[Equest-users] daily weather conditions
Nicholas Caton via Equest-users
equest-users at lists.onebuilding.org
Fri Jun 2 06:54:30 PDT 2017
As someone who has advocated for and used the eQ_WthProc a few times to good effect, I’ll also add that this particular weather visualization and format conversion toolset is IMHO superseded by another free option, ELEMENTS: http://bigladdersoftware.com/projects/elements/.
These two options mirror each other in functionality, but ELEMENTS is a relative breeze to install/execute, and offers a deeper/broader set of immediate visualization options for QC. I think the DOEWth processor also hosted at http://doe2.com/index_Wth.html has additional conversion functionalities.
I would use none of the above tools however to visualize something I already have loaded into an eQUEST model. Good advice = to use the GLOBAL custom hourly reporting variables to pull whatever set of weather file conditions you want to see and punch that out in a simulation. Combining that with other custom hourly outputs allows you to quickly scatterplot exterior conditions vs. useful metrics like specific fan/system/plant equipment operations/outputs to have your eQuest model tell you stories you won’t find in the default interface.
~Nick
[cid:image001.png at 01D2DB7D.05DCFF50]
Nick Caton, P.E., BEMP
Senior Energy Engineer
Regional Energy Engineering Manager
Energy and Sustainability Services
Schneider Electric
D 913.564.6361
M 785.410.3317
F 913.564.6380
E nicholas.caton at schneider-electric.com<mailto:nicholas.caton at schneider-electric.com>
15200 Santa Fe Trail Drive
Suite 204
Lenexa, KS 66219
United States
[cid:image002.png at 01D2DB7D.05DCFF50]
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Brian Fountain via Equest-users
Sent: Wednesday, May 24, 2017 5:49 AM
To: Julien MARREC via Equest-users <julien.marrec at gmail.com>; Fakeha Sehar <fakeha_s at yahoo.com>
Cc: via Equest-users <equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] daily weather conditions
Agreed. There is also a tool on doe2.com that will unpack the weather file but the hourly report method is quick and easy.
From: Julien MARREC via Equest-users
Sent: Wednesday, May 24, 2017 2:23 AM
To: Fakeha Sehar
Reply To: Julien MARREC
Cc: via Equest-users
Subject: Re: [Equest-users] daily weather conditions
Add an hourly report, you'll find variables for outside dry/wet bulb temperature, etc.
Envoyé de mon iPhone
Le 22 mai 2017 à 17:58, Fakeha Sehar via Equest-users <equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>> a écrit :
How can outside weather conditions, such as dry bulb temperature for a day be known in eQuest?
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170602/0459db1a/attachment-0005.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 255 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170602/0459db1a/attachment-0010.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 8477 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170602/0459db1a/attachment-0011.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: oledata.mso
Type: application/octet-stream
Size: 7118 bytes
Desc: oledata.mso
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170602/0459db1a/attachment-0005.obj>
More information about the Equest-users
mailing list