[Equest-users] Wall insulation in multifamily buildings
Maria Karpman via Equest-users
equest-users at lists.onebuilding.org
Thu Mar 16 07:09:57 PDT 2017
Good point Nathan – it makes sense that population density should trump
other factors. Even if low flow showers and faucets run 24/7, they can only
deliver so much hot water. It’s a good idea to check equivalent full load
hours (EFLH) of water heaters on projects with high usage and savings
associated with that end use (e.g. multifamily, gyms, dormitories). We
sometimes see models with EFLH way over 8760 hrs/yr based on the capacity
of the specified units J. I do think operating assumptions should be
prescribed for the compliance modeling to close loopholes, and also to help
modelers use inputs that are a better fit for their projects, with
understanding that these are just best guess estimates, and that the actual
post-occupancy usage will be different.
I missed Joe’s post from yesterday - it's funny that Chinese want 1 ACH of
their famously fresh outdoor air inside residential units J. And I like
your "modeling by intent" term. It will come handy when discussing
ventilation/infiltration matters, because between mechanical and energy
code, US air is regulated to the teeth, and modeling by intent is the
standard practice J.
Nathan, you wrote “When we do the envelope sensitivity analysis on high
rise multifamily projects … the glazing percentage isn’t as bad a penalty
…. with a WSHP system serving residences. If it is more of a traditional
hydronic job, that penalty seems to go up a little….” I would normally
expect an opposite trend. There was a nice article on that in ASHRAE
Journal (HVAC Selection for Envelope-Dominated Buildings
<https://www.noexperiencenecessarybook.com/rQOYL/hvac-selection-for-envelope-dominated-buildings.html>).
The outcome for a particular project would depend on the units used to
express the penalty (site energy, source energy, or energy cost), and
efficiencies of WSHPs, boilers, pumps, fans, etc. But since the original
question in this thread was for a project in NJ that may be participating
in EPA HRMF EStar program, we commonly see a lower $ penalty from high WWR
for hydronic system (w/condensing boiler and HW baseboards) versus WSHP. Or
to rephrase, the hydronic system is typically more efficient than WSHP, and
is thus more forgiving to envelope deficiencies.
*From:* Nathan Miller [mailto:nathanm at rushingco.com]
*Sent:* Thursday, March 16, 2017 9:24 AM
*To:* Nicholas Caton <Nicholas.Caton at schneider-electric.com>; Maria Karpman
<maria.karpman at karpmanconsulting.net>; Chris Jones <
Christopher.Jones at rwdi.com>; David Griffin II <DGriffin at archnexus.com>;
Michael Campbell <mcamp1206 at gmail.com>; Joe Huang <
yjhuang at whiteboxtechnologies.com>
*Cc:* equest-users at onebuilding.org; Krishnan.gowri at autodesk.com
*Subject:* RE: [Equest-users] Wall insulation in multifamily buildings
Ha, this conversation has sort of gone off the rails from the initial
question being asked, but I’ll continue to pile-on as well.
Here is some anecdotal information regarding DHW demand…
Maria pasted in a table that I am familiar with which indicates some
starting-point-assumptions for DHW in multifamily buildings for different
occupancies. Since images don’t show up in the archives, I’ll type a
summary here for posterity:
Demand: Residential Occupancy Type:
Baseline Daily DHW use (gal/occ/day)- Excluding
Clothes/Dishwashers
Low All occupants working, seniors, middle income,
and higher population density 12 gal/day
Medium Mix of working/non-working occupants, mixture of age
groups, medium pop density 25 gal/day
High High % of children, low income, public
assistance, no working
occupants 44 gal/day
The interesting data point I have to compare to this table is the *Seattle
Housing Authority* has provided guidance to design teams working on their
projects (low-income, subsidized, affordable housing multifamily
projects) *that
the actual metered DHW demand from their current generation of buildings is
only about 12-15 gal/occ/day*. And that includes laundry and dishwashing
(often done by hand, not dishwashers). Compare that to the 44 gal/occ/day
you might otherwise assume for this project type per the table.
They have been pretty aggressive in making sure low-flow fixtures are
specified, but other than that it again indicates that any of this national
guidance should be taken with a grain of salt. Their projects do tend to be
very high occupant density, so it suggests that the density variable might
be more important than the occupancy type?
