[Equest-users] User-Defined Default Expressions
Michael Campbell via Equest-users
equest-users at lists.onebuilding.org
Wed Mar 8 13:19:17 PST 2017
OK, I am now trying to create a default expression for occupancy schedule
and I am running into more issues.
I used the same statement from my lighting schedule but here I am getting
an error "UNKNOWN KEYWORD or PREVIOUS .. MISSING"
Here is my expression I am using:
SET-DEFAULT FOR SPACE
PEOPLE-SCHEDULE = (
{switch(Local("C-ACTIVITY-DESC",0)+Local("C-ACTIVITY-DESC",1))
case "Apartmen" : #SI("ASHRAE MultiFam Occ Sched", "SPACE",
"PEOPLE-SCHEDULE")
default : no_default
endswitch
} )
I must be missing something because it seems to me like this should work
the same as it did for the lighting schedule.
Thank you,
On Tue, Mar 7, 2017 at 2:35 PM, Michael Campbell <mcamp1206 at gmail.com>
wrote:
> Ok - I am now trying to set up default expressions to auto-populate 2nd,
> 3rd, 4th, and 5th values for plug loads.
>
> I have the following which is working for inputting the plug load schedule
> in EQUIP-SCHEDULE 1, but how can I specify the equipment schedule for
> Equipment Load #2/3/4/5?
>
> I've tried using the BDLDFT document as reference but was unable to get
> anything to work.
>
> EQUIP-SCHEDULE = (
> {switch(Local("C-ACTIVITY-DESC",0)+Local("C-ACTIVITY-DESC",1))
> case "Apartmen" : #SI("ESMFHR Unit Eqp Sched", "SPACE", "EQUIP-SCHEDULE")
> default : #SI("ESMFHR Non-Res Eqp Sched", "SPACE", "EQUIP-SCHEDULE")
> endswitch
> } )
>
> Thank you,
>
> On Fri, Mar 3, 2017 at 6:41 PM, Nicholas Caton <Nicholas.Caton at schneider-
> electric.com> wrote:
>
>> Stop asking me hard questions! It’s a Friday!
>>
>>
>>
>> If I had to guess I would likely credit David Reddy & the rest of crew at
>> 360 Analytics… but honestly I can’t recall (could have been you, Bill?).
>>
>>
>>
>> More constructively and to your point however, this optional argument
>> however is what the doe2 reference manual is generally referring to when it
>> lists “i" or “i1, i2” in its syntax / explanations of the BDL functions.
>> Example:
>>
>>
>>
>>
>>
>> These inputs can become very important if you are trying to set up user
>> defaults for, say, the 2nd or 3rd plug load entries. Study the doe2
>> defaults expressions in that area for further reference material. That’s
>> how the 3rd inputs know to be “n/a” before you entered at least the 1st
>> and 2nd entries for a given field.
>>
>>
>>
>> ~Nick
>>
>>
>>
>> *Nick Caton, P.E., BEMP*
>>
>> Senior Energy Engineer
>> Regional Energy Engineering Manager
>>
>> Energy and Sustainability Services
>> Schneider Electric
>>
>> D 913.564.6361 <(913)%20564-6361>
>> M 785.410.3317 <(785)%20410-3317>
>> F 913.564.6380 <(913)%20564-6380>
>> E nicholas.caton at schneider-electric.com
>>
>> 15200 Santa Fe Trail Drive
>> Suite 204
>> Lenexa, KS 66219
>> United States
>>
>>
>>
>>
>>
>> *From:* Bishop, Bill [mailto:bbishop at pathfinder-ea.com]
>> *Sent:* Friday, March 03, 2017 3:14 PM
>> *To:* Nicholas Caton <Nicholas.Caton at schneider-electric.com>; Chris
>> Jones <Christopher.Jones at RWDI.com>; Michael Campbell <mcamp1206 at gmail.com
>> >
>>
>> *Cc:* equest-users at onebuilding.org
>> *Subject:* RE: [Equest-users] User-Defined Default Expressions
>>
>>
>>
>> Nick,
>>
>> Where did you find that little gem of BDL?
