[Equest-users] LEED Baseline for onsite cogeneration

Nicholas.Caton at schneider-electric.com Nicholas.Caton at schneider-electric.com
Thu Mar 24 12:17:09 PDT 2016


Hi Steve,

 

I think the answer will depend on a few things.

 

Probably good advice to plan for eventually submitting a
project/site-specific query with GBCI (though you may not need to).
First peruse the published guidance for LEED district energy systems
"Treatment of District or Campus Thermal Energy in LEED."  I and others
have referenced this as the "DES guidance" as well (may be helpful as a
search term).  

 

You'll want to review the whole thing, but there's an appendix towards
the back specifically addressing EAp2/EAc1 credits post-processing for
district/campus systems including cogeneration/CHP equipment.  I've done
this a few times over now (for projects on a district
heating/power-generation loop).  Sadly I've yet to encounter a project
that "cleanly" fits this guidance to a tee (just my luck probably...),
but if you take some time to digest what's there you might be able to
ask more direct and productive questions for clarification specific to
your project, if needed.  If this equipment is not on a district/campus
loop, you may be able to isolate/extract some simpler direction using
this as a framework.  

 

It *might* be as simple as doing nothing special for the baseline and
just lopping off an electricity credit at the end for your proposed case
based upon simulated output (if you are modeling the equipment
explicitly within the simulation).  Hopefully that's the case and
someone else can confirm ;).  Even in that simplest case you should
probably plan on developing a write-up for supplemental documentation to
summarize the pertinent equipment documentation & simulation inputs +
outputs.

 

~Nick

 

------------------------------------------------------------------------
---------------------------------------------------------------------

Nick Caton, P.E.

  Senior Energy Engineer
  Energy and Sustainability Services
  North America Operations
  Schneider Electric

D  913.564.6361 
M  785.410.3317 
E  nicholas.caton at schneider-electric.com
<mailto:nicholas.caton at schneider-electric.com> 
F  913.564.6380

15200 Santa Fe Trail Drive
Suite 204
Lenexa, KS 66219
United States

  <http://www.schneider-electric.com/ww/en/> 

 

 

*Please consider the environment before printing this e-mail

 

 

 

From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org]
On Behalf Of Steve Jacobs
Sent: Thursday, March 24, 2016 11:50 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] LEED Baseline for onsite cogeneration

 

Has anyone done a LEED project with an onsite microturbine used for
electricity generation and heat recovery for the hot water loop. 

 

Appendix G seems to state clearly that I can take credit for the waste
heat recovery. My question is if I need to have the microturbine in the
baseline,  but not use the heat recovery feature. Or if the Baseline
should just be standard electrical use on the main meter. 


______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud
service.
______________________________________________________________________

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160324/77f9102d/attachment-0005.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.gif
Type: image/gif
Size: 1822 bytes
Desc: image001.gif
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160324/77f9102d/attachment-0005.gif>