Sincerely,
*Nathan Miller, PE, LEED AP BD+C** – **Mechanical Engineer/Senior Energy
Analyst*
*RUSHING* | *O* 206-285-7100 | *C* 207-650-3942
*www.rushingco.com <http://www.rushingco.com/>*
*From:* Equest-users [mailto:equest-users-bounces at lists.onebuilding.org
<equest-users-bounces at lists.onebuilding.org>] *On Behalf Of *Maria Karpman
via Equest-users
*Sent:* Tuesday, March 14, 2017 11:53 AM
*To:* Nathan Miller <nathanm at rushingco.com>; Chris Jones <
Christopher.Jones at rwdi.com>; David Griffin II <DGriffin at archnexus.com>;
Michael Campbell <mcamp1206 at gmail.com>; Joe Huang <
yjhuang at whiteboxtechnologies.com>
*Cc:* equest-users at onebuilding.org
*Subject:* Re: [Equest-users] Wall insulation in multifamily buildings
To David’s comment about infiltration (“Lower infiltration will save you
more energy than any other envelope ECM.”), there are a few caveats.
a) To document infiltration-related savings in App G models (e.g. for
LEED), the baseline air leakage would be modeled as 0.4 CFM/SF *@ 75Pa*
(90.1 2013 G3.1.1.4). 90.1 2013 Table G further requires that infiltration
inputs in the simulation tool are adjusted to account for factors such as
weather and “…. HVAC system operation….“. 90.1 leaves these adjustments to
the modeler, but PNNL’s Infiltration Modeling Guidelines for Commercial
Building Energy Analysis
<http://citeseerx.ist.psu.edu/viewdoc/download?doi=10.1.1.510.8703&rep=rep1&type=pdf>
mentions in passing (Note 2 on p.6) that “The total building infiltration
schedule fraction will be 1.0 when all heating, ventilation and air
conditioning (HVAC) systems are off and 0.25 when the HVAC systems are in
operation.” (It’s good that they used Energy Plus for the study, so results
must still be accurate in spite of this seemingly arbitrary assumption
J.) Since
HVAC systems are operating 24/7 in multifamily, infiltration schedule in
the baseline and proposed design would have to be set to 0.25 of the peak
if we follow the PNNL study, which very significantly reduces
infiltration-related heating load in the model. (The infiltration load is
shown in LS-F report.) As a side note, with LEED v3 and v4,
infiltration-reduction credit can be claimed via exceptional calculation
methods, or by using LEED pilot credit
<http://www.usgbc.org/credits/new-construction-core-and-shell-schools-new-construction-retail-new-construction-healthc-110>
which is based on 90.1 2016 Appendix G modeling rules with the appropriate
adjustment to performance targets and point scale. (I recommend that you
check out this credit, as it simplifies the baseline model.)
b) Potential savings from infiltration reduction should be considered
in conjunction with the specified ventilation strategy. In North East, it
is overwhelmingly common to have 100% OA units serving multifamily
corridors with no exhaust, and continuously running rooftop exhaust fans
serving kitchens and bathrooms in apartments on one vertical stack with no
make-up. Both supply and exhaust rates are often grossly oversized compared
to the minimum CFM required by code, and since the relevant code
(summarized here
<https://buildingscience.com/sites/default/files/document/ba-1507_ventilation_guidance_final_measure_guideline.pdf>)
requires that apartments are compartmentalized and envelope is air-tight,
it creates an interesting conundrum for air J. Balanced ventilation is
still a rarity in NE even in high performance buildings. Old editions of
ASHRAE Fundamentals had a way of taking into account this dynamics (see
below), which was crude but better than “one size fits all” approach in the
PNNL study. So I’d use ASHRAE’s method in lieu of PNNL’s to model
infiltration savings for LEED, and to decide whether tighter envelope
should be pursued for a given project.
Nathan, thanks for clarifying your plug load observations. Your explanation
makes total sense. On the related note, the latest LEED EAc1 template
includes the following info (based on ASHRAE Applications handbook) for the
impact of occupant demographics on HW usage. Perhaps you can reference this
data (also used in EPA HRMF program) to justify modeling lower plug loads
for certain projects. But I can also see that rating authorities may reject
this logic and insist on using “typical” plug loads in the model,
recognizing that occupant demographics may change over the life of the
building.
