[Equest-users] Outside wall to outside wall
John Aulbach via Equest-users
equest-users at lists.onebuilding.org
Fri Sep 2 07:32:26 PDT 2016
Too many tag emails !!
Nick, remember, this is only the two side walls to remain. Everything else is to be gutted and replaced. So the Base is two side mass walls, and front/back are steel frame ?? Never build a building this way !!
John
On Friday, September 2, 2016 7:20 AM, "Etherington, Dana" <detherington at RDKEngineers.com> wrote:
<!--#yiv8403078121 _filtered #yiv8403078121 {font-family:Helvetica;panose-1:2 0 5 0 0 0 0 0 0 0;} _filtered #yiv8403078121 {font-family:"Cambria Math";panose-1:2 4 5 3 5 4 6 3 2 4;} _filtered #yiv8403078121 {font-family:Calibri;panose-1:2 15 5 2 2 2 4 3 2 4;} _filtered #yiv8403078121 {font-family:Verdana;panose-1:2 11 6 4 3 5 4 4 2 4;} _filtered #yiv8403078121 {font-family:Tahoma;panose-1:2 11 6 4 3 5 4 4 2 4;}#yiv8403078121 #yiv8403078121 p.yiv8403078121MsoNormal, #yiv8403078121 li.yiv8403078121MsoNormal, #yiv8403078121 div.yiv8403078121MsoNormal {margin:0in;margin-bottom:.0001pt;font-size:12.0pt;font-family:"Times New Roman", serif;}#yiv8403078121 a:link, #yiv8403078121 span.yiv8403078121MsoHyperlink {color:blue;text-decoration:underline;}#yiv8403078121 a:visited, #yiv8403078121 span.yiv8403078121MsoHyperlinkFollowed {color:purple;text-decoration:underline;}#yiv8403078121 p.yiv8403078121MsoAcetate, #yiv8403078121 li.yiv8403078121MsoAcetate, #yiv8403078121 div.yiv8403078121MsoAcetate {margin:0in;margin-bottom:.0001pt;font-size:8.0pt;font-family:"Tahoma", sans-serif;}#yiv8403078121 span.yiv8403078121BalloonTextChar {font-family:"Tahoma", sans-serif;}#yiv8403078121 p.yiv8403078121msoacetate, #yiv8403078121 li.yiv8403078121msoacetate, #yiv8403078121 div.yiv8403078121msoacetate {margin-right:0in;margin-left:0in;font-size:12.0pt;font-family:"Times New Roman", serif;}#yiv8403078121 p.yiv8403078121msonormal, #yiv8403078121 li.yiv8403078121msonormal, #yiv8403078121 div.yiv8403078121msonormal {margin-right:0in;margin-left:0in;font-size:12.0pt;font-family:"Times New Roman", serif;}#yiv8403078121 p.yiv8403078121msochpdefault, #yiv8403078121 li.yiv8403078121msochpdefault, #yiv8403078121 div.yiv8403078121msochpdefault {margin-right:0in;margin-left:0in;font-size:12.0pt;font-family:"Times New Roman", serif;}#yiv8403078121 p.yiv8403078121msonormal1, #yiv8403078121 li.yiv8403078121msonormal1, #yiv8403078121 div.yiv8403078121msonormal1 {margin-right:0in;margin-left:0in;font-size:12.0pt;font-family:"Times New Roman", serif;}#yiv8403078121 p.yiv8403078121msochpdefault1, #yiv8403078121 li.yiv8403078121msochpdefault1, #yiv8403078121 div.yiv8403078121msochpdefault1 {margin-right:0in;margin-left:0in;font-size:12.0pt;font-family:"Times New Roman", serif;}#yiv8403078121 p.yiv8403078121msonormal2, #yiv8403078121 li.yiv8403078121msonormal2, #yiv8403078121 div.yiv8403078121msonormal2 {margin:0in;margin-bottom:.0001pt;font-size:12.0pt;font-family:"Times New Roman", serif;}#yiv8403078121 p.yiv8403078121msoacetate1, #yiv8403078121 li.yiv8403078121msoacetate1, #yiv8403078121 div.yiv8403078121msoacetate1 {margin:0in;margin-bottom:.0001pt;font-size:8.0pt;font-family:"Times New Roman", serif;}#yiv8403078121 p.yiv8403078121msonormal3, #yiv8403078121 li.yiv8403078121msonormal3, #yiv8403078121 div.yiv8403078121msonormal3 {margin-right:0in;margin-left:0in;font-size:12.0pt;font-family:"Times