[Equest-users] change fan schedule type
Nicholas Caton via Equest-users
equest-users at lists.onebuilding.org
Fri Jun 30 04:22:14 PDT 2017
Schedules exist in multiple parts: Annual, week schedule(s), day schedule(s). Changing just one part (a day or week schedule) to another type will throw a lot of errors because they all need to be of a consistent type (Fraction vs. ON/OFF).
Since your schedule looks relatively simple at the moment, It’s probably easiest to simply start a new annual/week/day schedule of the Fractional type from scratch, or copying an existing fractional system type (and all child components) to get each piece started in one action for edits.
Note also the freely available spreadsheet tool EMIT is something to be aware of for anyone with a heavy amount of custom scheduling work. Can make eQUEST schedule setups of any sort a relative breeze if you have a cluster to do at once or wish to do something as granular as an 8760 hourly schedule.
~Nick
[cid:image001.png at 01D2F0D9.196080D0]
Nick Caton, P.E., BEMP
Senior Energy Engineer
Regional Energy Engineering Manager
Energy and Sustainability Services
Schneider Electric
D 913.564.6361
M 785.410.3317
F 913.564.6380
E nicholas.caton at schneider-electric.com<mailto:nicholas.caton at schneider-electric.com>
15200 Santa Fe Trail Drive
Suite 204
Lenexa, KS 66219
United States
[cid:image002.png at 01D2F0D9.196080D0]
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Fakeha Sehar via Equest-users
Sent: Wednesday, June 28, 2017 8:54 PM
To: via Equest-users <equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] change fan schedule type
[Inline image]
I want to change the fan schedule from on/off to fraction in order to reduce the cooling consumption. But I am getting this error.
On Tuesday, June 27, 2017 12:41 PM, Fakeha Sehar <fakeha_s at yahoo.com<mailto:fakeha_s at yahoo.com>> wrote:
I want to change the fan schedule type from on/off flag type to fraction. Ho can I do this.
Regards
______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170630/67bd5349/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 255 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170630/67bd5349/attachment-0006.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 8477 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170630/67bd5349/attachment-0007.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 164996 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170630/67bd5349/attachment-0008.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: oledata.mso
Type: application/octet-stream
Size: 7143 bytes
Desc: oledata.mso
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170630/67bd5349/attachment-0002.obj>
More information about the Equest-users
mailing list