>>
>> ~Bill
>>
>>
>>
>> *From:* Nicholas Caton [mailto:Nicholas.Caton at schneider-electric.com
>> <Nicholas.Caton at schneider-electric.com>]
>> *Sent:* Friday, March 03, 2017 4:04 PM
>> *To:* Bishop, Bill <bbishop at pathfinder-ea.com>; Chris Jones <
>> Christopher.Jones at RWDI.com>; Michael Campbell <mcamp1206 at gmail.com>
>> *Cc:* equest-users at onebuilding.org
>> *Subject:* RE: [Equest-users] User-Defined Default Expressions
>>
>>
>>
>> Appending to this, while ("C-ACTIVITY-DESC") returns the first 4
>> characters by default, if you ever need to further distinguish inputs
>> within spaces sharing the same/similar activity descriptors, you can also
>> reference the 2nd set of 4 characters (or the 3rd set, or the 4th set…).
>>
>>
>>
>> To do this, append the optional argument “,#” wherever you’d normally
>> specify “C-ACTIVITY-DESC.”
>>
>>
>>
>> To build on the running example, say you had 2 tenants to distinguish in
>> a building with “Retail” space, but they had two different occupancy
>> densities. You could handle that by first adding to their descriptors,
>> such as follows:
>>
>> Retail_–_Best Buy
>>
>> Retail_–_Home Depot
>>
>>
>>
>> The first 4 characters for each case are the same: “RETA” (list position
>> 0). The second set of 4 is “IL_–“ (list position 1). The third set is
>> finally distinguishable: “_BES” and “_HOM” (list position 2).
>>
>>
>>
>> From here you could either insert an if/then statement for the “Reta”
>> case, or just nest another switch statement. Added some formatting for
>> clarity, but highlighted the new addition:
>>
>>
>>
>> AREA/PERSON =
>>
>> {if(#SV(#L("ZONE-TYPE"))==2) then no_def else
>>
>> if(#RV(#L("PEOPLE-SCHEDULE"))!=0) then unused else
>>
>> switch (#L("C-ACTIVITY-DESC"))
>>
>> case "Reta": switch (#L("C-ACTIVITY-DESC",2))
>>
>> case “_Bes” : 67
>>
>> case “_Hom” : 67*2
>>
>> default : 500
>>
>> endswitch
>>
>> case "Lobb": 150
>>
>> case "Clas": 100
>>
>> default: 500
>>
>> endswitch
>>
>> endif
>>
>> endif}
>>
>>
>>
>> ~Nick
>>
>>
>>
>> *Nick Caton, P.E., BEMP*
>>
>> Senior Energy Engineer
>> Regional Energy Engineering Manager
>>
>> Energy and Sustainability Services
>> Schneider Electric
>>
>> D 913.564.6361 <(913)%20564-6361>
>> M 785.410.3317 <(785)%20410-3317>
>> F 913.564.6380 <(913)%20564-6380>
>> E nicholas.caton at schneider-electric.com
>>
>> 15200 Santa Fe Trail Drive
>> Suite 204
>> Lenexa, KS 66219
>> United States
>>
>>
>>
>>
>>
>> *From:* Equest-users [mailto:equest-users-bounces at lists.onebuilding.org
>> <equest-users-bounces at lists.onebuilding.org>] *On Behalf Of *Bishop,
>> Bill via Equest-users
>> *Sent:* Friday, March 03, 2017 12:24 PM
>> *To:* Chris Jones <Christopher.Jones at RWDI.com>; Michael Campbell <
>> mcamp1206 at gmail.com>
>> *Cc:* equest-users at onebuilding.org
>> *Subject:* Re: [Equest-users] User-Defined Default Expressions
>>
>>
>>
>> Mike,
>>
>> You can start with the expression below. Paste only the text between the
>> brackets if you are pasting within the interface. If pasting into the input
>> file, this would go after “SET-DEFAULT FOR SPACE”. Like Chris said, the
>> case statement names should be four characters or less. However, they are
>> not case sensitive, so upper/lower case doesn’t matter.
>>
>> ~Bill
>>
>>
>>
>> AREA/PERSON =
>>
>> {if(#SV(#L("ZONE-TYPE"))==2) then no_def else
>>
>> if(#RV(#L("PEOPLE-SCHEDULE"))!=0) then unused else
>>
>> switch (#L("C-ACTIVITY-DESC"))
>>
>> case "Reta": 67
>>
>> case "Lobb": 150
>>
>> case "Clas": 100
>>
>> default: 500
>>
>> endswitch
>>
>> endif
>>
>> endif}
>>
>>
>>
>> *William Bishop, PE, BEMP, BEAP, CEM, LEED AP **|** Pathfinder Engineers
>> & Architects LLP*
>>
>> *Senior Energy Engineer*
>>
>>
>>
>>
>>
>> 134 South Fitzhugh Street Rochester, NY 14608
>>
>> *T: (585) 698-1956 <(585)%20698-1956>* F: (585)
>> 325-6005
>>
>> bbishop at pathfinder-ea.com <wbishop at pathfinder-ea.com>
>> www.pathfinder-ea.com
>>
>> [image: http://png-5.findicons.com/files/icons/977/rrze/720/globe.png]Carbon
>> Fee and Dividend - simple, effective, and market-based.
