[Equest-users] Boiler Fuel Type / Hot Water Pipe Properties

Jones, Christopher via Equest-users equest-users at lists.onebuilding.org
Wed Jun 8 07:22:29 PDT 2016


Keep in mind that different coal has different heating values.
The DOE2.2 default is 24,580,000 Btu/ton.

Coal Grade

Heating Value (Btu/Ton)


Anthracite

25,820,000

Semi-Anthracite

27,540,000

Low-volatile bituminous

28,680,000

Medium-volatile bituminous

27,680,000

High-volatile bituminous A

26,180,000

High-volatile bituminous B

24,260,000

High-volatile bituminous C

21,500,000

Sub-bituminous B

18,300,000

Sub-bituminous C

17,880,000

Lignite

13,800,000




[cid:image003.png at 01D09C46.E75BA0D0]
Christopher Jones, P.Eng.
Senior Engineer

WSP Canada Inc.
2300 Yonge Street, Suite 2300
Toronto, ON M4P 1E4
T +1 416-644-4226
F +1 416-487-9766
C +1 416-697-0056

www.wspgroup.com<http://www.wspgroup.com/>

From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of via Equest-users
Sent: Wednesday, June 08, 2016 10:01 AM
To: kasruko at hotmail.com
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Boiler Fuel Type / Hot Water Pipe Properties

Hello,

I think I might be able to answer at least a portion of the question. Right now, you seem to be switching between the wizards, and detailed mode. In eQuest,  I am not aware of any method of adding coal meters through the wizard, but I can help with adding coal to a model in detailed mode. Just as a warning, if you switch from detailed mode back into the wizards, all of the changes you made in detailed mode will be reversed. So, make sure you have everything you wanted to do in the wizard mode finished before you dive into detailed mode.

You can switch into the detailed editing mode using the main dropdown menu.

[cid:image010.png at 01D1C16F.A8DB25C0]

Once you’re in detailed mode, under the “Utility and Economics” tab, you can find all of the meters that you have for your building. eQuest will generate an electric meter (EM1) and a natural gas meter (FM1), that can be found in the component tree on the left hand side. Right click on the Fuel Meters folder, and select “Create Fuel Meter”
[cid:image011.png at 01D1C16F.A8DB25C0]

Select coal meter from the dropdown for meter type. In this example I chose to re-name it “Coal Meter”

[cid:image012.png at 01D1C16F.A8DB25C0]

Now that there is a meter for coal, I can assign the boiler to run on coal. Under the “Water-Side” HVAC tab, select the boiler(s) that you want to assign to run on coal. Under the “Fuel Meter” dropdown menu, select the coal meter you just created, and click done.

[cid:image013.png at 01D1C16F.A8DB25C0]

Now whenever you run the building simulation, your boiler will be using coal as its fuel source.

I hope that helps,

Greg
Greg Hildner, EIT, EMIT
Energy Engineer
Energy and Sustainability Services
Global Solutions

D  (913) 564-6358
M  (630) 380-4709
E  greg.hildner at schneider-electric.com<mailto:greg.hildner at schneider-electric.com>
F  (913) 564-6380

15200 Santa Fe Trail Dr
Suite 204
Lenexa, Kansas
United States




From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Tugçin Kirant via Equest-users
Sent: Wednesday, June 08, 2016 3:39 AM
To: Nicholas Caton; jra_sac at yahoo.com; dberty at baselineenergyconsulting.com
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Boiler Fuel Type / Hot Water Pipe Properties

Hello again,

First of all, i wanna thank all of you for your interests.

For pipe losses i will use your method Nicholas. It sounds as a reasonable solution for my problem.

However, I have problems about fuel type, still. When I click fuel type to change it to coal, it gives me warning as in picture:

[cid:image014.jpg at 01D1C16F.A8DB25C0]


and i say ok. Then it gives me another warning :

[cid:image015.jpg at 01D1C16F.A8DB25C0]

again i say ok to see what will happen and simulate it. As a result it doesnt give the results and the error is:

[cid:image016.jpg at 01D1C16F.A8DB25C0]

As i mentioned before, on the HW plant Equipment settings, it just gives me option for natural gas :/  I attached the picture below again:

[cid:image017.jpg at 01D1C16F.A8DB25C0]



I suppose that because of this, it doesnt calculate for coal, even i changed it on Utility&Economics section.

