[Equest-users] Define unique SUPPLY-FLOW for heating and cooling modes for a PSZ or PVVT system?
Phil Jordan via Equest-users
equest-users at lists.onebuilding.org
Wed Aug 23 12:01:32 PDT 2017
Thanks, Bill.
How about, for PVVT, is it possible to set a unique supply flow per cooling (or heating) stage? Could the hourly value of the COOL-STAGE keyword be used in a BDL expression to dictate SUPPLY-FLOW?
Thanks,
Phil
________________________________
From: Bishop, Bill <bbishop at pathfinder-ea.com>
Sent: Wednesday, August 16, 2017 1:50 PM
To: Phil Jordan
Cc: equest-users at lists.onebuilding.org
Subject: RE: [Equest-users] Define unique SUPPLY-FLOW for heating and cooling modes for a PSZ or PVVT system?
Hi Phil,
No, not exactly. But you can specify different system MIN-FLOW-RATIOs for cooling mode and heating mode.
For your example, you can set HMIN-FLOW-RATIO to 550/800 = 0.6875.
You would also need to change the FAN-CONTROL to something other than CONSTANT-VOLUME for PSZ systems.
For VAVS and PVAVS systems, you also have the option of specifying an HMAX-FLOW-RATIO, but not greater than 1.0.
You can change these values at the zone level as well.
Regards,
~Bill
William Bishop, PE, BEMP, BEAP, CEM, LEED AP | Pathfinder Engineers & Architects LLP
Senior Energy Engineer
[cid:image007.jpg at 01D316AF.D61A6BE0] [cid:image008.jpg at 01D316AF.D61A6BE0]
134 South Fitzhugh Street Rochester, NY 14608
T: (585) 698-1956 F: (585) 325-6005
bbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com> www.pathfinder-ea.com<http://www.pathfinder-ea.com/>
[http://png-5.findicons.com/files/icons/977/rrze/720/globe.png]Carbon Fee and Dividend - simple, effective, and market-based.
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Phil Jordan via Equest-users
Sent: Wednesday, August 16, 2017 4:32 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Define unique SUPPLY-FLOW for heating and cooling modes for a PSZ or PVVT system?
With a PSZ or PVVT system type in eQUEST, is it possible to define a different supply airflow in heating vs cooling mode (ex. 800 CFM in cooling mode; 550 CFM in heating mode)? If so, how can this be done? Thanks!
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170823/fcebec93/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image007.jpg
Type: image/jpeg
Size: 1517 bytes
Desc: image007.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170823/fcebec93/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image008.jpg
Type: image/jpeg
Size: 1647 bytes
Desc: image008.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170823/fcebec93/attachment-0001.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image009.png
Type: image/png
Size: 3858 bytes
Desc: image009.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170823/fcebec93/attachment.png>
More information about the Equest-users
mailing list