[Equest-users] Humidification Savings for LEED, BREEM
Bikesh Dahal via Equest-users
equest-users at lists.onebuilding.org
Fri Jan 27 12:07:07 PST 2017
Has anyone shown savings for atomizing humidifiers for LEED and BREEM Projects? I am working on an arts storage facility with significant humidification requirements. I would like to claim savings due to the atomizing humidifiers.
I am developing an exceptional calculation to demonstrate the savings. I was wondering if anyone has been able to claim savings for these either in LEED or BREEM certification?
Thanks a lot.
Bikesh Dahal, BEMP
Associate
[cid:image003.png at 01D06C70.35E5BD50]
129 West 27th Street
New York, NY 10001
tel: 212-529-5969, ext. 318
fax: 212-529-6023
bdahal at emegroup.com<mailto:bdahal at emegroup.com>
www.emegroup.com<http://www.emegroup.com/>
NY ▪ Albany ▪ Philadelphia ▪ Denver
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Chris Jones via Equest-users
Sent: Wednesday, November 30, 2016 2:42 PM
To: Arunabha Sau <runabha at gmail.com>
Cc: equest-users at onebuilding.org
Subject: Re: [Equest-users] ER Wheel in Baseline
The amount of outdoor air in the baseline determines whether or not the baseline requires heat recovery. The amount of outdoor air in the baseline depends on the ASHRAE 62.1 outdoor air amounts or the mandated exhaust/make-up air flow – which ever is larger. Given that the space is a car garage, exhaust likely determines the baseline outdoor air amount.
By way of an example, I am working on a project that has 100% OA systems. They are VAV systems with the minimum flow equal to the 62.1 calculated value ramping to maximum flow for cooling. The proposed design has ERVs. The baseline outdoor air is equal to the 62.1 calculated values but the total supply flow is such that the percentage of outdoor air is less than 70% so the baseline doesn’t have heat recovery.
Christopher Jones, P. Eng.
Rowan Williams Davies & Irwin Inc.
Consulting Engineers & Scientists
901 King Street West, Suite 400, Toronto, Ontario, M5V 3H5
T: (519) 823-1311 ext 2052
M: (416) 697-0056
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Arunabha Sau via Equest-users
Sent: Wednesday, November 30, 2016 1:48 PM
To: Anthony; equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] ER Wheel in Baseline
Hey Anthony,
I believe you're absolutely right. Because of this confusion I posted in the forum!
In my case, this is climate zone 5A. Supply Air is more than 5000 cfm per fan. And the proposed system is on 100% OA with HR wheel. It's for a car-repair bay/garage.
So you think the Baseline won't need an Heat Recovery Wheel? Should I be modeling it as even 100% OA?
Best,
Aru Sau
Architectural Sustainability | Energy Analyst
analyzing the ROI of your sustainable initiatives...
c: 678-467-7934, Ann Arbor, MI
On Tue, Nov 29, 2016 at 4:44 PM, Anthony <Anthony at greenengineer.com<mailto:Anthony at greenengineer.com>> wrote:
Aru,
I may be reading the question wrong but the proposed case system does NOT dictate baseline case ERV requirements. If the autosized baseline case systems meet the characteristics outlined in 90.1-2007(?) Section G3.1.2.10, then an ERV must be included on that system unless one of the exceptions apply.
Anthony Hardman, PE, BEAP, LEED AP BD+C
Senior Building Performance Analyst
The Green Engineer, Inc.
(978) 610-2801<tel:(978)%20610-2801>
From: Darryl Kasun via Equest-users [mailto:equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>]
Sent: Monday, November 28, 2016 10:12 PM
To: Arunabha Sau
Cc: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] ER Wheel in Baseline
Hi Aru,
Yes you are correct - you have to create an exhaust air heat recovery with at least 50% effectiveness in your baseline bldg. Check out section 6.5.6.1 of ASHRAE 90.1 for further guidance.
Darryl Kasun, P. Eng,
Interior Engineering
On Mon, Nov 28, 2016 at 6:58 PM, Arunabha Sau via Equest-users <equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>> wrote:
Hello there,
In a 5A climate zone, I am working with a Proposed model with a RTU (30,000 CFM, 100% OA) with exhaust air ER wheel in it. I am kinda sure that I've to create a ER wheel for the 90.1 Baseline (as per G3.1.2.10). Just want to make sure if I am correct?
Help please. Thanks
Best,
Aru Sau
Architectural Sustainability | Energy Analyst
analyzing the ROI of your sustainable initiatives...
c: 678-467-7934<tel:678-467-7934>, Ann Arbor, MI
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
________________________________
RWDI - One of Canada's 50 Best Managed Companies - This communication is intended for the sole use of the party to whom it was addressed and may contain information that is privileged and/or confidential. Any other distribution, copying or disclosure is strictly prohibited. If you received this email in error, please notify us immediately by replying to this email and delete the message without retaining any hard or electronic copies of same. Outgoing emails are scanned for viruses, but no warranty is made to their absence in this email or attachments. If you require any information supplied by RWDI in a different format to facilitate accessibility, contact the sender of the email, email solutions at rwdi.com<mailto:solutions at rwdi.com> or call +1.519.823.1311.
________________________________
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170127/d37e2d71/attachment-0004.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 8763 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170127/d37e2d71/attachment-0005.png>
More information about the Equest-users
mailing list