[Equest-users] ASHRAE Bldg_Modeling Comparisons
Jones, Christopher via Equest-users
equest-users at lists.onebuilding.org
Tue May 9 06:04:21 PDT 2017
Perhaps the discrepancy stems from the use of SIZING-OPTION in the eQuest model. This keyword is used in the SYSTEM and the ZONE definitions. It may be worth reading the DOE22 Dictionary manual for clarification.
Attached is an interesting paper comparing how the some of the different simulation programs calculate solar loads.
[cid:image001.jpg at 01D2A6E9.840756F0]
Christopher R. Jones, P.Eng.
Technical Specialist
WSP Canada Inc.
2300 Yonge Street, Suite 2300
Toronto, ON M4P 1E4 Canada
T +1 416-644-0252
www.wspgroup.ca<http://www.wspgroup.ca/>
Please consider the environment before printing...
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Mike Schaefer via Equest-users
Sent: Tuesday, May 09, 2017 8:54 AM
To: Annie Marston via Equest-users <equest-users at lists.onebuilding.org>
Subject: [Equest-users] ASHRAE Bldg_Modeling Comparisons
Per user comments from my previous post, below, I've included my model's input and sim files.
David Eldridge, I appreciate your input and I'm checking my loads per your comments.
I'm running an office building with three different energy programs (Trane Trace, Carrier HAP, and DOE's eQUEST to compare and contrast each energy modeling programs output. Two of my programs Trane Trace and Carrier HAP have similar rooftop unit sizing, however, my eQUEST model is producing rooftop unit sizes (RTU-1 & RTU-2) that greatly exceeds the other two programs. I believe that this difference is the ventilation load. CFM's and building sensible loads are similar, however. There is a large discrepancy between the total cooling capacity (defined by "cooling capacity" in eQUEST's SV-A reports. My eQuest model is reporting a much higher than expected total "Cooling Capacity" for my rooftop units. All models have two VAV rooftop units (one for each floor of a two story office building). The ventilation rates, internal loads and envelope are identical between my models. The models have air side economizers w/integrated dry bulb with an upper cutoff of 75 deg. F with the non-economizer outside air turned off during unoccupied hours. All programs are using KC, MO TMY2 weather data.
Can anyone explain, or find my error, in the eQUEST modeling that is causing the unusual load in ventilation? It seems obvious that the three programs would produce similar outputs, however, there must be an eQUEST modeling error that I've created.
Also, does eQUEST have a load breakdown that describes (lists) the values that make-up the "SV-A cooling capacity"?
I've attached the Carrier RTU-1 (1st floor office load) system report and the eQUEST model.
Thanks,
Michael Schaefer - P.E.*, LEED AP
Licensed in Kansas, Missouri, and Colorado
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170509/62b128e9/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 1510 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170509/62b128e9/attachment-0002.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: SB10-DOC-TS04A-01-Kasarekar.pdf
Type: application/pdf
Size: 1480535 bytes
Desc: SB10-DOC-TS04A-01-Kasarekar.pdf
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170509/62b128e9/attachment-0002.pdf>
More information about the Equest-users
mailing list