[Equest-users] Random Tip-of-the-Day: EQUIP-RAD-FRAC

Bishop, Bill via Equest-users equest-users at lists.onebuilding.org
Tue May 31 13:24:50 PDT 2016


You can designate the radiative/convective split of the heat gains from lighting using the LIGHT-RAD-FRAC keyword, the value for which can be accessed via the Space -> Lighting tab.
While there are (currently) no such input options for heat gains from Equipment and Internal Energy Sources, the keywords exist in DOE-2.2 and can be used in the input files for your eQUEST models.
For example, you can satisfy the requirement in PNNL's PRM Reference Manual<http://www.pnnl.gov/main/publications/external/technical_reports/PNNL-25130.pdf> for a default 20%/80% radiative/convective split for receptacle loads by adding this expression to the "SET-DEFAULT FOR SPACE" section of your input file:

   EQUIP-RAD-FRAC   = (
{if (#L("FLOOR-WEIGHT") > 0.  .or.  #RV(#L("EQUIP-SCHEDULE",0)) !=0)
  then unused
  else 0.20     /* Per PNNL-25130 90.1-2010 PRM Reference Manual */
  endif} )

The SOURCE-RAD-FRAC keyword is also available, for describing the heat gains from Internal Energy Sources.

Cheers,
~Bill

[cid:image002.png at 01D1BB58.F3BF4610]

William Bishop, PE, BEMP, BEAP, CEM, LEED AP | Pathfinder Engineers & Architects LLP
Senior Energy Engineer

[cid:image004.jpg at 01D1BB58.F3BF4610]  [cid:image006.jpg at 01D1BB58.F3BF4610]



134 South Fitzhugh Street                 Rochester, NY 14608

T: (585) 698-1956                        F: (585) 325-6005

bbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com>             www.pathfinder-ea.com<http://www.pathfinder-ea.com/>

[http://png-5.findicons.com/files/icons/977/rrze/720/globe.png]Carbon Fee and Dividend - simple, effective, and market-based.


-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160531/fc08a83c/attachment-0005.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 132067 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160531/fc08a83c/attachment-0010.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.jpg
Type: image/jpeg
Size: 1517 bytes
Desc: image004.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160531/fc08a83c/attachment-0010.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image006.jpg
Type: image/jpeg
Size: 1647 bytes
Desc: image006.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160531/fc08a83c/attachment-0011.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image012.png
Type: image/png
Size: 3859 bytes
Desc: image012.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160531/fc08a83c/attachment-0011.png>


More information about the Equest-users mailing list