>>
>>
>>
>> *From:* Equest-users [mailto:equest-users-bounces at lists.onebuilding.org
>> <equest-users-bounces at lists.onebuilding.org>] *On Behalf Of *Chris Jones
>> via Equest-users
>> *Sent:* Friday, March 03, 2017 12:52 PM
>> *To:* Michael Campbell <mcamp1206 at gmail.com>
>> *Cc:* equest-users at onebuilding.org
>> *Subject:* Re: [Equest-users] User-Defined Default Expressions
>>
>>
>>
>> Note, only the first 4 characters of the C-ACTIVITY-DESC field are
>> recognized in user defined expressions. Therefore, if your UDF uses
>> “RETAIL” as the test, it may fail because only “RETA” is used.
>>
>>
>>
>> Other than that, I suggest reviewing the BDLDFT.TXT file in the eQUEST
>> 3-65 Data folder. It is full of example default expressions.
>>
>>
>>
>>
>>
>> [image: Title: RWDI - Description: RWDI logo]
>> <http://www.rwdi.com/assets/logos/RWDI-logo.gif>
>>
>> *Christopher Jones, **P.Eng. *| Senior Energy Analyst
>> *RWDI*
>> 901 King Street West, Suite 400, Toronto, ON M5V 3H5 Canada
>> Tel: (519) 823-1311 ext 2052 <(519)%20823-1311>
>> rwdi.com <http://www.rwdi.com/>
>>
>>
>>
>>
>>
>> *From:* Equest-users [mailto:equest-users-bounces at lists.onebuilding.org
>> <equest-users-bounces at lists.onebuilding.org>] *On Behalf Of *Michael
>> Campbell via Equest-users
>> *Sent:* Friday, March 03, 2017 12:32 PM
>> *To:* equest-users
>> *Subject:* [Equest-users] User-Defined Default Expressions
>>
>>
>>
>> Hi eQUEST Users,
>>
>> I'm trying to create default user expressions in an effort to
>> auto-populate certain fields in my models.
>>
>> I want to reference the activity description (C-ACTIVITY-DESC) have it
>> automatically fill in fields such as Area/Person.
>>
>> So for this example, I'm trying to make all spaces that have Activity
>> Description of "RETAIL" to be populated with a Area/Person value of 67.
>>
>> I've tried using the "Switch" function and if-then statements but haven't
>> been able to get it to work.
>>
>> Any assistance is appreciated.
>>
>> Thank you,
>>
>> Mike Campbell
>> ------------------------------
>>
>> *RWDI - A Platinum Member of Canada's 50 Best Managed Companies*
>> This communication is intended for the sole use of the party to whom it
>> was addressed and may contain information that is privileged and/or
>> confidential. Any other distribution, copying or disclosure is strictly
>> prohibited. If you received this email in error, please notify us
>> immediately by replying to this email and delete the message without
>> retaining any hard or electronic copies of same. Outgoing emails are
>> scanned for viruses, but no warranty is made to their absence in this email
>> or attachments. If you require any information supplied by RWDI in a
>> different format to facilitate accessibility, contact the sender of the
>> email, email solutions at rwdi.com or call +1.519.823.1311
>> <(519)%20823-1311>.
>> ------------------------------
>>
>>
>> ______________________________________________________________________
>> This email has been scanned by the Symantec Email Security.cloud service.
>> ______________________________________________________________________
>>
>>
>> ______________________________________________________________________
>> This email has been scanned by the Symantec Email Security.cloud service.
>> ______________________________________________________________________
>>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170308/eb5912bf/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 1240 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170308/eb5912bf/attachment-0006.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 255 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170308/eb5912bf/attachment-0008.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image007.png
Type: image/png
Size: 9020 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170308/eb5912bf/attachment-0009.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.png
Type: image/png
Size: 2844 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170308/eb5912bf/attachment-0010.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 8477 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170308/eb5912bf/attachment-0011.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image006.jpg
Type: image/jpeg
Size: 2227 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170308/eb5912bf/attachment-0007.jpg>