[Equest-users] User-Defined Default Expressions - schedules
Bishop, Bill via Equest-users
equest-users at lists.onebuilding.org
Mon Mar 6 13:34:48 PST 2017
COOL-TEMP-SCH =
{switch (#SV(#P("TYPE")))
case 6 : unused
case 7 : unused
case 8 : unused
case 16 : unused
default :
switch (#LR("SPACE","C-ACTIVITY-DESC")) /* Unless you have mad skilz like Aaron or Nick */
case "labo": #SI("Table N2-7 Cool Sch", "ZONE", "COOL-TEMP-SCH")
case "elec": no_default
case "food": #SI("Cafeteria Cool Sch", "ZONE", "COOL-TEMP-SCH")
case "stai": #SI("Stairs Cool Sch", "ZONE", "COOL-TEMP-SCH")
case "data": #SI("Data Cool Sch", "ZONE", "COOL-TEMP-SCH")
default: #SI("Table N2-7 Cool Sch", "ZONE", "COOL-TEMP-SCH")
endswitch
endswitch}
William Bishop, PE, BEMP, BEAP, CEM, LEED AP | Pathfinder Engineers & Architects LLP
Senior Energy Engineer
[cid:image005.jpg at 01D29697.915153E0] [cid:image006.jpg at 01D29697.915153E0]
134 South Fitzhugh Street Rochester, NY 14608
T: (585) 698-1956 F: (585) 325-6005
bbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com> www.pathfinder-ea.com<http://www.pathfinder-ea.com/>
[http://png-5.findicons.com/files/icons/977/rrze/720/globe.png]Carbon Fee and Dividend - simple, effective, and market-based.
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Michael Campbell via Equest-users
Sent: Monday, March 06, 2017 3:53 PM
To: Aaron Powers <caaronpowers at gmail.com>
Cc: equest-users <equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] User-Defined Default Expressions
Has anyone had any luck creating default user expressions for schedules?
I was able to get it to work for other fields but when trying to use the Switch function for schedules I am getting errors.
Any advice?
Thank you,
On Sun, Mar 5, 2017 at 10:25 PM, Aaron Powers via Equest-users <equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>> wrote:
To expand on Nick's trick below, I wanted to share why only the 1st 4 characters are returned by default and why his code works (this is mostly a guess from reverse-engineering the source code, but it's consistent with the way the actual program works).
Old versions of Fortran had no built-in character or string data types, so programmers had to use tricks to deal with them. This would have been true of the dialect of Fortran used in the original DOE2.1A, and so a form of the original technique used to deal with string literals persists in the code today. As a warning, this next part may give the mechanical engineers out there a headache... A single character is traditionally encoded in ASCII using a single byte. A byte is 8 bits, and the largest 8 bit number is 11111111 = 255, so you can encode 256 unique characters using a single byte. As an example, the btye 01100001 = 97 represents the character 'a' in ASCII. The smallest built-in data type in early Fortran was the integer (or float) which is encoded using 4 bytes. The trick used in DOE2 is to encode string literals as an array of 8 integers (or float), and since each integer contains 4 bytes (i.e. 4 characters), the entire string array represents a total of 8x4 = 32 characters. This is why there's a 32 character limit on string fields. So accessing the first element of this array by #L("C-ACTIVITY-DESC") or #L("C-ACTIVITY-DESC",0) returns the first 4 characters, #L("C-ACTIVITY-DESC",1) returns the second 4 characters, and so on.
Now a little further into the weeds (this is more speculation into how it could be done rather than how it's actually done under the DOE2 hood). Consider the string 'abcd'. This can be encoded into a single integer by making the four bytes of the integer be the same as the 4 character's ASCII representation in sequence together. So the first byte is 97(01100001), the second 98(01100010), the third 99(01100011), and the fourth 100(01100100). Also, in Fortran, integers are encoded in little-endian style which just means that we need to order the bytes in reverse order when constructing the integer. The entire integer in binary form is then 01100100011000110110001001100001. The value of this integer in decimal is 1684234849. So, in DOE2-Land, the number 1684234849 is equivalent to 'abcd'.
However, it appears that you can't access the integer representation of these four character 'words' in keyword expressions. For example:
if ("abcd" == 1684234849) then ... produces an error.
