[Equest-users] DOAS MIN-AIR-SCH - schedule values for economizing?
Bishop, Bill via Equest-users
equest-users at lists.onebuilding.org
Fri Aug 18 12:02:26 PDT 2017
A value of 0.001 in the MIN-AIR-SCH activates an air-side economizer, allowing a unit to provide cooling by varying the volume of outside air.
In a dedicated outdoor air system (DOAS) or other air-side system with 100% outside air, hourly values of the MIN-AIR-SCH should be 1.0.
What about a 100% OA system with variable flow?
I think the hourly values in the MIN-AIR-SCH should still be set to 1.0 for all hours. Hourly reports in my tests show the flowrate increasing above the MIN-FLOW-RATIO during cooling conditions, while the OA is still at 100%.
If I use 0.001 in the MIN-AIR-SCH, the hourly OA% drops way below 100%.
Does this seem right?
Thanks,
~Bill
Custom hourly reports can show the flowrate and OA% of air handlers. This is a typical BDL input for hourly reporting of total system supply air flow rate and OA ratio, in this case for a system "RVU-2":
"RVU-2 Hourly Block" = REPORT-BLOCK
VARIABLE-TYPE = "RVU-2"
VARIABLE-LIST = ( 17, 39 )
..
"Hourly Report" = HOURLY-REPORT
LIBRARY-ENTRY "Hourly Report"
REPORT-BLOCK = ( "EM1 Hourly Report Block", "FM1 Hourly Report Block",
"RVU-2 Hourly Block" )
..
William Bishop, PE, BEMP, BEAP, CEM, LEED AP | Pathfinder Engineers & Architects LLP
Senior Energy Engineer
[cid:image007.jpg at 01D31833.1865A670] [cid:image008.jpg at 01D31833.1865A670]
134 South Fitzhugh Street Rochester, NY 14608
T: (585) 698-1956 F: (585) 325-6005
bbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com> www.pathfinder-ea.com<http://www.pathfinder-ea.com/>
[http://png-5.findicons.com/files/icons/977/rrze/720/globe.png]Carbon Fee and Dividend - simple, effective, and market-based.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170818/66cb1ba8/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image007.jpg
Type: image/jpeg
Size: 1517 bytes
Desc: image007.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170818/66cb1ba8/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image008.jpg
Type: image/jpeg
Size: 1647 bytes
Desc: image008.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170818/66cb1ba8/attachment-0001.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image009.png
Type: image/png
Size: 3862 bytes
Desc: image009.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170818/66cb1ba8/attachment.png>
More information about the Equest-users
mailing list