[Equest-users] User-Defined Default Expressions - GLASS-TYPE
Bishop, Bill via Equest-users
equest-users at lists.onebuilding.org
Tue Mar 7 10:29:11 PST 2017
Since we have a good thread going with expressions, I'll share an expression that assigns GLASS-TYPE based on WINDOW-TYPE and window orientation. In this case, south-facing windows (180 degrees, +/- 20 degrees) are assigned their own glass type. The part of the expression that determines orientation (in bold) can be used in other expressions for WINDOW keywords as you see fit.
~Bill
GLASS-TYPE =
{if(#L("WINDOW-TYPE")!=#SI("STANDARD","WINDOW","WINDOW-TYPE"))
then #SI("2Dome Acrylc White, Alum no Brk", "WINDOW", "GLASS-TYPE") else
if(#L("WIN-SPEC-METHOD")==#SI("GLASS-TYPE-INPUT","WINDOW","WIN-SPEC-METHOD"))
then if (ABS(#CDN(#P("AZIMUTH")+#P2("AZIMUTH")+
#G("BUILD-PARAMETERS","AZIMUTH"), #P("TILT")) - 180) <20)
then #SI("Type South U .19 SHGC .58", "WINDOW", "GLASS-TYPE")
else #SI("Type Other U .22 SHGC .36", "WINDOW", "GLASS-TYPE") endif
else unused endif endif}
William Bishop, PE, BEMP, BEAP, CEM, LEED AP | Pathfinder Engineers & Architects LLP
Senior Energy Engineer
[cid:image004.jpg at 01D29746.CD6E2BA0] [cid:image006.jpg at 01D29746.CD6E2BA0]
134 South Fitzhugh Street Rochester, NY 14608
T: (585) 698-1956 F: (585) 325-6005
bbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com> www.pathfinder-ea.com<http://www.pathfinder-ea.com/>
[http://png-5.findicons.com/files/icons/977/rrze/720/globe.png]Carbon Fee and Dividend - simple, effective, and market-based.
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Kevin McGaffigan via Equest-users
Sent: Tuesday, March 07, 2017 12:23 PM
To: 'Nicholas Caton' <Nicholas.Caton at schneider-electric.com>
Cc: 'equest-users' <equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] Window Properties - where to toggle glass type assignment?
Nick,
I'm not sure why your specification method is blank. Do you have "no_def" in the user expression? If you set the specification method to "composite" a dialog box should appear under specification method that allows you to select the type of glass.
[cid:image011.png at 01D29741.CBFF2490]
Kevin McGaffigan, PE
DMI
300 Chestnut Street, Suite 150
Needham, MA 02492
781-449-5700 x12
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Nicholas Caton via Equest-users
Sent: Tuesday, March 7, 2017 12:07 PM
To: equest-users <equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>>
Subject: [Equest-users] Window Properties - where to toggle glass type assignment?
Probably I'm missing something obvious... but is there no way to review/edit glass type assignment in detailed mode window properties? I've managed with creating expressions / reviewing / editing via the spreadsheet view but this has started bugging me as I keep catching myself looking for something I don't think is actually there...
[cid:image012.png at 01D29741.CBFF2490]
[cid:image013.png at 01D29741.CBFF2490]
Nick Caton, P.E., BEMP
Senior Energy Engineer
Regional Energy Engineering Manager
Energy and Sustainability Services
Schneider Electric
D 913.564.6361
M 785.410.3317
F 913.564.6380
E nicholas.caton at schneider-electric.com<mailto:nicholas.caton at schneider-electric.com>
15200 Santa Fe Trail Drive
Suite 204
Lenexa, KS 66219
United States
[cid:image014.png at 01D29741.CBFF2490]
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170307/91dcc1aa/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image011.png
Type: image/png
Size: 31250 bytes
Desc: image011.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170307/91dcc1aa/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image012.png
Type: image/png
Size: 196819 bytes
Desc: image012.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170307/91dcc1aa/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image013.png
Type: image/png
Size: 255 bytes
Desc: image013.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170307/91dcc1aa/attachment-0002.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image014.png
Type: image/png
Size: 8477 bytes
Desc: image014.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170307/91dcc1aa/attachment-0003.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.jpg
Type: image/jpeg
Size: 1517 bytes
Desc: image004.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170307/91dcc1aa/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image006.jpg
Type: image/jpeg
Size: 1647 bytes
Desc: image006.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170307/91dcc1aa/attachment-0001.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image008.png
Type: image/png
Size: 3859 bytes
Desc: image008.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170307/91dcc1aa/attachment-0004.png>
More information about the Equest-users
mailing list