The answer depends on your goal:
If you are looking for mandatory efficiency requirements for code
compliance, you would compare to the SPVHP numbers.
For Energy Cost Budget method or Appendix G analysis, you would use the
PTHP as your baseline system type, so you would use PTHP numbers as your
baseline efficiency.
Hope that helps! Cheers,
Elizabeth
*Elizabeth Gillmor PE, BEMP, LC, LEED AP*
*e n e r g e t i c s **consulting engineers, llc*
energetics-eng.com | 303.619.0091
**** Please note our office will be closed 5/27 - 6/4 ****
On Thu, May 12, 2016 at 12:09 PM, Sunayana Jain via Equest-users <
equest-users at lists.onebuilding.org> wrote:
> Hello,
>
> We have 1 ton single package vertical heat pump in each apartment of a
> multi-family building. For minimum efficiency as per ASHRAE 90.1-2007.
> should these systems be compared with Table 6.8.1D *PTHP* system or
> *SPVHP*?
>
> Please let me know.
>
> Thanks,
>
> Sunayana
>
>
>