Also, you can't do arithmetic with the integer representation. Interestingly though, the '+' operator functions as a concatenate operator when dealing with string literals. This can be used to compare the first 4, 8, 12, ... characters of a string. For example, try the following code for the lighting power density of a space. This expression considers the first 8 characters when checking the C-ACTIVITY-DESC field. This could be expanded to check all 32 characters, although the code would get a little bloated.
switch(#L("C-ACTIVITY-DESC",0) + #L("C-ACTIVITY-DESC",1))
case "office": 1.1
case "kitchen": 1.5
case "restroom": 0.7
default: 1.0
endswitch
In this code, the result when C-ACTIVITY-DESC = "office" is 1.1, but the result when C-ACTIVITY-DESC = "office1" is 1.0.
Aaron
From: Nicholas Caton [mailto:Nicholas.Caton at schneider-electric.com<mailto:Nicholas.Caton at schneider-electric.com>]
Sent: Friday, March 03, 2017 4:04 PM
To: Bishop, Bill <bbishop at pathfinder-ea.com<mailto:bbishop at pathfinder-ea.com>>; Chris Jones <Christopher.Jones at RWDI.com<mailto:Christopher.Jones at RWDI.com>>; Michael Campbell <mcamp1206 at gmail.com<mailto:mcamp1206 at gmail.com>>
Cc: equest-users at onebuilding.org<mailto:equest-users at onebuilding.org>
Subject: RE: [Equest-users] User-Defined Default Expressions
Appending to this, while ("C-ACTIVITY-DESC") returns the first 4 characters by default, if you ever need to further distinguish inputs within spaces sharing the same/similar activity descriptors, you can also reference the 2nd set of 4 characters (or the 3rd set, or the 4th set…).
To do this, append the optional argument “,#” wherever you’d normally specify “C-ACTIVITY-DESC.”
To build on the running example, say you had 2 tenants to distinguish in a building with “Retail” space, but they had two different occupancy densities. You could handle that by first adding to their descriptors, such as follows:
Retail_–_Best Buy
Retail_–_Home Depot
The first 4 characters for each case are the same: “RETA” (list position 0). The second set of 4 is “IL_–“ (list position 1). The third set is finally distinguishable: “_BES” and “_HOM” (list position 2).
From here you could either insert an if/then statement for the “Reta” case, or just nest another switch statement. Added some formatting for clarity, but highlightedthe new addition:
AREA/PERSON =
{if(#SV(#L("ZONE-TYPE"))==2) then no_def else
if(#RV(#L("PEOPLE-SCHEDULE"))!=0) then unused else
switch (#L("C-ACTIVITY-DESC"))
case "Reta": switch (#L("C-ACTIVITY-DESC",2))
case “_Bes” : 67
case “_Hom” : 67*2
default : 500
endswitch
case "Lobb": 150
case "Clas": 100
default: 500
endswitch
endif
endif}
~Nick
[cid:image013.png at 01D29696.18AC6DE0]
Nick Caton, P.E., BEMP
Senior Energy Engineer
Regional Energy Engineering Manager
Energy and Sustainability Services
Schneider Electric
D 913.564.6361<tel:(913)%20564-6361>
M 785.410.3317<tel:(785)%20410-3317>
F 913.564.6380<tel:(913)%20564-6380>
E nicholas.caton at schneider-electric.com<mailto:nicholas.caton at schneider-electric.com>
15200 Santa Fe Trail Drive
Suite 204
Lenexa, KS 66219
United States
[cid:image014.png at 01D29696.18AC6DE0]
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Bishop, Bill via Equest-users
Sent: Friday, March 03, 2017 12:24 PM
To: Chris Jones <Christopher.Jones at RWDI.com<mailto:Christopher.Jones at RWDI.com>>; Michael Campbell <mcamp1206 at gmail.com<mailto:mcamp1206 at gmail.com>>
Cc: equest-users at onebuilding.org<mailto:equest-users at onebuilding.org>
Subject: Re: [Equest-users] User-Defined Default Expressions
Mike,
You can start with the expression below. Paste only the text between the brackets if you are pasting within the interface. If pasting into the input file, this would go after “SET-DEFAULT FOR SPACE”. Like Chris said, the case statement names should be four characters or less. However, they are not case sensitive, so upper/lower case doesn’t matter.
