[Equest-users] Weird request to everyone
Bishop, Bill via Equest-users
equest-users at lists.onebuilding.org
Wed Jan 18 08:53:38 PST 2017
Hi Mayank,
You have a large model and there is a lot going on. Here are some comments:
- There are 184 systems and 81 of them are SUM systems. I never use SUM for simulations so I don’t know what effect it is having on your model. Understood that many of these are plenum spaces, but I usually assign these to the same system as the zone below.
- 60% of the zones are TYPE = UNCONDITIONED. Many of these are restrooms, corridors, stairways and storage spaces which are probably at least heated in the proposed design and may have ducted systems, so they should probably be modeled as CONDITIONED.
- The zone THROTTLING-RANGE has been increased to 4 and in many cases 6°F. This is likely unrealistic with the proposed design having tighter temperature control responsiveness.
- All systems have the same MIN-AIR-SCH which turns off ventilation at night, but the project appears to have a large residential component so this seems unrealistic. This is likely reducing the heating load considerably.
- The WLHP loop has LOOP-OPERATION=DEMAND-ONLY. This is unrealistic for a WLHP loop and STANDBY would make sense.
- The model has a high number of unmet hours (947 hrs heating; 5451 hrs cooling) even with the features above that tend to reduce them.
- It doesn’t make sense to compare the proposed design to a baseline until the unmet heating and cooling hours are fairly addressed. If the proposed model retains the features above after the unmet hours are minimized, make sure to duplicate these features in the baseline for a fair comparison.
Regards,
~Bill
William Bishop, PE, BEMP, BEAP, CEM, LEED AP | Pathfinder Engineers & Architects LLP
Senior Energy Engineer
[cid:image007.jpg at 01D27181.87EFB840] [cid:image008.jpg at 01D27181.87EFB840]
134 South Fitzhugh Street Rochester, NY 14608
T: (585) 698-1956 F: (585) 325-6005
bbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com> www.pathfinder-ea.com<http://www.pathfinder-ea.com/>
[http://png-5.findicons.com/files/icons/977/rrze/720/globe.png]Carbon Fee and Dividend - simple, effective, and market-based.
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Mayank Bhatnagar via Equest-users
Sent: Wednesday, January 18, 2017 1:20 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Weird request to everyone
Dear All,
Its a very weird request to all of you in your busy schedule. As in my earlier thread for modelling of Water loop heat pump in equest and query was regarding the low heating consumption. I am still doubtful about the heating consumption in the Proposed case in which system is water loop heat pump with supplemental boiler and cooling tower to maintain the loop temperature.
As the Proposed case is water loop heat pump with gas boiler, the baseline case system type will be System Type 1 (PTAC with fossil fuel boiler). The simulation results for baseline and proposed case shows around 97% energy savings in Heating end-use. The climate type as per ASHRAE is 4A (Washington DC). I have checked hourly loop temperature profile, boiler and cooling tower operation hours and seems fine. The boiler is working in winter months but with very little energy consumption.
Here, I am attaching the proposed case model with weather file and hoping if anyone can look into the model. I will appreciate any suggestions to improve the model.
Thank you.
Regards,
Mayank Bhatnagar
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170118/61c7c9ae/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image007.jpg
Type: image/jpeg
Size: 1517 bytes
Desc: image007.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170118/61c7c9ae/attachment-0004.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image008.jpg
Type: image/jpeg
Size: 1647 bytes
Desc: image008.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170118/61c7c9ae/attachment-0005.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image009.png
Type: image/png
Size: 3862 bytes
Desc: image009.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170118/61c7c9ae/attachment-0002.png>
More information about the Equest-users
mailing list