[Equest-users] Supply air temperature reset based on return air temperature on eQuest

Gamage Lakshan gamagelak2 at gmail.com
Tue Dec 12 19:16:23 PST 2017


Hi Jones,

Thanks for the quick reply.

Do you know about another way that I can control the supply air temperature
based on return air temperature. Note - The HVAC design requires the AHU
fans to run at constant volume all the time to maintain room pressure.

Thanks,
Gamage

On Tue, Dec 12, 2017 at 7:37 PM, Jones, Christopher <
Christopher.r.Jones at wsp.com> wrote:

> Gamage,
>
> Input functions are not implemented in DOE2.2. This is made clear in the
> DOE22Vol3-Topics manual:
>
>
>
>
>
> *Christopher R. Jones*, P.Eng.
>
> Technical Specialist
>
> Sustainability & Energy
>
>
>
> T +1 416-644-0252 <(416)%20644-0252>
>
>
>
> 2300 Yonge Street, Suite 2300
> <https://maps.google.com/?q=2300+Yonge+Street,+Suite+2300%0D+Toronto,+ON+M4P+1E4+Canada&entry=gmail&source=g>
>
> Toronto, ON M4P 1E4 Canada
> <https://maps.google.com/?q=2300+Yonge+Street,+Suite+2300%0D+Toronto,+ON+M4P+1E4+Canada&entry=gmail&source=g>
>
> wsp.com
>
>
>
>
>
> *Please consider the environment before printing...*
>
>
>
>
>
> *From:* Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] *On
> Behalf Of *Gamage Lakshan via Equest-users
> *Sent:* Monday, December 11, 2017 10:35 PM
> *To:* equest-users at lists.onebuilding.org
> *Subject:* [Equest-users] Supply air temperature reset based on return
> air temperature on eQuest
>
>
>
> Hi all,
>
> I am trying to model supply air temperature reset based on return air
> temperature on eQuest 3.64.
>
> HVAC Input function samples on DOE2.2 Vol3- Topics provides a sample input
> function for  Cold Deck Supply Air temperature reset using return air
> temperature.
>
> I am new to eQuest input functions. Does anyone know how code for HVAC
> input functions should be entered to the program, is there someplace that I
> can paste the sample code ? BDL file or INP file.
>
> Some basic insight in to HVAC input functions will be highly appreciated.
>
> Or is there an easy way to model supply air temp reset based on return air
> temp.
>
> Thanks,
>
> Gamage Lakshan,
>
> EE Engineer
>
> LEED AP BD+C, BEMP, B Eng
>
> ------------------------------
>
>
> NOTICE: This communication and any attachments ("this message") may
> contain information which is privileged, confidential, proprietary or
> otherwise subject to restricted disclosure under applicable law. This
> message is for the sole use of the intended recipient(s). Any unauthorized
> use, disclosure, viewing, copying, alteration, dissemination or
> distribution of, or reliance on, this message is strictly prohibited. If
> you have received this message in error, or you are not an authorized or
> intended recipient, please notify the sender immediately by replying to
> this message, delete this message and all copies from your e-mail system
> and destroy any printed copies. You are receiving this communication
> because you are listed as a current WSP contact. Should you have any
> questions regarding WSP's electronic communications policy, please consult
> our Anti-Spam Commitment at www.wsp.com/casl. For any concern or if you
> believe you should not be receiving this message, please forward this
> message to caslcompliance at wsp.com so that we can promptly address your
> request. Note that not all messages sent by WSP qualify as commercial
> electronic messages.
>
> AVIS : Ce message, incluant tout fichier l'accompagnant (« le message »),
> peut contenir des renseignements ou de l'information privilégiés,
> confidentiels, propriétaires ou à divulgation restreinte en vertu de la
> loi. Ce message est destiné à l'usage exclusif du/des destinataire(s)
> voulu(s). Toute utilisation non permise, divulgation, lecture,
> reproduction, modification, diffusion ou distribution est interdite. Si
> vous avez reçu ce message par erreur, ou que vous n'êtes pas un
> destinataire autorisé ou voulu, veuillez en aviser l'expéditeur
> immédiatement et détruire le message et toute copie électronique ou
> imprimée. Vous recevez cette communication car vous faites partie des
> contacts de WSP. Si vous avez des questions concernant la politique de
> communications électroniques de WSP, veuillez consulter notre Engagement
> anti-pourriel au www.wsp.com/lcap. Pour toute question ou si vous croyez
> que vous ne devriez pas recevoir ce message, prière de le transférer au
> conformitelcap at wsp.com afin que nous puissions rapidement traiter votre
> demande. Notez que ce ne sont pas tous les messages transmis par WSP qui
> constituent des messages electroniques commerciaux.
>
>
>
> -LAEmHhHzdJzBlTWfa4Hgs7pbKl
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20171213/590741c0/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 25844 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20171213/590741c0/attachment-0008.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 42752 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20171213/590741c0/attachment-0009.png>


More information about the Equest-users mailing list