Hi Prasad,

More or less energy must be spent to handle the calls for cooling in your model, as occurring.  The varying weather conditions & internal loads result in that otherwise constant volume system needing to cycle its cooling-associated energies (i.e. the water pump/sprayer) more/less often.

Note also that for evaporative cooling, even if you had zero fluctuations in heating loads to reject from the building, another factor is the varying exterior relative humidity, which will increase/decrease the effective heat rejection rate.

I anticipate through custom hourly reports you might be able to visualize/plot ventilation fan vs. evaporator cooling energies and find where one is constant/regular the other does correlate with the relative heating loads for the spaces conditioned.

Does that make sense?

~Nick

[cid:image001.png at 01D2E8E1.756366E0]
Nick Caton, P.E., BEMP
  Senior Energy Engineer
  Regional Energy Engineering Manager
  Energy and Sustainability Services
  Schneider Electric

D  913.564.6361
M  785.410.3317
F  913.564.6380
E  nicholas.caton at schneider-electric.com<mailto:nicholas.caton at schneider-electric.com>

15200 Santa Fe Trail Drive
Suite 204
Lenexa, KS 66219
United States

[cid:image002.png at 01D2E8E1.756366E0]



From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Prasad Wani via Equest-users
Sent: Thursday, June 15, 2017 8:15 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Evaporative cooler modelling

Dear All,

I am modelling Indirect-Direct Evaporating cooling system with constant volume and continuous setting. The minimum and maximum supply flow ratio is 1. The OA fraction is also 1.

The pump & secondary kW value is 0.00015 kW / cfm. This parameter is used for space cooling.

With the above settings, energy consumption for ventilation fan is constant. However, the space cooling energy consumption is different for each month. The screenshot is as follows:

[Inline image 1]


Why the space cooling energy consumption is not same for all months even when constant value of 0.00015 kW / cfm is given as input?

Kindly guide about this.

Thank you

Regards,


Prasad S Wani

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170619/d74b9448/attachment-0004.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 255 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170619/d74b9448/attachment-0015.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 8477 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170619/d74b9448/attachment-0016.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: oledata.mso
Type: application/octet-stream
Size: 7131 bytes
Desc: oledata.mso
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170619/d74b9448/attachment-0005.obj>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.png
Type: image/png
Size: 33384 bytes
Desc: image004.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170619/d74b9448/attachment-0017.png>


More information about the Equest-users mailing list