[Equest-users] Output of Space cool consumption comes innegative
Nicholas.Caton at schneider-electric.com
Nicholas.Caton at schneider-electric.com
Tue Mar 29 07:59:52 PDT 2016
Hi Nitin,
I suspect there are inadvertent changes beyond those you’ve described moving CFM’s around. Comparing a before/after save file case could prove enlightening if that’s available.
I searched the archives a bit – past instances of “negative cooling” have reportedly involved:
- Misapplied CHW loop reset scheduling
- Drastically undersized chiller capacities (review units, try auto-sizing)
- Drastically undersized heat rejection / towers, in a similar vein
- Custom chiller curves gone awry
Some other observations, beyond the negative cooling:
- Electric heating is more than doubling
- Electric fan energies are altogether slightly higher
- Gas heating is a full magnitude larger
From the above I’d suspect one or more edits to inputs on the hydronic side are playing a role…
Best regards,
~Nick
---------------------------------------------------------------------------------------------------------------------------------------------
Nick Caton, P.E.
Senior Energy Engineer
Energy and Sustainability Services
North America Operations
Schneider Electric
D 913.564.6361
M 785.410.3317
E nicholas.caton at schneider-electric.com <mailto:nicholas.caton at schneider-electric.com>
F 913.564.6380
15200 Santa Fe Trail Drive
Suite 204
Lenexa, KS 66219
United States
<http://www.schneider-electric.com/ww/en/>
*Please consider the environment before printing this e-mail
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Javed Iqbal
Sent: Monday, March 28, 2016 11:45 AM
To: Nitin Harjai
Cc: equest-users
Subject: Re: [Equest-users] Output of Space cool consumption comes innegative
Would you mind sharing your INP and PD files?
On Mon, Mar 28, 2016 at 10:13 PM, Nitin Harjai <nitin.harjai28 at gmail.com> wrote:
Hi...
I have a problem regarding the equest output & I need your help so that I can complete the project on time.
At the first step to remove the proposed case unmet hours,i have increased the cfm of same zone by diverting the cfm of other zone which is having zero unmet hour, in order to maintain the design CFM of particular system throughout the model.
After simulate the model, the unmet hour of same zone has been reduced without affecting the zone from where the CFM was diverted, but the output of space cool consumption comes in negative. I have attached the pics of before & after the simulation of monthly energy consumption graph.
I just want to know that why is this space cool output consumption showing in negative and how to make it correct?
For your information, this is the hospital project consist of ground+7 floors+3 basements and for cooling & heating, there are two water cooled screw chiller, two hot water generator are used on site.
Regards,
Nitin Harjai
Sustainability Engg.
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
--
Javed Iqbal, LEED AP, CEA
Sr. Energy Analyst
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160329/a9f9fe24/attachment-0005.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.gif
Type: image/gif
Size: 1822 bytes
Desc: image001.gif
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160329/a9f9fe24/attachment-0005.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 5423 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160329/a9f9fe24/attachment-0005.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Pic.jpg
Type: image/jpeg
Size: 200820 bytes
Desc: Pic.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160329/a9f9fe24/attachment-0010.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Pic2.jpg
Type: image/jpeg
Size: 195260 bytes
Desc: Pic2.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160329/a9f9fe24/attachment-0011.jpg>
More information about the Equest-users
mailing list