equest-users at lists.onebuilding.org
Wed May 17 00:20:51 PDT 2017
Hi
I had a similar case : I have declared an electric boiler and a cooling tower on the WL, and add meters for post processing hourly results.
1 meter “net hourly loop load” OR 2 meters “assigned load” on each source
Hope that helps
Carole LEHMANN
Ingénieur – Chargée d’étude
Pôle Simulation
ALTO Ingénierie
66, cours Charlemagne
69002 Lyon
Tel +33 4 72 82 86 88
www.alto-ingenierie.fr
De : Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] De la part de Daric Adair via Equest-users
Envoyé : mardi 16 mai 2017 22:38
À : equest-users at lists.onebuilding.org
Objet : [Equest-users] eQuest 3.65 - WLHP with Meters
All;
I have a configuration where I will have WSHP’s – but the loop will be tempered with a Landlord/utility Steam and Condenser Water System. According to the help files I should be able to assign a Steam meter to a WLHP Loop…but that isn’t being allowed? Any ideas why?
Second Issue is that Condenser Water Meter isn’t a thing. So, my thought is to use a Heat Rejection Tower with a flat response Curve, assigned to its own utility rate, and tune from there. Does anyone have any alternatives or other ideas? Any help appreciated.
Thanks,
DARIC R. ADAIR PE, C.E.M.
Mechanical Engineer, Energy Analyst
Henderson Engineers, Inc.
8345 Lenexa Drive, Suite 300 Lenexa, KS 66214
dir 913 742 5530 tel 913 742 5000 fax 913 742 5001 tx id #F-001236 www.hei-eng.com
Licensed in KS.
Sending me large files? Please use my HEI DropBox
This email and any files transmitted with it are confidential and are intended solely for the use of the individual or entity to whom they are addressed. This communication represents the originator's personal views and opinions, which do not necessarily reflect those of Henderson Engineers, Inc. If you are not the original recipient or the person responsible for delivering the email to the intended recipient, be advised that you have received this email in error, and that any use, dissemination, forwarding, printing, or copying of this email is strictly prohibited. If you received this email in error, please immediately notify administrator at hei-eng.com.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170517/2913ff55/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image010.gif
Type: image/gif
Size: 198 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170517/2913ff55/attachment-0008.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image009.gif
Type: image/gif
Size: 177 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170517/2913ff55/attachment-0009.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image008.gif
Type: image/gif
Size: 192 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170517/2913ff55/attachment-0010.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image007.gif
Type: image/gif
Size: 5566 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170517/2913ff55/attachment-0011.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image006.png
Type: image/png
Size: 2947 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170517/2913ff55/attachment-0004.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.png
Type: image/png
Size: 6003 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170517/2913ff55/attachment-0005.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 33285 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170517/2913ff55/attachment-0008.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 39275 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170517/2913ff55/attachment-0009.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 31232 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170517/2913ff55/attachment-0010.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 26473 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170517/2913ff55/attachment-0011.jpeg>
More information about the Equest-users
mailing list