[Equest-users] How Does the Chiller Water Economizer Work by Itself?

Bishop, Bill bbishop at pathfinder-ea.com
Thu Dec 14 15:09:10 PST 2017


Hi Kathryn,
eQUEST has two types of water economizers:

-        Chillers of TYPE:WATER-ECONOMIZER

-        Airside cooling coil SYSTEM:WS-ECONO accessible in System -> Cooling Tab -> Economizer Tab
The system-level water-side economizer is a coil attached to a condenser-water loop. That option is the one that is not currently implemented in DOE-2.3.
The WATER-ECONOMIZER chiller is usable in DOE-2.3 and has updated capabilities in eQUEST 3.65.
The error message shown below is common and can apply to any CHW coil - not just water economizers. The error is generated by a combination of system MIN-SUPPLY-T, fan SUPPLY-DELTA-T and FAN-PLACEMENT, and CHW loop DESIGN-COOL-T.
Regards,
~Bill

William Bishop, PE, BEMP, BEAP, CEM, LEED AP | Pathfinder Engineers & Architects LLP
Senior Energy Engineer

[cid:image003.jpg at 01D37506.CA89FA10]  [cid:image010.jpg at 01D37506.CA89FA10]



134 South Fitzhugh Street                 Rochester, NY 14608

T: (585) 698-1956                        F: (585) 325-6005

bbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com>             www.pathfinder-ea.com<http://www.pathfinder-ea.com/>

[http://png-5.findicons.com/files/icons/977/rrze/720/globe.png]Carbon Fee and Dividend - simple, effective, and market-based.


From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Kathryn Kerns via Equest-users
Sent: Tuesday, November 14, 2017 7:47 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] How Does the Chiller Water Economizer Work by Itself?

Everyone,  I am told that the water economizer function attached to the PVVT and other HVAC systems isn't supported by eQuest anymore although it does appear to work and produce reasonable answers. Is this correct? If so is there some other way of introducing a water economizer to a zone for cooling purposes? I have attached a *.inp file with a water tower, condenser loop, water economizer chiller, chw loop attached to a SZRH system in an interior zone with a 10 w/sqft process load and an 80 F cooling setpoint. It is computer server room. I want this cooling system to cool the interior space as much as possible but I can't figure out to get the loops to even run, let alone cool. The error message that shows up is:

[cid:image012.jpg at 01D37506.CA89FA10]

If there is no regular chiller, only the water economizer, does anybody know what condenser, chilled water loop and water economizer parameters you have to set to get this to work? Surely the model should run and cool the zone somewhat?

And can someone tell me why the water economizer function is not supported? It seems to work.
I would really like to hear from the folks who supports the eQuest software because I find all this very confusing.

Kathryn Kerns
Systems Specialist
BCE Engineers, Inc.
| Ph: 253.922.0446 | Fx: 253.922.0896 |

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20171214/949f0cbe/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 1517 bytes
Desc: image003.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20171214/949f0cbe/attachment-0012.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image010.jpg
Type: image/jpeg
Size: 1647 bytes
Desc: image010.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20171214/949f0cbe/attachment-0013.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image011.png
Type: image/png
Size: 3852 bytes
Desc: image011.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20171214/949f0cbe/attachment-0004.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image012.jpg
Type: image/jpeg
Size: 19441 bytes
Desc: image012.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20171214/949f0cbe/attachment-0014.jpg>


More information about the Equest-users mailing list