[Equest-users] I missed you guys and I feel like sharing

Jones, Christopher via Equest-users equest-users at lists.onebuilding.org
Wed Aug 16 12:47:13 PDT 2017


Thank you Bill,
I am wondering if there is a UDF means to determine the parent floor name of the spaces in the model?


Christopher R. Jones, P.Eng.
Technical Specialist
Sustainability & Energy

[cid:image001.png at 01D316A6.E688BEE0]
T +1 416-644-0252

2300 Yonge Street, Suite 2300
Toronto, ON M4P 1E4 Canada

wsp.com


Please consider the environment before printing...


From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Bishop, Bill via Equest-users
Sent: Wednesday, August 16, 2017 3:35 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] I missed you guys and I feel like sharing

I've been too clueless to notice that I haven't gotten eQUEST-users messages since May. I blocked Rodrigo's vacation messages which we all got 500 of and everything else was blocked too...

So here's a random Tip-of-the-Day!
Create custom User-Defined Default Expressions that set system and/or zone defaults based on the occurrence number of the system.
Example:
Your project uses 12 systems - five PVAV systems, five PSZ systems, one HVSYS and one UVT, and the order you created them is PVAV-1, PVAV-2,...,PVAV-5, PSZ-1,...,PSZ-5, HVSYS, UVT
The corresponding occurrence numbers for these systems is 1,2,3,4,5,6,7,8,9,10,11,12.
Using the BDL function SymValue combined with LocalSym or ParentSym, you can create expressions such as this one, which assigns different zone cooling thermostat schedules based on the system the zone is assigned to:
   COOL-TEMP-SCH    =
{if (#SV(#PS())==1 .OR. #SV(#PS())==7) then
   #SI("72F Cool Sch", "ZONE", "COOL-TEMP-SCH")
  else if (#SV(#PS())>10) then unused
         else #SI("74F Cool Sch", "ZONE", "COOL-TEMP-SCH")
       endif
endif}

You could make the same assignments with a SWITCH statement:
   COOL-TEMP-SCH    =
{switch #SV(#PS())
   case  1 : #SI("72F Cool Sch", "ZONE", "COOL-TEMP-SCH")
   case  7 : #SI("72F Cool Sch", "ZONE", "COOL-TEMP-SCH")
   case 11 : unused
   case 12 : unused
   default : #SI("74F Cool Sch", "ZONE", "COOL-TEMP-SCH")
endswitch}

You would use the BDL function LocalSym to assign SYSTEM keywords by system occurrence number. Since each system TYPE has its own keyword defaults, you would need to customize the expression for each system type, or copy the same expression into each of the system types you want to apply it to.
   COOLING-EIR      =
{switch #SV(#LS())
   case 1  : 0.2945  $ PVAV-1
   case 2  : 0.3051  $ PVAV-2
   case 3  : 0.2945  $ PVAV-3
   case 4  : 0.2945  $ PVAV-4
   case 5  : 0.3051  $ PVAV-5
   case 7  : 0.3283  $ PSZ-2
   default : 0.2267  $ All other systems for which this expression is used
endswitch}

Regards,
~Bill

William Bishop, PE, BEMP, BEAP, CEM, LEED AP | Pathfinder Engineers & Architects LLP
Senior Energy Engineer

[cid:image002.jpg at 01D316A6.E68FEAD0]  [cid:image004.jpg at 01D316A6.E68FEAD0]



134 South Fitzhugh Street                 Rochester, NY 14608

T: (585) 698-1956                        F: (585) 325-6005

bbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com>             www.pathfinder-ea.com<http://www.pathfinder-ea.com/>

[http://png-5.findicons.com/files/icons/977/rrze/720/globe.png]Carbon Fee and Dividend - simple, effective, and market-based.




________________________________


You are receiving this communication because you are listed as a current WSP contact. Should you have any questions regarding WSP's electronic communications policy, please consult our Anti-Spam Commitment www.wsp.com/casl<http://www.wsp.com/casl>. For any concern or if you believe you should not be receiving this message, please forward this message to caslcompliance at wsp.com<mailto:caslcompliance at wsp.com> so that we can promptly address your request. This message is intended only for the addressee and may contain information which is privileged, confidential, proprietary, or exempt from disclosure under applicable law. If you are not the intended recipient, you are strictly prohibited from disclosing, distributing, copying, or in any way using this message. If you have received this communication in error, please notify the sender and delete any copies you may have received.

----------------------------------------------------------------------------------------------------------------------------------------

Vous recevez cette communication car vous faites partie des contacts de WSP. Si vous avez des questions concernant la politique de communications ?lectroniques de WSP, veuillez consulter notre Engagement anti-pourriel www.wsp.com/lcap<http://www.wsp.com/casl>. Pour toute question ou si vous croyez que vous ne devriez pas recevoir ce message, pri?re de le transf?rer au conformitelcap at wsp.com<mailto:conformitelcap at wsp.com> afin que nous puissions rapidement traiter votre demande. Ce message est destin? uniquement au destinataire et il peut contenir des informations privil?gi?es, confidentielles ou non divulgables en vertu de la loi. Si vous n'?tes pas le destinataire du pr?sent message, il vous est strictement interdit de le divulguer, de le distribuer, de le copier ou de l'utiliser de quelque fa?on que ce soit. Si vous avez re?u la pr?sente communication par erreur, veuillez en aviser l'exp?diteur et supprimer le message.

______________________________________________________________________
NOTICE: This communication and any attachments ("this message") may contain confidential information for the sole use of the intended recipient(s). Any unauthorized use, disclosure, viewing, copying, alteration, dissemination or distribution of, or reliance on this message is strictly prohibited. If you have received this message in error, or you are not an authorized recipient, please notify the sender immediately by replying to this message, delete this message and all copies from your e-mail system and destroy any printed copies.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170816/64cc27ba/attachment-0004.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 25844 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170816/64cc27ba/attachment-0008.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 1240 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170816/64cc27ba/attachment-0008.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.jpg
Type: image/jpeg
Size: 1309 bytes
Desc: image004.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170816/64cc27ba/attachment-0009.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image006.png
Type: image/png
Size: 2847 bytes
Desc: image006.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170816/64cc27ba/attachment-0009.png>


More information about the Equest-users mailing list