~Bill
AREA/PERSON =
{if(#SV(#L("ZONE-TYPE"))==2) then no_def else
if(#RV(#L("PEOPLE-SCHEDULE"))!=0) then unused else
switch (#L("C-ACTIVITY-DESC"))
case "Reta": 67
case "Lobb": 150
case "Clas": 100
default: 500
endswitch
endif
endif}
William Bishop, PE, BEMP, BEAP, CEM, LEED AP | Pathfinder Engineers & Architects LLP
Senior Energy Engineer
[cid:image015.jpg at 01D29696.18AC6DE0] [cid:image016.jpg at 01D29696.18AC6DE0]
134 South Fitzhugh Street Rochester, NY 14608
T: (585) 698-1956<tel:(585)%20698-1956> F: (585) 325-6005<tel:(585)%20325-6005>
bbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com> www.pathfinder-ea.com<http://www.pathfinder-ea.com/>
[http://png-5.findicons.com/files/icons/977/rrze/720/globe.png]Carbon Fee and Dividend - simple, effective, and market-based.
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Chris Jones via Equest-users
Sent: Friday, March 03, 2017 12:52 PM
To: Michael Campbell <mcamp1206 at gmail.com<mailto:mcamp1206 at gmail.com>>
Cc: equest-users at onebuilding.org<mailto:equest-users at onebuilding.org>
Subject: Re: [Equest-users] User-Defined Default Expressions
Note, only the first 4 characters of the C-ACTIVITY-DESC field are recognized in user defined expressions. Therefore, if your UDF uses “RETAIL” as the test, it may fail because only “RETA” is used.
Other than that, I suggest reviewing the BDLDFT.TXT file in the eQUEST 3-65 Data folder. It is full of example default expressions.
[Title: RWDI - Description: RWDI logo]<http://www.rwdi.com/assets/logos/RWDI-logo.gif>
Christopher Jones, P.Eng. | Senior Energy Analyst
RWDI
901 King Street West, Suite 400, Toronto, ON M5V 3H5 Canada
Tel: (519) 823-1311 ext 2052<tel:(519)%20823-1311>
rwdi.com<http://www.rwdi.com/>
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Michael Campbell via Equest-users
Sent: Friday, March 03, 2017 12:32 PM
To: equest-users
Subject: [Equest-users] User-Defined Default Expressions
Hi eQUEST Users,
I'm trying to create default user expressions in an effort to auto-populate certain fields in my models.
I want to reference the activity description (C-ACTIVITY-DESC) have it automatically fill in fields such as Area/Person.
So for this example, I'm trying to make all spaces that have Activity Description of "RETAIL" to be populated with a Area/Person value of 67.
I've tried using the "Switch" function and if-then statements but haven't been able to get it to work.
Any assistance is appreciated.
Thank you,
Mike Campbell
________________________________
RWDI - A Platinum Member of Canada's 50 Best Managed Companies
This communication is intended for the sole use of the party to whom it was addressed and may contain information that is privileged and/or confidential. Any other distribution, copying or disclosure is strictly prohibited. If you received this email in error, please notify us immediately by replying to this email and delete the message without retaining any hard or electronic copies of same. Outgoing emails are scanned for viruses, but no warranty is made to their absence in this email or attachments. If you require any information supplied by RWDI in a different format to facilitate accessibility, contact the sender of the email, email solutions at rwdi.com<mailto:solutions at rwdi.com> or call +1.519.823.1311<tel:(519)%20823-1311>.
________________________________
______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170306/7c85c5ed/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image013.png
Type: image/png
Size: 255 bytes
Desc: image013.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170306/7c85c5ed/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image014.png
Type: image/png
Size: 8477 bytes
Desc: image014.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170306/7c85c5ed/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image015.jpg
Type: image/jpeg
Size: 1240 bytes
Desc: image015.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170306/7c85c5ed/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image016.jpg
Type: image/jpeg
Size: 1309 bytes
Desc: image016.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170306/7c85c5ed/attachment-0001.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image017.png
Type: image/png
Size: 2844 bytes
Desc: image017.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170306/7c85c5ed/attachment-0002.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image018.jpg
Type: image/jpeg
Size: 2227 bytes
Desc: image018.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170306/7c85c5ed/attachment-0002.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.jpg
Type: image/jpeg
Size: 1517 bytes
Desc: image005.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170306/7c85c5ed/attachment-0003.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image006.jpg
Type: image/jpeg
Size: 1647 bytes
Desc: image006.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170306/7c85c5ed/attachment-0004.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image007.png
Type: image/png
Size: 3859 bytes
Desc: image007.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170306/7c85c5ed/attachment-0003.png>
More information about the Equest-users
mailing list