[Equest-users] Subhour demand metering

Lapierre, Patrick via Equest-users equest-users at lists.onebuilding.org
Mon Mar 27 11:54:41 PDT 2017


Hello everyone,

I've got a project on my hand in which the electrical demand reported in the PS-E report doesn't match the billing demand in the ES-E report.
I've found that this was due to the "demand interval" of 15 mins on the utility meter. Fixing the demand interval to 60 mins solved the matching demand problem between the PS-E and ES-E report.

I'm just curious as how does eQUEST calculate subhour demand and determined that some electric heating power in my building didn't last more than 15min.
I need a captain here. Anyone can enlighten me?

Thanks,


  [Bouthillette Parizeau] <http://www.bpa.ca/>

Patrick Lapierre_ing.
plapierre at bpa.ca<mailto:plapierre at bpa.ca>   |  www.bpa.ca<http://www.bpa.ca>  |  t: 5143833747x2807

Les informations contenues dans le courriel que vous venez de recevoir, y compris les pièces jointes, sont destinées à l'usage exclusif de la (ou des) personne(s) identifiée(s) comme destinataires et sont confidentielles. Si vous n'en êtes pas le destinataire, soyez avisé que tout usage en est interdit. Si vous avez reçu ce courriel par erreur, veuillez le retourner à l'expéditeur et le supprimer complètement de votre système informatique.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170327/fb684946/attachment-0004.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 5690 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170327/fb684946/attachment-0005.jpg>


More information about the Equest-users mailing list