[Equest-users] Effective Insulation/Farming Layer R-Value Value

Morteza Kasmai via Equest-users equest-users at lists.onebuilding.org
Thu Jul 20 07:26:22 PDT 2017


Nathan, Daniel, Nick and Chris,

Thank you all for your helpful recommendations and guidance.

Morteza




On Wed, Jul 19, 2017 at 7:43 PM, Chris Baker <CBaker at cci-alliance.com>
wrote:

> I agree with Daniel on this one.
>
>
>
> If you wanted to go above and beyond, you could check out Table A3.3 in
> the section A tables of 90.1 since it has effective overall U-factors and
> R-values for different construction types and insulation applications – to
> include steel framing @ 16 o.c. and 24 o.c.
>
>
>
> You can select from the insulation R-values for each construction type and
> from there you can get the overall U-factor for the entire wall assembly
> which might also come in handy for any detail edits you might need to make.
>
>
>
> There is also an R-value calculator online that will allow you to model
> each wall component and calculate the overall/composite R-value of the
> system.  It might just be interesting to compare it to the ASHRAE 90.1
> numbers in Section A tables or other values online.
>
>
>
> *Chris Baker*
>
> *CCI Alliance of Companies*
>
> *Fort Wainwright, Alaska*
>
> *907-356-1681 <(907)%20356-1681> (x105) office*
>
> *907-750-4922 <(907)%20750-4922> cell*
>
>
>
> *From:* Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] *On
> Behalf Of *Morteza Kasmai via Equest-users
> *Sent:* Wednesday, July 19, 2017 6:16 AM
> *To:* equest-users at lists.onebuilding.org
> *Subject:* [Equest-users] Effective Insulation/Farming Layer R-Value Value
>
>
>
> There is a wall section in this project with 4” thick interior
> polyurethane spray foam inside the metal studs.
>
> Since Table A9.2B of ASHRAE 90.1 does not provide the effective
> insulation/framing layer R-Value for this type of insulation, how can one
> calculate this value?
>
> Your thoughts and suggestions would be highly appreciated,
> Morteza
>
>
>
>
>
> ------------------------------
>
> CCI-Alliance Confidentiality notice: This message is intended only for the
> person to whom addressed in the text above and may contain privileged or
> confidential information. If you are not that person, any use of this
> message is prohibited. We request that you notify us by reply to this
> message, and then delete all copies of this message including any contained
> in your reply. Thank you.
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170720/c387555c/attachment-0004.htm>


More information about the Equest-users mailing list