[Equest-users] Supply air temperature reset based on return air temperature on eQuest
Bishop, Bill
bbishop at pathfinder-ea.com
Wed Dec 13 07:24:16 PST 2017
Hi Gamage,
I don’t know of a direct way to control SAT based on RAT in eQUEST. Here are some approaches to consider:
1.) Set the ZONE keywords for THERMOSTAT-TYPE, THROTTLING-RANGE and (in eQUEST 3.65/DOE2.3) THERMOSTAT-LOCN to best approximate your control strategy. You should use a PROPORTIONAL or REVERSE-ACTION thermostat type if you want to adjust the heat addition/extraction rate in proportion to the difference between the zone set point and the zone temperature (which should match or closely match the RAT).
2.) Set the SYSTEM:COOL-CONTROL to WARMEST to adjust the cold deck temperature based on the highest zone temperature (highest RAT).
3.) Set the SYSTEM:COOL-CONTROL to SCHEDULED and create a COOL-SET-SCH and/or HEAT-SET-SCH to force the cold/hot deck supply air temperatures. You could set the SAT in these schedules to be consistent with the thermostat schedules, space loads, cooling/heating season, or whatever else is driving your control strategy.
Note that you can select a SYSTEM:TYPE of PVAVS or VAVS to enable the COOL-CONTROL keywords, even if your actual system is constant volume. You would just want to set the system for constant volume FAN-CONTROL and 1.0 for MIN-FLOW-RATIO.
Regards,
~Bill
William Bishop, PE, BEMP, BEAP, CEM, LEED AP | Pathfinder Engineers & Architects LLP
Senior Energy Engineer
[cid:image004.jpg at 01D373FC.AE93C8F0] [cid:image006.jpg at 01D373FC.AE93C8F0]
134 South Fitzhugh Street Rochester, NY 14608
T: (585) 698-1956 F: (585) 325-6005
bbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com> www.pathfinder-ea.com<http://www.pathfinder-ea.com/>
[http://png-5.findicons.com/files/icons/977/rrze/720/globe.png]Carbon Fee and Dividend - simple, effective, and market-based.
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Gamage Lakshan via Equest-users
Sent: Tuesday, December 12, 2017 10:16 PM
To: Jones, Christopher <Christopher.r.Jones at wsp.com>
Cc: equest-users at onebuilding.org
Subject: Re: [Equest-users] Supply air temperature reset based on return air temperature on eQuest
Hi Jones,
Thanks for the quick reply.
Do you know about another way that I can control the supply air temperature based on return air temperature. Note - The HVAC design requires the AHU fans to run at constant volume all the time to maintain room pressure.
Thanks,
Gamage
On Tue, Dec 12, 2017 at 7:37 PM, Jones, Christopher <Christopher.r.Jones at wsp.com<mailto:Christopher.r.Jones at wsp.com>> wrote:
Gamage,
Input functions are not implemented in DOE2.2. This is made clear in the DOE22Vol3-Topics manual:
[cid:image009.png at 01D373F6.01E350E0]
Christopher R. Jones, P.Eng.
Technical Specialist
Sustainability & Energy
[cid:image010.png at 01D373F6.01E350E0]
T +1 416-644-0252<tel:(416)%20644-0252>
2300 Yonge Street, Suite 2300<https://maps.google.com/?q=2300+Yonge+Street,+Suite+2300%0D+Toronto,+ON+M4P+1E4+Canada&entry=gmail&source=g>
Toronto, ON M4P 1E4 Canada<https://maps.google.com/?q=2300+Yonge+Street,+Suite+2300%0D+Toronto,+ON+M4P+1E4+Canada&entry=gmail&source=g>
wsp.com<http://wsp.com>
Please consider the environment before printing...
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org>] On Behalf Of Gamage Lakshan via Equest-users
Sent: Monday, December 11, 2017 10:35 PM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: [Equest-users] Supply air temperature reset based on return air temperature on eQuest
Hi all,
I am trying to model supply air temperature reset based on return air temperature on eQuest 3.64.
HVAC Input function samples on DOE2.2 Vol3- Topics provides a sample input function for Cold Deck Supply Air temperature reset using return air temperature.
I am new to eQuest input functions. Does anyone know how code for HVAC input functions should be entered to the program, is there someplace that I can paste the sample code ? BDL file or INP file.
Some basic insight in to HVAC input functions will be highly appreciated.
Or is there an easy way to model supply air temp reset based on return air temp.
Thanks,
Gamage Lakshan,
EE Engineer
LEED AP BD+C, BEMP, B Eng
________________________________
NOTICE: This communication and any attachments ("this message") may contain information which is privileged, confidential, proprietary or otherwise subject to restricted disclosure under applicable law. This message is for the sole use of the intended recipient(s). Any unauthorized use, disclosure, viewing, copying, alteration, dissemination or distribution of, or reliance on, this message is strictly prohibited. If you have received this message in error, or you are not an authorized or intended recipient, please notify the sender immediately by replying to this message, delete this message and all copies from your e-mail system and destroy any printed copies. You are receiving this communication because you are listed as a current WSP contact. Should you have any questions regarding WSP's electronic communications policy, please consult our Anti-Spam Commitment at www.wsp.com/casl<http://www.wsp.com/casl>. For any concern or if you believe you should not be receiving this message, please forward this message to caslcompliance at wsp.com<mailto:caslcompliance at wsp.com> so that we can promptly address your request. Note that not all messages sent by WSP qualify as commercial electronic messages.
AVIS : Ce message, incluant tout fichier l'accompagnant (« le message »), peut contenir des renseignements ou de l'information privilégiés, confidentiels, propriétaires ou à divulgation restreinte en vertu de la loi. Ce message est destiné à l'usage exclusif du/des destinataire(s) voulu(s). Toute utilisation non permise, divulgation, lecture, reproduction, modification, diffusion ou distribution est interdite. Si vous avez reçu ce message par erreur, ou que vous n'êtes pas un destinataire autorisé ou voulu, veuillez en aviser l'expéditeur immédiatement et détruire le message et toute copie électronique ou imprimée. Vous recevez cette communication car vous faites partie des contacts de WSP. Si vous avez des questions concernant la politique de communications électroniques de WSP, veuillez consulter notre Engagement anti-pourriel au www.wsp.com/lcap<http://www.wsp.com/lcap>. Pour toute question ou si vous croyez que vous ne devriez pas recevoir ce message, prière de le transférer au conformitelcap at wsp.com<mailto:conformitelcap at wsp.com> afin que nous puissions rapidement traiter votre demande. Notez que ce ne sont pas tous les messages transmis par WSP qui constituent des messages electroniques commerciaux.
-LAEmHhHzdJzBlTWfa4Hgs7pbKl
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20171213/f5f6cb29/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image009.png
Type: image/png
Size: 42752 bytes
Desc: image009.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20171213/f5f6cb29/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image010.png
Type: image/png
Size: 25844 bytes
Desc: image010.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20171213/f5f6cb29/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.jpg
Type: image/jpeg
Size: 1517 bytes
Desc: image004.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20171213/f5f6cb29/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image006.jpg
Type: image/jpeg
Size: 1647 bytes
Desc: image006.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20171213/f5f6cb29/attachment-0001.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image008.png
Type: image/png
Size: 3859 bytes
Desc: image008.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20171213/f5f6cb29/attachment-0002.png>
More information about the Equest-users
mailing list