*From:* Nathan Miller [mailto:nathanm at rushingco.com]
*Sent:* Tuesday, March 14, 2017 9:38 AM
*To:* Chris Jones <Christopher.Jones at RWDI.com>; David Griffin II <
DGriffin at archnexus.com>; Maria Karpman <maria.karpman at karpmanconsulting.net>;
Michael Campbell <mcamp1206 at gmail.com>; Joe Huang <
yjhuang at whiteboxtechnologies.com>
*Cc:* equest-users at onebuilding.org
*Subject:* RE: [Equest-users] Wall insulation in multifamily buildings
I can’t think of the last high-rise project I worked on that stayed
anywhere near 25% WWR. 40-50% is very much the norm in Seattle (climate
where I do most of my modeling work). Owners want 60%+. Mid-rise resi (and
mixed use), I do tend to see 25-35% WWR as typical.
When we do the envelope sensitivity analysis on high rise multifamily
projects, honestly the glazing percentage isn’t as bad a penalty as you’d
think. Like on the order of 0.1-0.25% energy penalty for each 1% increase
in glazing when we are already in the 40%+ glazing band, meaning we are
comparing extra glazing to opaque wall. This is with a WSHP system serving
residences. If it is more of a traditional hydronic job, that penalty seems
to go up a little, but still isn’t a killer.
Using standard ESMFHRSG plug loads we see the conditioning load of the
buildings driven by internal loads, ventilation, and infiltration, not
envelope. Related to the previous comment in this thread from Maria:
“I am curious about the reasoning behind Nathan’s comment that “… many of
us in the Seattle market are starting to believe the standard plug/misc
load assumptions from the Energy Star MF High Rise Sim Guidelines
overestimate that energy use”. EPA’s plug loads are 4 times lower than
COMNET’s for Multifamily/Residential, and are also lower than the loads in
PNNL High Rise Apartment prototype. Passive house protocols are the only
two sources that I know off that prescribe lower in-unit loads -
Passivehaus Institute (PHI) loads are less than half of EPA’s, and US
passive house off-shoot (PHIUS) loads are 15% lower than EPA’s. In general,
in-unit electricity consumption can vary significantly depending on
occupant demographics (by factor of 10 based on some papers), so both
COMNET and PHI may be correct for *some* apartments. We compared EPA
assumptions to the in-unit electricity usage in several apartment complexes
in NJ, and the numbers were in the right ballpark, so appear to represent
reasonable averages.”
Her comment made me realize I’m suffering a bit from selection-bias. The
projects I tend to model are the newest multifamily projects to hit the
market. These projects in Seattle are almost all studios and 1 BR, with a
few 2 BR and penthouses sprinkled in. They aren’t serving as housing for
families, but more professionally-employed individuals, who don’t cook
much, who probably concentrate their electronics (laptop plus maybe a flat
screen) more than the typical American family, and certainly do less
laundry. Some of the trend on housing design seems to be minimal living
space and more amenities. That is probably why the national averages for
dwelling unit plug loads seem high for THE TYPE OF PROJECTS I WORK ON.
Hope that makes more sense (given some reflection).
*Nathan Miller, PE, LEED AP BD+C** – **Mechanical Engineer/Senior Energy
Analyst*
*RUSHING* | *O* 206-285-7100 | *C* 207-650-3942
*www.rushingco.com <http://www.rushingco.com/>*
*From:* Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] *On
Behalf Of *Chris Jones via Equest-users
*Sent:* Tuesday, March 14, 2017 7:46 AM
*To:* David Griffin II <DGriffin at archnexus.com>; Maria Karpman <
maria.karpman at karpmanconsulting.net>; Michael Campbell <mcamp1206 at gmail.com>;
Joe Huang <yjhuang at whiteboxtechnologies.com>
*Cc:* equest-users at onebuilding.org
*Subject:* Re: [Equest-users] Wall insulation in multifamily buildings
My only comment is that developers and contractors like curtain wall
(window wall for high rise MURBS) because it is less expensive to install
and can be installed in any weather. This may be the main reason we see
glass towers north of the 49th.
