[Equest-users] Double Facade wall modeling strategies
Lapierre, Patrick via Equest-users
equest-users at lists.onebuilding.org
Tue Jun 27 09:57:44 PDT 2017
Hi Pasha,
I’ve completed one project that used a double facade wall.
The strategy used was to model a thin zone alongside all the perimeter of the building, something like 2 ft wide. Then I modeled windows in the internal wall between the “facade zone” and the “interior zone” and modeled the “facade zone” as a sunspace.
Results were making sense but it was a pain to model the reference building since the zoning had to be done anew.
Hope that helps you.
[Bouthillette Parizeau]<http://www.bpa.ca/>
Patrick Lapierre_ing. BEMP
plapierre at bpa.ca | t: 5143833747x2807
De : Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] De la part de Pasha Korber-Gonzalez via Equest-users
Envoyé : 27 juin 2017 11:50
À : eQUEST Users List <equest-users at lists.onebuilding.org>
Objet : [Equest-users] Double Facade wall modeling strategies
Hi all-- does anyone have a successful example or strategy to model a double facade in eQuest?
At this point I am open to any ideas and tips. Everything I have tried thus far is not yielding anything useful to the model.
Thanks,
Pasha
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170627/545e320a/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 1706 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170627/545e320a/attachment-0002.jpg>
More information about the Equest-users
mailing list