New Roman", serif;}#yiv8403078121 p.yiv8403078121msochpdefault2, #yiv8403078121 li.yiv8403078121msochpdefault2, #yiv8403078121 div.yiv8403078121msochpdefault2 {margin-right:0in;margin-left:0in;font-size:12.0pt;font-family:"Times New Roman", serif;}#yiv8403078121 p.yiv8403078121msonormal11, #yiv8403078121 li.yiv8403078121msonormal11, #yiv8403078121 div.yiv8403078121msonormal11 {margin:0in;margin-bottom:.0001pt;font-size:12.0pt;font-family:"Times New Roman", serif;}#yiv8403078121 p.yiv8403078121msochpdefault11, #yiv8403078121 li.yiv8403078121msochpdefault11, #yiv8403078121 div.yiv8403078121msochpdefault11 {margin-right:0in;margin-left:0in;font-size:10.0pt;font-family:"Times New Roman", serif;}#yiv8403078121 span.yiv8403078121msohyperlink {}#yiv8403078121 span.yiv8403078121msohyperlinkfollowed {}#yiv8403078121 span.yiv8403078121msohyperlink1 {}#yiv8403078121 span.yiv8403078121msohyperlinkfollowed1 {}#yiv8403078121 span.yiv8403078121emailstyle171 {}#yiv8403078121 span.yiv8403078121emailstyle27 {}#yiv8403078121 span.yiv8403078121msohyperlink2 {color:blue;text-decoration:underline;}#yiv8403078121 span.yiv8403078121msohyperlinkfollowed2 {color:purple;text-decoration:underline;}#yiv8403078121 span.yiv8403078121msohyperlink11 {color:#0563C1;text-decoration:underline;}#yiv8403078121 span.yiv8403078121msohyperlinkfollowed11 {color:#954F72;text-decoration:underline;}#yiv8403078121 span.yiv8403078121emailstyle1711 {color:#1F497D;}#yiv8403078121 span.yiv8403078121emailstyle271 {color:#1F497D;}#yiv8403078121 span.yiv8403078121EmailStyle42 {font-family:"Calibri", sans-serif;color:#1F497D;}#yiv8403078121 span.yiv8403078121EmailStyle43 {font-family:"Calibri", sans-serif;color:#1F497D;}#yiv8403078121 span.yiv8403078121EmailStyle44 {font-family:"Calibri", sans-serif;color:#1F497D;}#yiv8403078121 span.yiv8403078121EmailStyle45 {font-family:"Calibri", sans-serif;color:windowtext;}#yiv8403078121 .yiv8403078121MsoChpDefault {font-size:10.0pt;} _filtered #yiv8403078121 {margin:1.0in 1.0in 1.0in 1.0in;}#yiv8403078121 div.yiv8403078121WordSection1 {}-->Hi Folks, Just a heads up that this language is removed from 90.1 – 2013. We’ll still be able to get the point bumps on LEED v4 projects since the baseline is 90.1 – 2010, but it will impact new code adoption in certain states. There are also key changes to the window to wall ratio baseline requirements and baseline building rotation. We’ve been prepping for the imminent code changes in MA and have had to deal with these things…. Good luck with that project John! -Dana ---- Dana Etherington | PE, CEM, BEMP, WELL AP RDK Engineers P: (857) 221-5920 | C: (617) 583-3009 | F: (617) 345-4226 From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org]On Behalf Of via Equest-users
Sent: Friday, September 02, 2016 9:57 AM
To: CBaker at cci-alliance.com; jra_sac at yahoo.com
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Outside wall to outside wall Confirming – that language remains in 90.1-2010. I’ve had similar experiences with old concrete & masonry buildings (zero insulation), where that’s turned out to be a boon for the likes of LEED points. Also since it sounds like you’re dancing with compliance, be advised for any prescriptive purposes those concrete walls are most likely amass wall by 90.1 definitions. Sounds like a fun one alright! Nick Caton, P.E.
