[Equest-users] Heat recovery ventilation
Bishop, Bill via Equest-users
equest-users at lists.onebuilding.org
Fri Jun 10 15:52:23 PDT 2016
Peter,
The model looks sound and I don't see any "oops" inputs so quick QC looks okay.
Several things are going on that can minimize the benefit of heat recovery:
- Oregon weather file with peak heating load at 34F
- Modest ventilation requirement with roughly 20% OA
- Low ventilation hours (2600 hrs/year)
- High (?) infiltration rate (0.7 ACH) representing 1/3 of your heating load for system sizing
- Efficient boiler
- BOILER: MIN-RATIO = 0; START-UP-TIME = 0; STANDBY-TIME = 0 which totally eliminates cycling and standby losses
Regards,
~Bill
William Bishop, PE, BEMP, BEAP, CEM, LEED AP | Pathfinder Engineers & Architects LLP
Senior Energy Engineer
[cid:image003.jpg at 01D1C349.38F22FC0] [cid:image005.jpg at 01D1C349.38F22FC0]
134 South Fitzhugh Street Rochester, NY 14608
T: (585) 698-1956 F: (585) 325-6005
bbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com> www.pathfinder-ea.com<http://www.pathfinder-ea.com/>
[http://png-5.findicons.com/files/icons/977/rrze/720/globe.png]Carbon Fee and Dividend - simple, effective, and market-based.
\
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Peter Reppe, CPHC, LEED AP via Equest-users
Sent: Friday, June 10, 2016 4:47 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Heat recovery ventilation
Hi folks,
In double-checking the savings numbers from ventilation air heat recovery on my straight-forward VAV system, I noticed that the heating savings are less than half what I'd expect (based on back-of-the-envelope QC). I'm now out of ideas where to look for input errors, and am rather frustrated to see this happen on a pretty standard VAV system...
Would someone here have a moment and take a look, please (when running it, please use parametric run 4)? I'd appreciate any feedback.
Thanks much!!!
Peter Reppe, LEED AP, CPHC
Energy Analyst
[cid:image003.jpg at 01CE44D4.DD6A74A0]Systems West Engineers
p. 541.342.7210
Our website has been renovated! See what's new at www.systemswestengineers.com<http://www.systemswestengineers.com/>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160610/4740a528/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image008.jpg
Type: image/jpeg
Size: 828 bytes
Desc: image008.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160610/4740a528/attachment-0006.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 1517 bytes
Desc: image003.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160610/4740a528/attachment-0007.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.jpg
Type: image/jpeg
Size: 1647 bytes
Desc: image005.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160610/4740a528/attachment-0008.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image007.png
Type: image/png
Size: 3856 bytes
Desc: image007.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160610/4740a528/attachment-0002.png>
More information about the Equest-users
mailing list