[Equest-users] ER Wheel in Baseline
Darryl Kasun via Equest-users
equest-users at lists.onebuilding.org
Mon Nov 28 21:11:43 PST 2016
Hi Aru,
Yes you are correct - you have to create an exhaust air heat recovery with
at least 50% effectiveness in your baseline bldg. Check out section
6.5.6.1 of ASHRAE 90.1 for further guidance.
Darryl Kasun, P. Eng,
Interior Engineering
On Mon, Nov 28, 2016 at 6:58 PM, Arunabha Sau via Equest-users <
equest-users at lists.onebuilding.org> wrote:
> Hello there,
>
>
> In a 5A climate zone, I am working with a Proposed model with a RTU
> (30,000 CFM, 100% OA) with exhaust air ER wheel in it. I am kinda sure that
> I've to create a ER wheel for the 90.1 Baseline (as per G3.1.2.10). Just
> want to make sure if I am correct?
>
> Help please. Thanks
>
>
> Best,
> Aru Sau
> *Architectural Sustainability | Energy Analyst*
> *analyzing the ROI of your sustainable initiatives...
> *
> *c: 678-467-7934 <678-467-7934>, **Ann Arbor, MI*
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20161128/7dfb095d/attachment-0005.htm>
More information about the Equest-users
mailing list