[Equest-users] Boiler Curves in Library
Brad Painting via Equest-users
equest-users at lists.onebuilding.org
Tue Jan 10 05:47:14 PST 2017
Thanks for the feedback everyone. I am comparing some of the information in the PG&E study with the algorithms described in the DOE2 Engineer’s manual. I am confused about how the MIN-RATIO variable is used. It seems like the engineer’s manual states that the equipment only cycles on/off when the load drops below MIN-RATIO, but it also states that the part load performance curves account for cycling (pg. v.10):
[cid:image004.png at 01D26B1B.F18A56F0]
For a single stage boiler then, what is the MIN-RATIO doing if all of the part load performance is already attributed to cycling?
The graph of “Unit 1” performance in the PG&E study (pg. 40) closely matches the performance curve from the Atmospheric-Blr-HIR-fPLR curve in the library. “Unit 1” is a single stage boiler, so all part load performance would occur from cycling. What would the best curve be to simulate the part load performance of a modulating non-condensing boiler?
[cid:image005.jpg at 01D26B1D.45019180]
From: erik.kolderup at gmail.com [mailto:erik.kolderup at gmail.com] On Behalf Of Erik Kolderup
Sent: Thursday, January 05, 2017 1:15 PM
To: Brad Painting <Bpainting at fstrategies.com>; equest-users <equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] Boiler Curves in Library
Doesn't directly answer your question, but this report by Taylor Engineering and PG&E discusses the DOE2.2 boiler curves and compares to measured boiler performance: http://www.etcc-ca.com/sites/default/files/OLD/images/boiler_research_project_-_ats-te_final_report_pcb_05092012.pdf.
-Erik
Erik Kolderup, PE, LEED AP
erik at kolderupconsulting.com<mailto:erik at kolderupconsulting.com> | 415.531.5198 | www.kolderupconsulting.com<http://www.kolderupconsulting.com>
On Thu, Jan 5, 2017 at 9:39 AM, Bishop, Bill via Equest-users <equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>> wrote:
Hi Brad,
I don’t know how the default boiler curves were developed, but…
It is easy enough to create custom curves based on manufacturer performance data, which is available for many boiler models.
There are other inputs that affect simulated fuel consumption in eQUEST besides the boiler HIR-FPLR curve and full-load HIR, including MIN-RATIO and STANDBY-TIME. If the boiler part-load ratio is below the MIN-RATIO, there are cycling losses based on the STANDBY-TIME. The MIN-RATIO is usually known based on the boiler model but I don’t think I’ve seen published numbers on cycling losses sufficient to calculate STANDBY-TIME. But I have adjusted the defaults when calibrating a model to known fuel consumption.
The ASHRAE Handbook has some reference material. S32.6 is on boiler efficiency and includes an efficiency curve for a modulating boiler, showing efficiency improving slightly at part loads (instead of degrading) “from the increase in the ratio of heat exchanger surface area to heat input as the firing rate is reduced”. F19.12 Boiler Model provides some fundamental research and lists references if you want to dig into it further.
Regards,
~Bill
William Bishop, PE, BEMP, BEAP, CEM, LEED AP | Pathfinder Engineers & Architects LLP
Senior Energy Engineer
[cid:image001.jpg at 01D26B18.5441C7F0] [cid:image002.jpg at 01D26B18.5441C7F0]
134 South Fitzhugh Street Rochester, NY 14608
T: (585) 698-1956<tel:(585)%20698-1956> F: (585) 325-6005<tel:(585)%20325-6005>
bbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com> www.pathfinder-ea.com<http://www.pathfinder-ea.com/>
[http://png-5.findicons.com/files/icons/977/rrze/720/globe.png]Carbon Fee and Dividend - simple, effective, and market-based.
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org>] On Behalf Of Brad Painting via Equest-users
Sent: Thursday, January 05, 2017 9:02 AM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: [Equest-users] Boiler Curves in Library
Can someone direct me to where I can find an explanation of how the part-load boiler curves were developed? I can find the formula coefficients for the heat-input ratio in the BDLLIB.dat file and an explanation of how to apply them in the DOE2 Engineer’s Manual. But how were the formulas and coefficients developed? Are they based on some study results described somewhere in the documentation? I am seeing very little part-load degradation in performance using the forced draft curve and I was wondering why. Thanks.
Brad Painting
Facility Strategies Group, LLC
1012 Market Street, Suite 307
Fort Mill, SC 29708
Phone: (803) 493-9706<tel:(803)%20493-9706>
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170110/517870f9/attachment-0005.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 1517 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170110/517870f9/attachment-0015.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 1647 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170110/517870f9/attachment-0016.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 3859 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170110/517870f9/attachment-0010.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.png
Type: image/png
Size: 43188 bytes
Desc: image004.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170110/517870f9/attachment-0011.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.jpg
Type: image/jpeg
Size: 31118 bytes
Desc: image005.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170110/517870f9/attachment-0017.jpg>
More information about the Equest-users
mailing list