[Equest-users] Can envelope be rotated in Detailed Data Mode?
Brian Fountain
bfountain at greensim.com
Wed Dec 20 19:20:32 PST 2017
Absolutely.
The keyword is AZIMUTH. It is found under the Building Data on the
Building Shell tab of the detailed interface:
The easiest way to do the 3 rotations is to change the AZIMUTH to 90,
180 & 270 in parametric runs:
On 20/12/2017 4:31 PM, Jing Hong via Equest-users wrote:
> Dear All,
>
> I wonder, can the whole building be rotated 90, 180 and 270 degree in
> Detailed Data Mode? If I switch back to Wizard Data Mode and change
> orientation, the parts and pieces edited in Detail would be gone. Is
> there any way to make rotation easy?
>
> Thank you,
>
> Jing
>
> --
> PhD Candidate, LEED AP BD+C
>
> School of Architecture and Urban Planning
> University of Wisconsin-Milwaukee
>
>
> <http://www.avg.com/email-signature?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient>
> Virus-free. www.avg.com
> <http://www.avg.com/email-signature?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient>
>
>
> <#DAB4FAD8-2DD7-40BB-A1B8-4E2AA1F9FDF2>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20171220/eab529f5/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: apojjmehoaoeepja.png
Type: image/png
Size: 107519 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20171220/eab529f5/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: bkhllgpkmjhjlheh.png
Type: image/png
Size: 51229 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20171220/eab529f5/attachment-0001.png>
More information about the Equest-users
mailing list