[Equest-users] Multi-Family Corridor Baseline
Elizabeth Gillmor via Equest-users
equest-users at lists.onebuilding.org
Thu Jun 9 18:24:48 PDT 2016
In my experience LEED will accept a second baseline system type for the
corridors, but then following appendix G, you would use a System type 7. I
would take the same interpretation for MFHR.
You could probably make a case to do all residential systems, but with gas
heating in the corridor, that would put you in a System Type 1 throughout,
which would unnecessarily punish your dwelling units.
Cheers,
Elizabeth
*Elizabeth Gillmor PE, BEMP, LC, LEED AP*
*e n e r g e t i c s **consulting engineers, llc*
energetics-eng.com | 303.619.0091
On Thu, Jun 9, 2016 at 1:41 PM, Sunayana Jain via Equest-users <
equest-users at lists.onebuilding.org> wrote:
> I have 10 floors multi-family building. Units are served by packaged
> terminal heat pumps and corridors are pressurized and are served by RTUs
> (MAUs) with gas heat. Units are naturally ventilated. Total corridor area
> is greater than 20,000 SF.
>
>
>
> I wanted to know if residential systems (System 1 or System 2) should be
> applied for the corridors in the baseline as recommended by Multi-Family
> High Rise (MFHR) guideline? Would LEED also accept residential systems for
> corridors instead of non-residential systems?
>
>
>
> I have seen this discussion in the past but was curious to know the latest
> take on it.
>
>
>
> Thanks,
>
>
>
> Sunayana
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160609/7c3517d2/attachment-0002.htm>
More information about the Equest-users
mailing list