[image: Title: RWDI - Description: RWDI logo]
<http://www.rwdi.com/assets/logos/RWDI-logo.gif>
*Christopher Jones, **P.Eng. *| Senior Energy Analyst
*RWDI*
901 King Street West, Suite 400, Toronto, ON M5V 3H5 Canada
Tel: (519) 823-1311 ext 2052
rwdi.com <http://www.rwdi.com/>
*From:* Equest-users [mailto:equest-users-bounces at lists.onebuilding.org
<equest-users-bounces at lists.onebuilding.org>] *On Behalf Of *David Griffin
II via Equest-users
*Sent:* Monday, March 13, 2017 7:46 PM
*To:* Maria Karpman; Michael Campbell; Joe Huang
*Cc:* equest-users at lists.onebuilding.org
*Subject:* Re: [Equest-users] Wall insulation in multifamily buildings
I thought I might chime in on this discussion as well to drive a few points
home.
I have attached a file illustrating a graph to explain Joe’s comment below.
It shows diminishing returns from increased insulation. When it comes to
effective envelope ECMs for projects. I focus on two very important things:
1) Lower infiltration will save you more energy than any other
envelope ECM. However, it is hard to get an owner to buy off on this and
enforce the requirement with the contractor. Typically, an envelope
consultant will be brought in to assist the architect with details,
supervise the contractor during construction, and test the building (or a
portion thereof) to verify performance. You can see how something like this
is hard sell to an owner because it can be a costly process, and if the
building fails the blower door test, the contractor has a $$ issue and the
a lot of rework.
2) Window-to-Wall Ratio (WWR) reduction is great. On the curve
illustrated in the attached file, you essentially replace an expensive
window with a cheaper wall assembly and saving more energy! It’s a true
win-win-win. However, windows exist for more reasons than daylight
controls. Comfort and views are essential for occupants. Some architects
may also argue they are essential for aesthetics as well, so you have to
have a target in mind for the project you are willing to negotiate. On
commercial projects, I generally shoot for 25% WWR.
3) Window upgrades are next since they have the most potential to save
energy on the illustrated curve. Since you tried to minimize the WWR on #2,
this ECM will be cheaper than it would have been otherwise – always saving
the client $$ J This includes glazing and frames.
4) After all three of the above items are addressed, I start to talk
about added insulation in the walls, roof, etc.
Anyway, this is my approach on new construction. Is this what you guys see,
or am I missing something?
Let me know.
[image: Image removed by sender. ARCH | NEXUS] <http://www.archnexus.com>
DAVID W. GRIFFIN II
BEMP
ENERGY ANALYST
2505 E Parleys Way
Salt Lake City, UT 84109
*Office* 801.924.5028
archnexus.com <http://www.archnexus.com>
[image: Image removed by sender. Twitter]
<https://twitter.com/arch_nexus>[image:
Image removed by sender. Facebook]
<https://www.facebook.com/pages/Architectural-Nexus/179588705397563?ref=ts&fref=ts>[image:
Image removed by sender. Youtube]
<https://www.youtube.com/channel/UCYRPWKF-yp-AUiI8ia2XfKw?feature=mhee>[image:
Image removed by sender. LinkedIn]
<https://www.linkedin.com/company/architectural-nexus>
*From:* Maria Karpman via Equest-users [
mailto:equest-users at lists.onebuilding.org
<equest-users at lists.onebuilding.org>]
*Sent:* Friday, March 10, 2017 9:24 PM
*To:* Michael Campbell; Joe Huang
*Cc:* equest-users at lists.onebuilding.org
*Subject:* Re: [Equest-users] Wall insulation in multifamily buildings
Few more thoughts on this:
1) I agree with Joe and David that R-19 “…has already captured most of
the energy losses (or savings) for the wall”. R-19 is better than 90.1 2016
requirements for steel-framed wall in climate zone 4A, and since 90.1
requirements are set taking into account cost effectiveness, it is not
surprising that further improvement does not often pay off.
2) Overwhelming majority of high performance multifamily projects have
efficient heating systems, often condensing boilers or VRF HPs, which
lowers heating costs and potential savings from envelope improvements.