| Senior Energy Engineer
Energy and Sustainability Services
Schneider Electric | D 913.564.6361
M 785.410.3317
E nicholas.caton at schneider-electric.com
F 913.564.6380 | 15200 Santa Fe Trail Drive
Suite 204
Lenexa, KS 66219
United States |
| |
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org]On Behalf Of Chris Baker via Equest-users
Sent: Thursday, September 01, 2016 7:01 PM
To: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Outside wall to outside wall John, It would be worth checking in the tables in Appendix G – however, there used to be the following wording at the bottom of the baseline performance column… Existing Buildings. For existingbuilding envelopes, the baseline building designshall reflect existing conditions prior to any revisions that are part of the scope of work being evaluated. This one is from ASHRAE 90.1 (2007) and I’m not sure if it is in the 2010 version but it would be worth a look. Though modeling 1855 concrete side walls would be a different issue, entirely! LOL. Good luck, sir! Chris Baker CCI Alliance of Companies Fort Wainwright, AK From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org]On Behalf Of John Aulbach via Equest-users
Sent: Thursday, September 01, 2016 3:32 PM
To: Nicholas.Caton at schneider-electric.com;nathanm at rushingco.com
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Outside wall to outside wall Thanks, Nick. I have an even more interesting scenario. This building was built originally in 1855 (yes, even before me and 19 years after the Battle of the Alamo)). The owners will leave the concrete 1855 side walls (I think I will let them be totally shaded outside walls), gut the rest of the building, and rebuild a 5 story single residence (no, not one of the Trump kids). SO..for the City of New York 2011 Energy Code (2014 doesn't take place until October, 2016), we use ASHRAE 90.1-2010. Good old Appendix G (as I interpret it) say that, for either New or Alterations, the Base model is Steel Frame. ALL of it. So I don't apply the 1855 walls (with some added insulation) until the Proposed Run (Thank GOD I don't have to spin the building like LEED). Does this base building approach seem correct to you? Don't forget. I am originally a Chicago boy. John On Thursday, September 1, 2016 3:19 PM, "Nicholas.Caton at schneider-electric.com" <Nicholas.Caton at schneider-electric.com> wrote: John, looks like this didn’t leave my outbox… sorry! Give me time to refine my response: How I’d react would depend on my motives/goals. Ideally, I’d like to find & assert both neighbors are conditioned to similar temperatures and therefore declare no substantive heat transfer: adiabatic surfaces with thermal mass to effect hourly heat storage/transfer lag. This is probably accurate enough (in-aggregate) for many cases, short of exposed walls where one building is taller than another. Conservatively– Nathan’s suggestion is the ticket however. If there’s going to be appreciable heat transfer, you’re now in a position to decide where to draw a line in the sand: what’s your worst-case? This may be the more appropriate response if you’re doing simulation to aid/inform equipment sizing or if you know of planned demolition/renovations in the neighboring spaces. I can say short of FEMA shelters and the like (this is tornado country…), I don’t normally make the destruction of an attached portion of my buildings a part of my design calculations or energy simulations, but you might have some good reasons to pull that possibility into the picture. Applying the likes of 90.1 conditioned envelope definitions notably gets a little trickier if you have an enclosed or partially enclosed gap between the buildings. If you’re heading down a 90.1/LEED based simulation path or something similar for compliance, look hard for shared wall/space construction details on that front to understand what exactly lies beyond your“envelope.” Finally, I notice you mentioned an disquieting location: New York City (or NEW YORK CITY?!? as we say in the midwest). I want to say there was a mailing list discussion on this exact issue in relation to NY’s energy standards some time back either in equest-users or bldg-sim… but on cursory searching I’m having trouble finding it… suggest digging the archives further! ~Nick Nick Caton, P.E.
| Senior Energy Engineer
Energy and Sustainability Services
Schneider Electric | D 913.564.6361
M 785.410.3317
E nicholas.caton at schneider-electric.com
F 913.564.6380 | 15200 Santa Fe Trail Drive
Suite 204
Lenexa, KS 66219
United States |
| |
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org]On Behalf Of John Aulbach via Equest-users
Sent: Thursday, September 01, 2016 4:09 PM
To: Nathan Miller
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Outside wall to outside wall Thank you all. I just had to shake the trees to jog my DOE-2.1 memory. A fully shaded outdoor wall is probably the best way, so thank you all. John On Thursday, September 1, 2016 1:17 PM, Nathan Miller <nathanm at rushingco.com> wrote: Tough call, but I’d probably be conservative and err on the side of making assumptions that result in MORE energy consumption in my modeling (unless there is some benchmarking you can compare to). That means I’d probably assume the walls are exterior and fully shaded. There is a pretty good chance there is at least small dead-air-space between the buildings (even if it is only a few inches), plus you have no control over what is happening on the other side of the wall… maybe the neighboring building is minimally conditioned, or becomes abandoned. Nathan Miller, PE, LEED AP BD+C–Mechanical Engineer/Senior Energy Analyst RUSHING |D 206-788-4577 | O 206-285-7100 | C 207-650-3942 www.rushingco.com From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org]On Behalf Of John Aulbach via Equest-users
Sent: Wednesday, August 31, 2016 5:42 PM
To: via Equest-users <equest-users at lists.onebuilding.org>
Subject: [Equest-users] Outside wall to outside wall Hi Gang: Food (and query) for thought. I am doing a remodel of a New York Building that is essentially a tenement (?). Building squished between other buildings. Side walls essentially lay against next building. Inside wall? Outside wall with no solar? How would you model this? John R. Aulbach, PE
______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
CCI-Alliance Confidentiality notice: This message is intended only for the person to whom addressed in the text above and may contain privileged or confidential information. If you are not that person, any use of this message is prohibited. We request that you notify us by reply to this message, and then delete all copies of this message including any contained in your reply. Thank you.
______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160902/f2ff2d58/attachment-0005.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 255 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160902/f2ff2d58/attachment-0010.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 7893 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160902/f2ff2d58/attachment-0011.png>
More information about the Equest-users
mailing list