship of systems to floors.
What you could do is include the name of the system in the space description (C-ACTIVITY-DESC) and then reference the space description with a SWITCH statement.
Regards,
~Bill
William Bishop, PE, BEMP, BEAP, CEM, LEED AP | Pathfinder Engineers & Architects LLP
Senior Energy Engineer
[cid:image007.jpg at 01D35C6E.641F09B0]  [cid:image008.jpg at 01D35C6E.641F09B0]
134 South Fitzhugh Street                 Rochester, NY 14608
T: (585) 698-1956                        F: (585) 325-6005
bbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com>             www.pathfinder-ea.com<http://www.pathfinder-ea.com/>
[http://png-5.findicons.com/files/icons/977/rrze/720/globe.png]Carbon Fee and Dividend - simple, effective, and market-based.
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Jennings, Coles via Equest-users
Sent: Sunday, November 12, 2017 8:28 PM
To: equest-users at onebuilding.org
Subject: [Equest-users] Advanced Scripting/Custom Default Question - Change Space Property based on System?
Hello all,
I'm modeling a hospital building with some areas that are 24/7 and others that are on a typical 8-5 M-F schedule. There are numerous AHUs and each AHU operates on one of these two schedules. What I'd like to do is write a default script that sets the space interior load schedules (lighting, occupancy, equipment) based on which AHU that space's thermal zone is assigned to.
I often use the trick of assigning a unique min. humidity ratio for each system in a model and then writing a switch() script to change zone properties, but I am having trouble figuring out the syntax to use this trick to change space properties. There's something in the BDL hierarchy that I'm not getting.
Has anyone had success with this before?
Thanks,
Coles Jennings PE, BEMP, LEED AP BD+C
Sr. Energy Engineer, Building Sciences Manager | Mason & Hanger
A Day & Zimmermann Company
D 804.521.7045 | O 804.285.4171 | F 804.217.8520
4880 Sadler Road, Suite 300 | Glen Allen, VA 23060
Mason & Hanger<http://www.masonandhanger.com/>
We do what we say.(r)
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20171113/2c36bd19/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image007.jpg
Type: image/jpeg
Size: 1517 bytes
Desc: image007.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20171113/2c36bd19/attachment-0008.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image008.jpg
Type: image/jpeg
Size: 1647 bytes
Desc: image008.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20171113/2c36bd19/attachment-0009.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image009.png
Type: image/png
Size: 3859 bytes
Desc: image009.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20171113/2c36bd19/attachment-0004.png>
    
    
More information about the Equest-users
mailing list