[Equest-users] ASHRAE 90.1 ERV 50% energy recovery effectiveness - eQUEST inputs?
Keith Swartz via Equest-users
equest-users at lists.onebuilding.org
Mon May 22 06:39:12 PDT 2017
Bill,
For all practical purposes, I also simply set the sensible and latent effectivenesses to 50%. If your energy model will get thorough scrutiny, you may want to use Equation 6-K in the User's Manual, 2013 edition.
Keith Swartz, PE | Senior Energy Engineer
Seventhwave
608.210.7123 seventhwave.org
From: Lapierre, Patrick via Equest-users [mailto:equest-users at lists.onebuilding.org]
Sent: Thursday, May 18, 2017 11:57 AM
To: Bishop, Bill <bbishop at pathfinder-ea.com>
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] ASHRAE 90.1 ERV 50% energy recovery effectiveness - eQUEST inputs?
It is my interpretation as well and what I always do.
[Bouthillette Parizeau]<http://www.bpa.ca/>
Patrick Lapierre_ing. BEMP
plapierre at bpa.ca<mailto:plapierre at bpa.ca> | t: 5143833747x2807
De : Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] De la part de Bishop, Bill via Equest-users
Envoyé : 18 mai 2017 12:53
À : equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Objet : [Equest-users] ASHRAE 90.1 ERV 50% energy recovery effectiveness - eQUEST inputs?
I'd appreciate some sensible guidance. Please don't dampen my spirits...
Section 6.5.6.1 describes that required energy recovery systems (ERVs) "shall have at least 50% energy recovery effectiveness", meaning "a change in enthalpy of the outdoor air supply equal to 50% of the difference between the outdoor air and return air enthalpies at design conditions".
My reaction is to model this by setting both the sensible and latent effectiveness (ERV-SENSIBLE-EFF and ERV-LATENT-EFF) to 50% (0.50).
Is this correct?
Ye be thanked,
~Bill
William Bishop, PE, BEMP, BEAP, CEM, LEED AP | Pathfinder Engineers & Architects LLP
Senior Energy Engineer
[cid:image007.jpg at 01D2D2D6.09E850E0] [cid:image009.jpg at 01D2D2D6.09E850E0]
134 South Fitzhugh Street Rochester, NY 14608
T: (585) 698-1956 F: (585) 325-6005
bbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com> www.pathfinder-ea.com<http://www.pathfinder-ea.com/>
[http://png-5.findicons.com/files/icons/977/rrze/720/globe.png]Carbon Fee and Dividend - simple, effective, and market-based.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170522/39143e5e/attachment-0004.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.jpg
Type: image/jpeg
Size: 988 bytes
Desc: image005.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170522/39143e5e/attachment-0015.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image007.jpg
Type: image/jpeg
Size: 1254 bytes
Desc: image007.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170522/39143e5e/attachment-0016.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image009.jpg
Type: image/jpeg
Size: 1326 bytes
Desc: image009.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170522/39143e5e/attachment-0017.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image011.png
Type: image/png
Size: 2847 bytes
Desc: image011.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170522/39143e5e/attachment-0005.png>
More information about the Equest-users
mailing list