[Equest-users] Building Peak Cooling Load
Nicholas Caton via Equest-users
equest-users at lists.onebuilding.org
Wed Aug 30 15:32:34 PDT 2017
As a general practice I’d advise referencing the net peak listed for the baseline CHW loop in the PS-D report for determining plant peak cooling load, independent of chiller distribution.
One difference between the numbers is that where SS-D is simply the peak load seen at the HVAC coils, the PS-D figure incorporates heat of CHW pumping & distribution, which is additionally handled at the primary equipment. I’m not sure if that explains the whole gap you’re seeing, but that’d be a part of it.
~Nick
[cid:image001.png at 01D321B5.8BBE0640]
Nick Caton, P.E., BEMP
Senior Energy Engineer
Regional Energy Engineering Manager
Energy and Sustainability Services
Schneider Electric
D 913.564.6361
M 785.410.3317
F 913.564.6380
E nicholas.caton at schneider-electric.com<mailto:nicholas.caton at schneider-electric.com>
15200 Santa Fe Trail Drive
Suite 204
Lenexa, KS 66219
United States
[cid:image002.png at 01D321B5.8BBE0640]
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of siddharth patil via Equest-users
Sent: Wednesday, August 30, 2017 4:42 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Building Peak Cooling Load
Hello,
Which report shows actual building peak cooling load? Is it the SS-D report? I am modeling ASHRAE 90.1 2007 system 8 - VAV w/PFP boxes and have chillers in baseline case. Shall I look at the SS-D report peak cooling load or PS-C equipment peak cooling load? I am getting different values in both reports(SS-D = 529.22 tons and PS-C = 642 tons).
Siddharth
[https://mailfoogae.appspot.com/t?sender=acGF0aWxzaWRkaGFydGg1QGdtYWlsLmNvbQ%3D%3D&type=zerocontent&guid=0153a4ea-0cb9-4206-ae68-6efcf4307fbf]ᐧ
______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170830/38d48fcf/attachment-0004.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 255 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170830/38d48fcf/attachment-0008.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 8477 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170830/38d48fcf/attachment-0009.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: oledata.mso
Type: application/octet-stream
Size: 7132 bytes
Desc: oledata.mso
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170830/38d48fcf/attachment-0004.obj>
More information about the Equest-users
mailing list