3) Most multifamily projects in North East have gas heating, and gas
is cheap compared to electricity. For example EPA EStar MFHR projects in NY
typically use $0.15/kWh and $1/Therm in performance rating calculations,
which effectively makes BTU of electricity ~4.4 times more expensive than
BTU of gas. This further shrinks contribution of heating toward the total
building energy $, and reduces potential savings from envelope
improvements. (Using source energy instead of $ in performance rating
calculations makes envelope improvements more appealing, because with EPA
PM site-to-source conversions BTU of electricity has only ~ 3 times greater
weight than BTU of gas.)
4) I am curious about the reasoning behind Nathan’s comment that “…
many of us in the Seattle market are starting to believe the standard
plug/misc load assumptions from the Energy Star MF High Rise Sim Guidelines
overestimate that energy use”. EPA’s plug loads are 4 times lower than
COMNET’s for Multifamily/Residential, and are also lower than the loads in
PNNL High Rise Apartment prototype. Passive house protocols are the only
two sources that I know off that prescribe lower in-unit loads -
Passivehaus Institute (PHI) loads are less than half of EPA’s, and US
passive house off-shoot (PHIUS) loads are 15% lower than EPA’s. In general,
in-unit electricity consumption can vary significantly depending on
occupant demographics (by factor of 10 based on some papers), so both
COMNET and PHI may be correct for *some* apartments. We compared EPA
assumptions to the in-unit electricity usage in several apartment complexes
in NJ, and the numbers were in the right ballpark, so appear to represent
reasonable averages.
*From:* Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] *On
Behalf Of *Michael Campbell via Equest-users
*Sent:* Thursday, March 09, 2017 9:55 PM
*To:* Joe Huang <yjhuang at whiteboxtechnologies.com>
*Cc:* equest-users <equest-users at lists.onebuilding.org>
*Subject:* Re: [Equest-users] Wall insulation in multifamily buildings
Wow, thank you everyone for the extremely helpful responses.
To answer a few of the questions... the project is in NJ, Climate Zone 4A.
I did account for the thermal bridging of the walls studs. This project
has some metals studs and some wood studs and I accounted for both using
Appendix A of ASHRAE 90.1-2013.
Nathan, thanks for the input specifically regarding the Energy Star
Multifamily High Rise inputs values. This particular project is
participating in the ESMFHR Program so I am using their guidelines for
equipment/plug loads.
On Thu, Mar 9, 2017 at 6:32 PM, Joe Huang via Equest-users <
equest-users at lists.onebuilding.org> wrote:
I'd say the message is that R-19 wall insulation has already "captured"
most of the energy losses (or savings) for the wall.
(leaning heavily on my cane...) Back in 1986, I did a project in support of
ASHRAE and DOE residential energy standards where I did what then seemed an
endless number of DOE-2 simulations (~ 20,000) for five prototypical
residences in 45 US climates, from which using regression analyses I came
up with the component loads (KBtu/ft2) for various components of the
building (walls, roofs, internal loads, windows, etc.). Just picking out
the wall component loads for an apartment in Seattle, Miami, and DC, I get
the following:
Seattle Miami Washington DC
HL CL HL CL HL CL
R-0 28.8 0.8 1.1 4.7 23.1 1.5
R-11 10.9 0.4 0.3 1.5 8.9 0.8
R-19 7.1 0.3 0.2 0.9 5.9 0.5
R-34 3.9 0.2 0.1 0.5 3.2 0.3
So, by R-19, you're already on the flat part of the curve and more
insulation buys you very little.
Incidentally, this data base of component loads was then turned into a PC
program called PEAR (Program for Energy Analysis of Residences) that then
multiplied the regression curves by the component scalar (ft2 of wall,
e.g.), and added them up to derive the heating and cooling energy use of a
house.
PEAR is now so out-of-date technologically that the display no longer
functions, but I still think there's some good basic information contained
in the data base. David - maybe something that could be updated and
maintained by IBPSA? Or better yet, put it on the Web ?
source: "Technical documentation for a Residential Energy Use Data Base
Developed in Support of ASHRAE Special Project 53", Huang, Ritschard, and
Bull,
LBL-24306, November 1987.
Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 205A
Moraga CA 94556
yjhuang at whiteboxtechnologies.com
http://weather.whiteboxtechnologies.com for simulation-ready weather data
(o) (925)388-0265 <(925)%20388-0265>
(c) (510)928-2683 <(510)%20928-2683>
"building energy simulations at your fingertips"
On 3/9/2017 2:07 PM, David Eldridge via Equest-users wrote:
R-19 is not the worst starting point, I’d expect diminishing returns going
from good insulation to great insulation, but a much bigger jump in
efficiency from poor to good insulation levels.