Do you have any idea about this?

Sincerely.

Ms. H. Tuğçin KIRANT


________________________________
Subject: RE: [Equest-users] Boiler Fuel Type / Hot Water Pipe Properties
Date: Tue, 7 Jun 2016 17:30:59 -0500
From: Nicholas.Caton at schneider-electric.com<mailto:Nicholas.Caton at schneider-electric.com>
To: jra_sac at yahoo.com<mailto:jra_sac at yahoo.com>; dberty at baselineenergyconsulting.com<mailto:dberty at baselineenergyconsulting.com>; kasruko at hotmail.com<mailto:kasruko at hotmail.com>
CC: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
I might add something contrarian, but this does require getting past wizards and into detailed edits per John’s advice:

eQuest can certainly be used to assess distribution losses.  If you are willing/able to determine a reasonable assessment of pipe area and average insulation level (U*A), eQuest can actually determine on an hourly basis the losses in that circulation loop (U*A*dT).  For this you can choose between a few different loop “locations” which will vary how the delta in temperatures is assessed each hour.  Suggest further reading up on the inputs located here in detailed mode:
[Image removed by sender.]

Fair counterpoint: piping/distribution losses are (for reasonable reasons) deliberately excluded from common modes of code compliance simulation and the performance rating method (i.e. LEED, Appendix G), which are generally focused upon “design side” simulation/validation modeling and typically are trying to avoid such realities in an effort to minimize “arbitrary” penalization (i.e. why must my distributed campus with necessarily larger distribution losses have a harder go at meeting threshold XYZ?).  In turn such inputs don’t get a ton of attention from that side of our industry.

Further, once you’re looking at the “rainbow reports,” note the “gas” consumption/demand charts really more generically mean to reference “Fuel.”  The numbers should be analogous (if with slightly different rounding sometimes) to the PS-E report for “all fuel meters,” IIRC.

You can also directly edit those titles for presentation if need be by right-clicking the chart for a context menu – it’s in one of the tabs there ;).
[Image removed by sender.]

------------------------------------------------------------------------------------------------------------------------------
Nick Caton, P.E.
  Senior Energy Engineer
  Energy and Sustainability Services
  North America Operations
  Schneider Electric

D  913.564.6361
M  785.410.3317
E  nicholas.caton at schneider-electric.com<mailto:nicholas.caton at schneider-electric.com>
F  913.564.6380

15200 Santa Fe Trail Drive
Suite 204
Lenexa, KS 66219
United States

[Image removed by sender. cid:image001.png at 01D189AB.58634A10]



From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of John Aulbach via Equest-users
Sent: Tuesday, June 07, 2016 11:59 AM
To: David Berty; Tuğçin Kırant
Cc: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] Boiler Fuel Type / Hot Water Pipe Properties

Sir:

If you are familiar with the DETAIL-EDIT mode, place your project in that Mode (after making a copy of it to stay in Wizard mode) - by all means give it another name to avoid confusion.

On the Horizontal Tab that says UTILITIES and ECONOMICS, you can then go to the tree hierarchy on the left side of the page. Go to subfolder FUEL-METER and click on. The main screen now displays FUEL-METER attributes. Now if you click FUel Meter Type, Coal will appear. Make sure the Btu/unit is what you expect from your Coal, as i understand there are several types in use.

Hope this helps.

John R. Aulbach, PE
Los Angeles, CA

On Tuesday, June 7, 2016 7:03 AM, David Berty via Equest-users <equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>> wrote:

I don't personally know the answer to your question on the fuel source coal vs. natural gas.
Regarding the 2nd question on simulation of piping pressure and thermal losses; these modelling software programs do not model these energy losses. They don't "care" where your central utility plant is physically located in relation to your load. They make the assumption that you have properly sized pipelines, insulation etc. EQuest is only attempting to estimate the fuel consumption of meeting the building's heating and cooling load, not assess the pipe sizing and insulation condition.
David Berty, P.E.
Baseline Energy Consulting
317.220.9272
On Jun 7, 2016 9:18 AM, "Tuğçin Kırant" <equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>> wrote:
Hi everyone :)

I am a new user and modelling a district heating system. Probably my questions are easy, but i couldnt solve the problems.

