[Equest-users] Resolving equest error messages

Ilana Cember via Equest-users equest-users at lists.onebuilding.org
Wed Apr 12 08:37:11 PDT 2017


Hi team - I'm getting the following error messages for my multi-family midrise (see attached attn review report):
For my residential areas: "System has unused exhaust cfm specified. This has been converted to outside air."
For my other areas: "Min OA without using assigned cfm to raise total zone flow."

I'm guessing this has something to do with incorrectly modeling exhaust? The residential areas only have toilet exhaust, which I've entered as exhaust cfm in the zone group DD screen. The other areas have dedicated return to rooftop units or exhausts, which I've also entered as exhaust in the zone group DD screen.

I'm also getting errors for "heating capacity is inconsistent with cooling capacity," but I've entered in the capacities from the design documents. (Residential areas have PTHP and other areas have AC or RTUs with EUH.) Attached are the INP and PD2 files.

Any suggestions are welcome. Thank you!

Regards,
Ilana

ILANA CEMBER, PE, CEM, LEED Green Assoc
COMMISSIONING AND ENERGY ENGINEER
[cid:image001.png at 01D11184.F926CD40]
180 N LaSalle | Suite 2210 | Chicago, IL 60201
main +1 312 386 7710 | direct +1 312 386 7705 | cell +1 312 721 8507
email i.cember@@baumann-us.com<mailto:k.adighije at baumann-us.com>
www.baumann-us.com<http://www.baumann-us.com/>
[In-2C-14px]<https://www.linkedin.com/company/baumann-consulting>

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170412/02438cc6/attachment-0004.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.jpg
Type: image/jpeg
Size: 3182 bytes
Desc: image005.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170412/02438cc6/attachment-0005.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image006.png
Type: image/png
Size: 823 bytes
Desc: image006.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170412/02438cc6/attachment-0005.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: U385 Marshall Hotel vOB.INP
Type: application/octet-stream
Size: 527798 bytes
Desc: U385 Marshall Hotel vOB.INP
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170412/02438cc6/attachment-0010.obj>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: U385 Marshall Hotel vOB.PD2
Type: application/octet-stream
Size: 65102 bytes
Desc: U385 Marshall Hotel vOB.PD2
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170412/02438cc6/attachment-0011.obj>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Attn Review Report.pdf
Type: application/pdf
Size: 51038 bytes
Desc: Attn Review Report.pdf
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170412/02438cc6/attachment-0005.pdf>


More information about the Equest-users mailing list