Make sure you are modeling the cavity insulation accurately including any
equivalent assembly resistance due to the studs. i.e. continuous insulation
requirements are there because the cavity insulation is de-rated quite a
bit from the studs and which can be important in colder climates.
In terms of an overall percentage difference due to envelope changes you
may also see that window performance dominates if the WWR is relatively
high.
David
David S. Eldridge, Jr., P.E., LEED AP BD+C, BEMP, BEAP, HBDP
*Grumman/Butkus Associates*
*From:* Equest-users [mailto:equest-users-bounces at lists.onebuilding.org
<equest-users-bounces at lists.onebuilding.org>] *On Behalf Of *Nathan Miller
via Equest-users
*Sent:* Thursday, March 09, 2017 2:52 PM
*To:* Michael Campbell <mcamp1206 at gmail.com> <mcamp1206 at gmail.com>
*Cc:* equest-users at lists.onebuilding.org
*Subject:* Re: [Equest-users] Wall insulation in multifamily buildings
Don’t know where your building is located, but on the Seattle area
multifamily projects we routinely model, envelope has very little impact on
building energy use. DHW and ventilation seem to be the items we have the
most influence over that really can change the energy consumption.
FWIW, many of us in the Seattle market are starting to believe the standard
plug/misc load assumptions from the Energy Star MF High Rise Sim Guidelines
(if you are using them) overestimate that energy use, and result in more
“free heat” in the building and thus less sensitivity to envelope changes
(among other implications).
*Nathan Miller, PE, LEED AP BD+C** – **Mechanical Engineer/Senior Energy
Analyst*
*RUSHING* | *O* 206-285-7100 <(206)%20285-7100> |*C* 207-650-3942
<(207)%20650-3942>
*www.rushingco.com <http://www.rushingco.com/>*
*From:* Equest-users [mailto:equest-users-bounces at lists.onebuilding.org
<equest-users-bounces at lists.onebuilding.org>] *On Behalf Of *Michael
Campbell via Equest-users
*Sent:* Thursday, March 09, 2017 3:44 PM
*To:* equest-users <equest-users at lists.onebuilding.org>
*Subject:* [Equest-users] Wall insulation in multifamily buildings
Hello eQUEST Users,
I've been working on a model for a multifamily building, 5 stories,
approximately 300,000 square feet. I've been running a few iterations of
the model to see how changes to the wall assembly affect the model
results.
What I've found is that changes in the wall assembly seem to have a minimal
impact on the model results. I just did a comparison where I took an
assembly with R-19 cavity insulation and 2" rigid insulation and compared
that to the same assembly but without the rigid insulation. This was
applied to the entire building. What I found was only a 0.4% increase in
total energy cost after taking out the rigid insulation. I'm wondering if
others have found similar results in multifamily buildings?
Any input is appreciated.
Thank you,
Mike Campbell
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
------------------------------
*RWDI - A Platinum Member of Canada's 50 Best Managed Companies*
This communication is intended for the sole use of the party to whom it was
addressed and may contain information that is privileged and/or
confidential. Any other distribution, copying or disclosure is strictly
prohibited. If you received this email in error, please notify us
immediately by replying to this email and delete the message without
retaining any hard or electronic copies of same. Outgoing emails are
scanned for viruses, but no warranty is made to their absence in this email
or attachments. If you require any information supplied by RWDI in a
different format to facilitate accessibility, contact the sender of the
email, email solutions at rwdi.com or call +1.519.823.1311.
------------------------------
______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170316/ea7d1298/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image006.jpg
Type: image/jpeg
Size: 74551 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170316/ea7d1298/attachment-0010.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image008.jpg
Type: image/jpeg
Size: 29634 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170316/ea7d1298/attachment-0011.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image010.jpg
Type: image/jpeg
Size: 2242 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170316/ea7d1298/attachment-0012.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image012.jpg
Type: image/jpeg
Size: 488 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170316/ea7d1298/attachment-0013.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image014.jpg
Type: image/jpeg
Size: 347 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170316/ea7d1298/attachment-0014.jpg>
More information about the Equest-users
mailing list