1- I define boiler but the fuel type must be coal. However, Equest doesnt let me get the results for coal. It simulates as natural gas. Even i create new fuel meter for coal and select it on boil properties. How can i get the results for coal? (Maybe it is related to pic1. But there is no other choice except Natural Gas )


[Image removed by sender.]

 2- As i mentioned before, this is a district heating system and there are 6 residential villas. Combined Heat Power Plant supplies the hot water and it is located very far away. I wanna see the effect of pipe lenght, dimension and insulataion material of the hot water pipes. So,  how can i enter the pipes and their properties?


Sincerely.

H. Tuğçin KIRANT

_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>

_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>


______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________

________________________________


You are receiving this communication because you are listed as a current WSP contact. Should you have any questions regarding WSP’s electronic communications policy, please consult our Anti-Spam Commitment www.wspgroup.com/casl<http://www.wspgroup.com/casl>. For any concern or if you believe you should not be receiving this message, please forward this message to caslcompliance at wspgroup.com.com<mailto:caslcompliance at wspgroup.com> so that we can promptly address your request. This message is intended only for the addressee and may contain information which is privileged, confidential, proprietary, or exempt from disclosure under applicable law. If you are not the intended recipient, you are strictly prohibited from disclosing, distributing, copying, or in any way using this message. If you have received this communication in error, please notify the sender and delete any copies you may have received.

----------------------------------------------------------------------------------------------------------------------------------------

Vous recevez cette communication car vous faites partie des contacts de WSP. Si vous avez des questions concernant la politique de communications électroniques de WSP, veuillez consulter notre Engagement anti-pourriel www.wspgroup.com/lcap<http://www.wspgroup.com/casl>. Pour toute question ou si vous croyez que vous ne devriez pas recevoir ce message, prière de le transférer au conformitelcap at wspgroup.com<mailto:conformitelcap at wspgroup.com> afin que nous puissions rapidement traiter votre demande. Ce message est destiné uniquement au destinataire et il peut contenir des informations privilégiées, confidentielles ou non divulgables en vertu de la loi. Si vous n’êtes pas le destinataire du présent message, il vous est strictement interdit de le divulguer, de le distribuer, de le copier ou de l’utiliser de quelque façon que ce soit. Si vous avez reçu la présente communication par erreur, veuillez en aviser l’expéditeur et supprimer le message.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160608/fd0dc22d/attachment-0005.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image009.png
Type: image/png
Size: 6574 bytes
Desc: image009.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160608/fd0dc22d/attachment-0025.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image010.png
Type: image/png
Size: 12345 bytes
Desc: image010.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160608/fd0dc22d/attachment-0026.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image011.png
Type: image/png
Size: 4981 bytes
Desc: image011.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160608/fd0dc22d/attachment-0027.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image012.png
Type: image/png
Size: 24534 bytes
Desc: image012.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160608/fd0dc22d/attachment-0028.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image013.png
Type: image/png
Size: 55199 bytes
Desc: image013.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160608/fd0dc22d/attachment-0029.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image014.jpg
Type: image/jpeg
Size: 89669 bytes
Desc: image014.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160608/fd0dc22d/attachment-0040.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image015.jpg
Type: image/jpeg
Size: 75085 bytes
Desc: image015.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160608/fd0dc22d/attachment-0041.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image016.jpg
Type: image/jpeg
Size: 17703 bytes
Desc: image016.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160608/fd0dc22d/attachment-0042.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image017.jpg
Type: image/jpeg
Size: 99319 bytes
Desc: image017.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160608/fd0dc22d/attachment-0043.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image018.jpg
Type: image/jpeg
Size: 2555 bytes
Desc: image018.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160608/fd0dc22d/attachment-0044.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image019.jpg
Type: image/jpeg
Size: 4253 bytes
Desc: image019.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160608/fd0dc22d/attachment-0045.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image020.jpg
Type: image/jpeg
Size: 809 bytes
Desc: image020.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160608/fd0dc22d/attachment-0046.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image021.jpg
Type: image/jpeg
Size: 2574 bytes
Desc: image021.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160608/fd0dc22d/attachment-0047.jpg>


More information about the Equest-users mailing list