Yep - Julien has the right idea!

The other input of interest for your case is that at the same input screen, you can select the exhaust source as "infiltration," which means the associated makeup airstream = outside conditions.

~Nick

Nick Caton, P.E., BEMP
  Senior Energy Engineer
  Energy and Sustainability Services
  Schneider Electric
D  913.564.6361
M  785.410.3317
E  nicholas.caton at schneider-electric.com
F  913.564.6380
15200 Santa Fe Trail Drive
Suite 204
Lenexa, KS 66219
United States



-----Original Message-----
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Julien MARREC via Equest-users
Sent: Saturday, October 15, 2016 3:41 PM
To: Darryl Kasun <darryl.kasun at gmail.com>
Cc: equest <equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] Modeling Reverse Acting TStat EF

Zonal exhaust fan has an option to control that on a temp schedule if I recall correctly.

Open the zone, tab "outside air" then at the right you can specify a zonal exhaust fan. (All this from memory so might differ slightly)

Cheers,
Julien

Envoyé de mon iPhone

> Le 15 oct. 2016 à 20:57, Darryl Kasun via Equest-users <equest-users at lists.onebuilding.org> a écrit :
>
> Hi eQUESTers,
>
> First off, you probably will not likely appreciate this and I'll preface this with saying that I'm a total bandwagon jumper but I am okay with that.
>
> GO JAYS!!!
>
> Now that that's out of the way I am trying to model a very simple system that I'm sure many of you have modeled before.
>
> I have a zone that has an exhaust fan in it.  When the temp. reaches above 80 degF, an exhaust fan turns on and a damper opens to draw OA into the zone.
>
> I've been fooling around with a few systems trying to figure out a good way to model this but haven't come up with one yet.
>
> Let me know if have any recommendations.
>
> Thanks!
> Darryl
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
________________________________
 This message was scanned by Exchange Online Protection Services.
________________________________


More information about the Equest-users mailing list