You can only have one CHW meter per CHW loop, so you’d have to create a separate CHW loop for each system if you want cooling metered separately for each system. You would need to decide how to prorate the pump energy to each CHW loop pump by entering a reduced pump power. You can create separate electric meters for each system if you want to see the pumping energy broken out by system.
The CHW meter(s) will only report peak and cumulative loads in MMBtu/hr and MMBtu. You can get the same information for each system from the SS-A reports.
Regards,
~Bill
William Bishop, PE, BEMP, BEAP, CEM, LEED AP | Pathfinder Engineers & Architects LLP
Senior Energy Engineer
[cid:image004.jpg at 01D179E7.3BC70500] [cid:image005.jpg at 01D179E7.3BC70500]
134 South Fitzhugh Street Rochester, NY 14608
T: (585) 698-1956 F: (585) 325-6005
bbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com> www.pathfinder-ea.com<http://www.pathfinder-ea.com/>
[http://png-5.findicons.com/files/icons/977/rrze/720/globe.png]Carbon Fee and Dividend - simple, effective, and market-based.
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Rehana Jiffrey
Sent: Wednesday, March 09, 2016 12:48 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Multiple CHW meters
Dear All,
I'm modeling a residential building where a district cooling system provides cooling to spaces via AHU's and FCU's.
I want to track the CHW consumption of AHU's, FCU's and then the whole building seperately(3 chw meters).
Current CHW meter as shown in the Water-side schematic tracks all the FAHU's and FCU's chw consumption. Creating another chw meter causes creation of another chw pump(although linked to existing chw pump), and I have set it to as standby, my electricity and chw meter consumption has been increased.
Can anyone give ideas on how to add several chw meters to track individual FAHU or FCU chw consumption?.
Any ideas much appreciated.
Thanks.
Rehana
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160309/69c92979/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.jpg
Type: image/jpeg
Size: 1517 bytes
Desc: image004.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160309/69c92979/attachment-0004.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.jpg
Type: image/jpeg
Size: 1647 bytes
Desc: image005.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160309/69c92979/attachment-0005.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image006.png
Type: image/png
Size: 3856 bytes
Desc: image006.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160309/69c92979/attachment-0002.png>
More information about the Equest-users
mailing list