[Equest-users] Supply air temperature reset based on return air temperature on eQuest

Sharad Kumar sharadcapricious at gmail.com
Thu Dec 14 08:59:08 PST 2017


Hi Gamage,

As per me at the higher return air temperature the supply leaving air
temperature should be set to the higher values among all. It can be kept as
lower temp among all but it will have to cool the air drastically.
Also at lower return air temperature the supply leaving air temperature
should be higher value among the two supply leaving air temperature.


In eQuest the following method is used to have the reset temperature in the
Air side.

The outside temperature can be used as supply air temperature.
Here is the snapshot for that which you can link in the cooling side in th
Air side as the Cold deck schedule.


[image: Inline image 1]


The line graph obtained from the above supply temperature and supply
leaving air temperature is like this:


[image: Inline image 2]


As per this reset the temperature above and below the reset  behaves with
no temperature change. It will have another cooling side aspects
controlling it.
But as per ASHRAE 90.1 it ill be a linear functioning the SAT reset.The
temperature shall be functioning in a linear proportional way to have
increase in the temperature.
It is just an example. There can be several go around.


Thanks,
Sharad.Kumar.

........................................................................................................................................

*From:* Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] *On
Behalf Of *Gamage Lakshan via Equest-users
*Sent:* Monday, December 11, 2017 10:35 PM
*To:* equest-users at lists.onebuilding.org
*Subject:* [Equest-users] Supply air temperature reset based on return air
temperature on eQuest



Hi all,

I am trying to model supply air temperature reset based on return air
temperature on eQuest 3.64.

HVAC Input function samples on DOE2.2 Vol3- Topics provides a sample input
function for  Cold Deck Supply Air temperature reset using return air
temperature.

I am new to eQuest input functions. Does anyone know how code for HVAC
input functions should be entered to the program, is there someplace that I
can paste the sample code ? BDL file or INP file.

Some basic insight in to HVAC input functions will be highly appreciated.

Or is there an easy way to model supply air temp reset based on return air
temp.

Thanks,

Gamage Lakshan,

EE Engineer

LEED AP BD+C, BEMP, B Eng

------------------------------


NOTICE: This communication and any attachments ("this message") may contain
information which is privileged, confidential, proprietary or otherwise
subject to restricted disclosure under applicable law. This message is for
the sole use of the intended recipient(s). Any unauthorized use,
disclosure, viewing, copying, alteration, dissemination or distribution of,
or reliance on, this message is strictly prohibited. If you have received
this message in error, or you are not an authorized or intended recipient,
please notify the sender immediately by replying to this message, delete
this message and all copies from your e-mail system and destroy any printed
copies. You are receiving this communication because you are listed as a
current WSP contact. Should you have any questions regarding WSP's
electronic communications policy, please consult our Anti-Spam Commitment
at www.wsp.com/casl. For any concern or if you believe you should not be
receiving this message, please forward this message to
caslcompliance at wsp.com so that we can promptly address your request. Note
that not all messages sent by WSP qualify as commercial electronic
messages.

AVIS : Ce message, incluant tout fichier l'accompagnant (« le message »),
peut contenir des renseignements ou de l'information privilégiés,
confidentiels, propriétaires ou à divulgation restreinte en vertu de la
loi. Ce message est destiné à l'usage exclusif du/des destinataire(s)
voulu(s). Toute utilisation non permise, divulgation, lecture,
reproduction, modification, diffusion ou distribution est interdite. Si
vous avez reçu ce message par erreur, ou que vous n'êtes pas un
destinataire autorisé ou voulu, veuillez en aviser l'expéditeur
immédiatement et détruire le message et toute copie électronique ou
imprimée. Vous recevez cette communication car vous faites partie des
contacts de WSP. Si vous avez des questions concernant la politique de
communications électroniques de WSP, veuillez consulter notre Engagement
anti-pourriel au www.wsp.com/lcap. Pour toute question ou si vous croyez
que vous ne devriez pas recevoir ce message, prière de le transférer au
conformitelcap at wsp.com afin que nous puissions rapidement traiter votre
demande. Notez que ce ne sont pas tous les messages transmis par WSP qui
constituent des messages electroniques commerciaux.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20171214/0072c54b/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image.png
Type: image/png
Size: 61244 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20171214/0072c54b/attachment-0008.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image.png
Type: image/png
Size: 9423 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20171214/0072c54b/attachment-0009.png>


More information about the Equest-users mailing list